Re: [EnergyPlus_Support] Strange Dates in Daylighting Map
Thanks again,
Re weather files; when trying to manually change the time zone to 2 in the ETMY file and using it, this yielded in different (less required sensible cooling) from the results when using the IWEC file, ??
Any possible reasons? isn't the onnly difference the time zone value?
Thank you
Abeer
Linda Lawrie <linda@xxxxxxxxxx> wrote:
The "strange dates" in the Daylighting Map were not produced by
EnergyPlus. Rather it is after you read the file with Excel. (Other
spreadsheet programs may be similar -- I didn't try them).
As it turns out, the fix is rather simple. I noticed that our
"regular" csv files did not have the same problem. Because there is
a space in front of the date string (i.e. " 1/01" rather than
"1/01"). So, the Map file will use that convention and the inserting
of years (and getting confused by regional date settings) won't occur
in the next release.
Thanks for pointing this out.
Linda
EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team
[Non-text portions of this message have been removed]
Abeer M. Eisa
Visiting Scholar
School of Architecture
University of Sheffield
Western Bank
Sheffield S10 2TN, UK
tel. 0114 2220372 , Mob. 0789 44 69159
---------------------------------
Need a vacation? Get great deals to amazing places on Yahoo! Travel.
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/