Regarding the schedules:

The WEEKSCHEDULE "pessoas" object is correct.  The WEEKSCHEDULE:COMPACT 
"pessoas" object is incomplete, but it also duplicates the same weekschedule.  
The two objects are just different forms of specifying the same thing - 
associting specific day schedule objects with certain day types.  Delete the 
WEEKSCHEDULE:COMPACT object and add a SCHEDULE object:

  SCHEDULE,
    pessoas schedule,            !- Name
    ,              !- ScheduleType
    pessoas,              !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    12,                      !- End Month 1
    31;                      !- End Day 1

In the PEOPLE object, the schedule name should be "pessoas schedule" to 
reference this top-level SCHEDULE object.

Your thermostat, zone equipment, purchased air, and reporting objects look 
correct for the heating and cooling loads.  Once you fix the schedule problems, 
it should report what you want.

Mike



On 6 Aug 2007 at 8:43, grossonomato wrote:

> Hello all
> 
> I'm trying to do a simple case where i want to make a weekschedule 
> and a weenkendscedule for people and lights. And in the output report 
> i want it to give me the cooling load and heating load necessary 
> trough the year.
> 
> For example: 
> for people i can have 20 people in the buildind maximum during 
> day.During the dayweek i want to make 9:00 10%; 10:00;20%;11;:00 30 
> (order and % not important)...
> During the weekend i want to make 9:00 11%; 10:00 22%;11:00 33% 
> (order and % not important)...
> 
> For lights something similar but with diferent values like max power 
> output 1000Watt and during the week i have an hourly percentage of 
> that power.
> In the output report i want it to give me the cooling load and 
> heating load necessary trough the year hourly.
> 
> This is what i have tryed to do without success, i defined the 
> building,materials and all the rest.
> 
> 
> 
> 
> 
> !-Generator IDFEditor 1.28g
> !-Option SortedOrder
> 
> !-NOTE: All comments with '!-' are ignored by the IDFEditor and are 
> generated automatically.
> !-      Use '!' comments if they need to be retained when using the 
> IDFEditor.
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: VERSION ===========
> 
> VERSION,
>     2.00;                    !- Version Identifier
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: BUILDING ===========
> 
> BUILDING,
>     caso simples,            !- Building Name
>     0,                       !- North Axis {deg}
>     Suburbs,                 !- Terrain
>     0.04,                    !- Loads Convergence Tolerance Value
>     0.4,                     !- Temperature Convergence Tolerance 
> Value {deltaC}
>     FullInteriorAndExterior, !- Solar Distribution
>     25;                      !- Maximum Number of Warmup Days
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: TIMESTEP IN HOUR ===========
> 
> TIMESTEP IN HOUR,
>     4;                       !- Time Step in Hour
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: INSIDE CONVECTION ALGORITHM 
> ===========
> 
> INSIDE CONVECTION ALGORITHM,
>     Detailed;                !- Algorithm
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SOLUTION ALGORITHM ===========
> 
> SOLUTION ALGORITHM,
>     CTF;                     !- SolutionAlgo
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SHADOWING CALCULATIONS 
> ===========
> 
> SHADOWING CALCULATIONS,
>     20,                      !- Period_for_calculations
>     15000;                   !- Max_figures_shadow
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: ZONE VOLUME CAPACITANCE 
> MULTIPLIER ===========
> 
> ZONE VOLUME CAPACITANCE MULTIPLIER,
>     1;                       !- Capacitance Multiplier
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: RUN CONTROL ===========
> 
> RUN CONTROL,
>     Yes,                     !- Do the zone sizing calculation
>     No,                      !- Do the system sizing calculation
>     Yes,                     !- Do the plant sizing calculation
>     Yes,                     !- Do the design day simulations
>     No;                      !- Do the weather file simulation
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: RUNPERIOD ===========
> 
> RunPeriod,
>     1,                       !- Begin Month
>     1,                       !- Begin Day Of Month
>     1,                       !- End Month
>     31,                      !- End Day Of Month
>     UseWeatherFile,          !- Day Of Week For Start Day
>     Yes,                     !- Use WeatherFile Holidays/Special Days
>     Yes,                     !- Use WeatherFile DaylightSavingPeriod
>     No,                      !- Apply Weekend Holiday Rule
>     Yes,                     !- Use WeatherFile Rain Indicators
>     Yes,                     !- Use WeatherFile Snow Indicators
>     1;                       !- Number of years of simulation
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: DAYLIGHTSAVINGPERIOD 
> ===========
> 
> DaylightSavingPeriod,
>     Last Sunday in March,    !- StartDate
>     Last Sunday in October;  !- EndDate
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: LOCATION ===========
> 
> Location,
>     Lisboa_PRT Design_Conditions,  !- LocationName
>     38.73,                   !- Latitude {deg}
>     -9.15,                   !- Longitude {deg}
>     0.00,                    !- TimeZone {hr}
>     71.00;                   !- Elevation {m}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: DESIGNDAY ===========
> 
> DesignDay,
>     Lisboa Ann Htg 99.6% Condns DB,  !- DesignDayName
>     4.2,                     !- Maximum Dry-Bulb Temperature {C}
>     0.0,                     !- Daily Temperature Range {deltaC}
>     4.2,                     !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     2.1,                     !- Wind Speed {m/s}
>     50,                      !- Wind Direction {deg}
>     0.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     1,                       !- Month
>     WinterDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Wet-Bulb;                !- Humidity Indicating Type
> 
> DesignDay,
>     Lisboa Ann Htg 99% Condns DB,  !- DesignDayName
>     5.8,                     !- Maximum Dry-Bulb Temperature {C}
>     0.0,                     !- Daily Temperature Range {deltaC}
>     5.8,                     !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     2.1,                     !- Wind Speed {m/s}
>     50,                      !- Wind Direction {deg}
>     0.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     1,                       !- Month
>     WinterDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Wet-Bulb;                !- Humidity Indicating Type
> 
> DesignDay,
>     Lisboa Ann Hum_n 99.6% Condns DP=>MCDB,  !- DesignDayName
>     10.1,                    !- Maximum Dry-Bulb Temperature {C}
>     0.0,                     !- Daily Temperature Range {deltaC}
>     -2.9,                    !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     2.1,                     !- Wind Speed {m/s}
>     50,                      !- Wind Direction {deg}
>     0.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     1,                       !- Month
>     WinterDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Dew-Point;               !- Humidity Indicating Type
> 
> DesignDay,
>     Lisboa Ann Hum_n 99% Condns DP=>MCDB,  !- DesignDayName
>     10.6,                    !- Maximum Dry-Bulb Temperature {C}
>     0.0,                     !- Daily Temperature Range {deltaC}
>     -0.8,                    !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     2.1,                     !- Wind Speed {m/s}
>     50,                      !- Wind Direction {deg}
>     0.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     1,                       !- Month
>     WinterDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Dew-Point;               !- Humidity Indicating Type
> 
> DesignDay,
>     Lisboa Ann Htg Wind 99.6% Condns WS=>MCDB,  !- DesignDayName
>     13.3,                    !- Maximum Dry-Bulb Temperature {C}
>     0.0,                     !- Daily Temperature Range {deltaC}
>     13.3,                    !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     11.3,                    !- Wind Speed {m/s}
>     50,                      !- Wind Direction {deg}
>     0.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     1,                       !- Month
>     WinterDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Wet-Bulb;                !- Humidity Indicating Type
> 
> DesignDay,
>     Lisboa Ann Htg Wind 99% Condns WS=>MCDB,  !- DesignDayName
>     13.6,                    !- Maximum Dry-Bulb Temperature {C}
>     0.0,                     !- Daily Temperature Range {deltaC}
>     13.6,                    !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     10.1,                    !- Wind Speed {m/s}
>     50,                      !- Wind Direction {deg}
>     0.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     1,                       !- Month
>     WinterDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Wet-Bulb;                !- Humidity Indicating Type
> 
> DesignDay,
>     Lisboa Ann Clg .4% Condns DB=>MWB,  !- DesignDayName
>     34.1,                    !- Maximum Dry-Bulb Temperature {C}
>     10,                      !- Daily Temperature Range {deltaC}
>     20.5,                    !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     4.3,                     !- Wind Speed {m/s}
>     330,                     !- Wind Direction {deg}
>     1.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     8,                       !- Month
>     SummerDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Wet-Bulb;                !- Humidity Indicating Type
> 
> DesignDay,
>     Lisboa Ann Clg 1% Condns DB=>MWB,  !- DesignDayName
>     32,                      !- Maximum Dry-Bulb Temperature {C}
>     10,                      !- Daily Temperature Range {deltaC}
>     19.9,                    !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     4.3,                     !- Wind Speed {m/s}
>     330,                     !- Wind Direction {deg}
>     1.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     8,                       !- Month
>     SummerDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Wet-Bulb;                !- Humidity Indicating Type
> 
> DesignDay,
>     Lisboa Ann Clg 2% Condns DB=>MWB,  !- DesignDayName
>     30,                      !- Maximum Dry-Bulb Temperature {C}
>     10,                      !- Daily Temperature Range {deltaC}
>     19.6,                    !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     4.3,                     !- Wind Speed {m/s}
>     330,                     !- Wind Direction {deg}
>     1.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     8,                       !- Month
>     SummerDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Wet-Bulb;                !- Humidity Indicating Type
> 
> DesignDay,
>     Lisboa Ann Clg .4% Condns WB=>MDB,  !- DesignDayName
>     29.7,                    !- Maximum Dry-Bulb Temperature {C}
>     10,                      !- Daily Temperature Range {deltaC}
>     22.4,                    !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     4.3,                     !- Wind Speed {m/s}
>     330,                     !- Wind Direction {deg}
>     1.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     8,                       !- Month
>     SummerDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Wet-Bulb;                !- Humidity Indicating Type
> 
> DesignDay,
>     Lisboa Ann Clg 1% Condns WB=>MDB,  !- DesignDayName
>     27.9,                    !- Maximum Dry-Bulb Temperature {C}
>     10,                      !- Daily Temperature Range {deltaC}
>     21.5,                    !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     4.3,                     !- Wind Speed {m/s}
>     330,                     !- Wind Direction {deg}
>     1.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     8,                       !- Month
>     SummerDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Wet-Bulb;                !- Humidity Indicating Type
> 
> DesignDay,
>     Lisboa Ann Clg 2% Condns WB=>MDB,  !- DesignDayName
>     26.6,                    !- Maximum Dry-Bulb Temperature {C}
>     10,                      !- Daily Temperature Range {deltaC}
>     20.9,                    !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     4.3,                     !- Wind Speed {m/s}
>     330,                     !- Wind Direction {deg}
>     1.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     8,                       !- Month
>     SummerDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Wet-Bulb;                !- Humidity Indicating Type
> 
> DesignDay,
>     Lisboa Ann Clg .4% Condns DP=>MDB,  !- DesignDayName
>     23.8,                    !- Maximum Dry-Bulb Temperature {C}
>     10,                      !- Daily Temperature Range {deltaC}
>     20.8,                    !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     4.3,                     !- Wind Speed {m/s}
>     330,                     !- Wind Direction {deg}
>     1.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     8,                       !- Month
>     SummerDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Dew-Point;               !- Humidity Indicating Type
> 
> DesignDay,
>     Lisboa Ann Clg 1% Condns DP=>MDB,  !- DesignDayName
>     23,                      !- Maximum Dry-Bulb Temperature {C}
>     10,                      !- Daily Temperature Range {deltaC}
>     19.9,                    !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     4.3,                     !- Wind Speed {m/s}
>     330,                     !- Wind Direction {deg}
>     1.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     8,                       !- Month
>     SummerDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Dew-Point;               !- Humidity Indicating Type
> 
> DesignDay,
>     Lisboa Ann Clg 2% Condns DP=>MDB,  !- DesignDayName
>     22.6,                    !- Maximum Dry-Bulb Temperature {C}
>     10,                      !- Daily Temperature Range {deltaC}
>     19.1,                    !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     4.3,                     !- Wind Speed {m/s}
>     330,                     !- Wind Direction {deg}
>     1.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     8,                       !- Month
>     SummerDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Dew-Point;               !- Humidity Indicating Type
> 
> DesignDay,
>     Lisboa Ann Clg .4% Condns Enth=>MDB,  !- DesignDayName
>     30,                      !- Maximum Dry-Bulb Temperature {C}
>     10,                      !- Daily Temperature Range {deltaC}
>     66.2,                    !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     4.3,                     !- Wind Speed {m/s}
>     330,                     !- Wind Direction {deg}
>     1.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     8,                       !- Month
>     SummerDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Enthalpy;                !- Humidity Indicating Type
> 
> DesignDay,
>     Lisboa Ann Clg 1% Condns Enth=>MDB,  !- DesignDayName
>     27.8,                    !- Maximum Dry-Bulb Temperature {C}
>     10,                      !- Daily Temperature Range {deltaC}
>     63.4,                    !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     4.3,                     !- Wind Speed {m/s}
>     330,                     !- Wind Direction {deg}
>     1.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     8,                       !- Month
>     SummerDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Enthalpy;                !- Humidity Indicating Type
> 
> DesignDay,
>     Lisboa Ann Clg 2% Condns Enth=>MDB,  !- DesignDayName
>     26.9,                    !- Maximum Dry-Bulb Temperature {C}
>     10,                      !- Daily Temperature Range {deltaC}
>     61.1,                    !- Humidity Indicating Conditions at Max 
> Dry-Bulb
>     100475.,                 !- Barometric Pressure {Pa}
>     4.3,                     !- Wind Speed {m/s}
>     330,                     !- Wind Direction {deg}
>     1.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day Of Month
>     8,                       !- Month
>     SummerDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     Enthalpy;                !- Humidity Indicating Type
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: GROUNDTEMPERATURES ===========
> 
> GroundTemperatures,
>     15,                      !- January Ground Temperature {C}
>     15,                      !- February Ground Temperature {C}
>     15,                      !- March Ground Temperature {C}
>     15,                      !- April Ground Temperature {C}
>     15,                      !- May Ground Temperature {C}
>     18,                      !- June Ground Temperature {C}
>     20,                      !- July Ground Temperature {C}
>     20,                      !- August Ground Temperature {C}
>     20,                      !- September Ground Temperature {C}
>     18,                      !- October Ground Temperature {C}
>     15,                      !- November Ground Temperature {C}
>     15;                      !- December Ground Temperature {C}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: GROUNDREFLECTANCES ===========
> 
> GroundReflectances,
>     0.2,                     !- January Ground Reflectance 
> {dimensionless}
>     0.2,                     !- February Ground Reflectance 
> {dimensionless}
>     0.2,                     !- March Ground Reflectance 
> {dimensionless}
>     0.2,                     !- April Ground Reflectance 
> {dimensionless}
>     0.2,                     !- May Ground Reflectance {dimensionless}
>     0.2,                     !- June Ground Reflectance 
> {dimensionless}
>     0.2,                     !- July Ground Reflectance 
> {dimensionless}
>     0.2,                     !- August Ground Reflectance 
> {dimensionless}
>     0.2,                     !- September Ground Reflectance 
> {dimensionless}
>     0.2,                     !- October Ground Reflectance 
> {dimensionless}
>     0.2,                     !- November Ground Reflectance 
> {dimensionless}
>     0.2;                     !- December Ground Reflectance 
> {dimensionless}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: MATERIAL:REGULAR ===========
> 
> MATERIAL:REGULAR,
>     parede de alvenaria,     !- Name
>     MediumRough,             !- Roughness
>     0.14,                    !- Thickness {m}
>     0.56,                    !- Conductivity {W/m-K}
>     8214,                    !- Density {kg/m3}
>     800,                     !- Specific Heat {J/kg-K}
>     0.9,                     !- Absorptance:Thermal
>     0.7,                     !- Absorptance:Solar
>     0.7;                     !- Absorptance:Visible
> 
> MATERIAL:REGULAR,
>     betão,                   !- Name
>     MediumRough,             !- Roughness
>     0.2,                     !- Thickness {m}
>     1.72,                    !- Conductivity {W/m-K}
>     224258,                  !- Density {kg/m3}
>     830,                     !- Specific Heat {J/kg-K}
>     0.9,                     !- Absorptance:Thermal
>     0.6,                     !- Absorptance:Solar
>     0.6;                     !- Absorptance:Visible
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: MATERIAL:REGULAR-R ===========
> 
> MATERIAL:REGULAR-R,
>     isolante,                !- Name
>     VeryRough,               !- Roughness
>     0.03,                    !- Thermal Resistance {m2-K/W}
>     0.9,                     !- Absorptance:Thermal
>     0.5,                     !- Absorptance:Solar
>     0.5;                     !- Absorptance:Visible
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: MATERIAL:WINDOWGLASS 
> ===========
> 
> MATERIAL:WINDOWGLASS,
>     Glass - clear plate,     !- Name
>     SpectralAverage,         !- Optical Data Type
>     ,                        !- Name of Window Glass Spectral Data Set
>     0.012,                   !- Thickness {m}
>     0.653,                   !- Solar Transmittance at Normal 
> Incidence
>     0.064000003,             !- Solar Reflectance at Normal 
> Incidence: Front Side
>     0.064000003,             !- Solar Reflectance at Normal 
> Incidence: Back Side
>     0.841,                   !- Visible Transmittance at Normal 
> Incidence
>     0.077,                   !- Visible Reflectance at Normal 
> Incidence: Front Side
>     0.077,                   !- Visible Reflectance at Normal 
> Incidence: Back Side
>     0,                       !- IR Transmittance at Normal Incidence
>     0.84,                    !- IR Hemispherical Emissivity: Front 
> Side
>     0.84,                    !- IR Hemispherical Emissivity: Back Side
>     0.9,                     !- Conductivity {W/m-K}
>     1,                       !- Dirt Correction Factor for Solar and 
> Visible Transmittance
>     No;                      !- Solar Diffusing
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: MATERIAL:WINDOWGAS ===========
> 
> MATERIAL:WINDOWGAS,
>     AIRSPACE,                !- Name
>     Air,                     !- Gas Type
>     0.013;                   !- Thickness {m}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: CONSTRUCTION ===========
> 
> CONSTRUCTION,
>     PAREDE DE BETAO,         !- Name
>     betão;                   !- Outside Layer
> 
> CONSTRUCTION,
>     PAREDE ISOLADA IN,       !- Name
>     betão,                   !- Outside Layer
>     isolante;                !- Layer #2
> 
> CONSTRUCTION,
>     PAREDE ISOLADA OUT,      !- Name
>     isolante,                !- Outside Layer
>     betão;                   !- Layer #2
> 
> CONSTRUCTION,
>     VIDRO SIMPLES,           !- Name
>     Glass - clear plate;     !- Outside Layer
> 
> CONSTRUCTION,
>     VIDRO DUPLO,             !- Name
>     Glass - clear plate,     !- Outside Layer
>     AIRSPACE,                !- Layer #2
>     Glass - clear plate;     !- Layer #3
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: ZONE ===========
> 
> ZONE,
>     zone,                    !- Zone Name
>     0,                       !- Relative North (to building) {deg}
>     0,                       !- X Origin {m}
>     0,                       !- Y Origin {m}
>     0,                       !- Z Origin {m}
>     1,                       !- Type
>     1,                       !- Multiplier
>     autocalculate,           !- Ceiling Height {m}
>     0;                       !- Volume {m3}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SURFACEGEOMETRY ===========
> 
> SurfaceGeometry,
>     UpperLeftCorner,         !- SurfaceStartingPosition
>     ClockWise,               !- VertexEntry
>     relative;                !- CoordinateSystem
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SURFACE:HEATTRANSFER 
> ===========
> 
> Surface:HeatTransfer,
>     surface north,           !- User Supplied Surface Name
>     WALL,                    !- Surface Type
>     PAREDE DE BETAO,         !- Construction Name of the Surface
>     zone,                    !- Zone Name
>     ExteriorEnvironment,     !- OutsideFaceEnvironment
>     ,                        !- OutsideFaceEnvironment Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     0.5,                     !- View Factor to Ground
>     4,                       !- Number of Surface Vertex Groups -- 
> Number of (X,Y,Z) groups in this surface
>     0,                       !- Vertex 1 X-coordinate {m}
>     8,                       !- Vertex 1 Y-coordinate {m}
>     3,                       !- Vertex 1 Z-coordinate {m}
>     0,                       !- Vertex 2 X-coordinate {m}
>     0,                       !- Vertex 2 Y-coordinate {m}
>     3,                       !- Vertex 2 Z-coordinate {m}
>     0,                       !- Vertex 3 X-coordinate {m}
>     0,                       !- Vertex 3 Y-coordinate {m}
>     0,                       !- Vertex 3 Z-coordinate {m}
>     0,                       !- Vertex 4 X-coordinate {m}
>     8,                       !- Vertex 4 Y-coordinate {m}
>     0;                       !- Vertex 4 Z-coordinate {m}
> 
> Surface:HeatTransfer,
>     surface east,            !- User Supplied Surface Name
>     WALL,                    !- Surface Type
>     PAREDE DE BETAO,         !- Construction Name of the Surface
>     zone,                    !- Zone Name
>     ExteriorEnvironment,     !- OutsideFaceEnvironment
>     ,                        !- OutsideFaceEnvironment Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     0.5,                     !- View Factor to Ground
>     4,                       !- Number of Surface Vertex Groups -- 
> Number of (X,Y,Z) groups in this surface
>     0,                       !- Vertex 1 X-coordinate {m}
>     0,                       !- Vertex 1 Y-coordinate {m}
>     3,                       !- Vertex 1 Z-coordinate {m}
>     10,                      !- Vertex 2 X-coordinate {m}
>     0,                       !- Vertex 2 Y-coordinate {m}
>     3,                       !- Vertex 2 Z-coordinate {m}
>     10,                      !- Vertex 3 X-coordinate {m}
>     0,                       !- Vertex 3 Y-coordinate {m}
>     0,                       !- Vertex 3 Z-coordinate {m}
>     0,                       !- Vertex 4 X-coordinate {m}
>     0,                       !- Vertex 4 Y-coordinate {m}
>     0;                       !- Vertex 4 Z-coordinate {m}
> 
> Surface:HeatTransfer,
>     surface south,           !- User Supplied Surface Name
>     WALL,                    !- Surface Type
>     PAREDE DE BETAO,         !- Construction Name of the Surface
>     zone,                    !- Zone Name
>     ExteriorEnvironment,     !- OutsideFaceEnvironment
>     ,                        !- OutsideFaceEnvironment Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     0.5,                     !- View Factor to Ground
>     4,                       !- Number of Surface Vertex Groups -- 
> Number of (X,Y,Z) groups in this surface
>     10,                      !- Vertex 1 X-coordinate {m}
>     0,                       !- Vertex 1 Y-coordinate {m}
>     3,                       !- Vertex 1 Z-coordinate {m}
>     10,                      !- Vertex 2 X-coordinate {m}
>     8,                       !- Vertex 2 Y-coordinate {m}
>     3,                       !- Vertex 2 Z-coordinate {m}
>     10,                      !- Vertex 3 X-coordinate {m}
>     8,                       !- Vertex 3 Y-coordinate {m}
>     0,                       !- Vertex 3 Z-coordinate {m}
>     10,                      !- Vertex 4 X-coordinate {m}
>     0,                       !- Vertex 4 Y-coordinate {m}
>     0;                       !- Vertex 4 Z-coordinate {m}
> 
> Surface:HeatTransfer,
>     surface west,            !- User Supplied Surface Name
>     WALL,                    !- Surface Type
>     PAREDE DE BETAO,         !- Construction Name of the Surface
>     zone,                    !- Zone Name
>     ExteriorEnvironment,     !- OutsideFaceEnvironment
>     ,                        !- OutsideFaceEnvironment Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     0.5,                     !- View Factor to Ground
>     4,                       !- Number of Surface Vertex Groups -- 
> Number of (X,Y,Z) groups in this surface
>     10,                      !- Vertex 1 X-coordinate {m}
>     8,                       !- Vertex 1 Y-coordinate {m}
>     3,                       !- Vertex 1 Z-coordinate {m}
>     0,                       !- Vertex 2 X-coordinate {m}
>     8,                       !- Vertex 2 Y-coordinate {m}
>     3,                       !- Vertex 2 Z-coordinate {m}
>     0,                       !- Vertex 3 X-coordinate {m}
>     8,                       !- Vertex 3 Y-coordinate {m}
>     0,                       !- Vertex 3 Z-coordinate {m}
>     10,                      !- Vertex 4 X-coordinate {m}
>     8,                       !- Vertex 4 Y-coordinate {m}
>     0;                       !- Vertex 4 Z-coordinate {m}
> 
> Surface:HeatTransfer,
>     surface floor,           !- User Supplied Surface Name
>     FLOOR,                   !- Surface Type
>     PAREDE DE BETAO,         !- Construction Name of the Surface
>     zone,                    !- Zone Name
>     Ground,                  !- OutsideFaceEnvironment
>     ,                        !- OutsideFaceEnvironment Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     0.5,                     !- View Factor to Ground
>     4,                       !- Number of Surface Vertex Groups -- 
> Number of (X,Y,Z) groups in this surface
>     0,                       !- Vertex 1 X-coordinate {m}
>     0,                       !- Vertex 1 Y-coordinate {m}
>     0,                       !- Vertex 1 Z-coordinate {m}
>     10,                      !- Vertex 2 X-coordinate {m}
>     0,                       !- Vertex 2 Y-coordinate {m}
>     0,                       !- Vertex 2 Z-coordinate {m}
>     10,                      !- Vertex 3 X-coordinate {m}
>     8,                       !- Vertex 3 Y-coordinate {m}
>     0,                       !- Vertex 3 Z-coordinate {m}
>     0,                       !- Vertex 4 X-coordinate {m}
>     8,                       !- Vertex 4 Y-coordinate {m}
>     0,                       !- Vertex 4 Z-coordinate {m}
>     0;                       !- Vertex 5 X-coordinate {m}
> 
> Surface:HeatTransfer,
>     surface roof,            !- User Supplied Surface Name
>     ROOF,                    !- Surface Type
>     PAREDE DE BETAO,         !- Construction Name of the Surface
>     zone,                    !- Zone Name
>     ExteriorEnvironment,     !- OutsideFaceEnvironment
>     ,                        !- OutsideFaceEnvironment Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     0.5,                     !- View Factor to Ground
>     4,                       !- Number of Surface Vertex Groups -- 
> Number of (X,Y,Z) groups in this surface
>     10,                      !- Vertex 1 X-coordinate {m}
>     0,                       !- Vertex 1 Y-coordinate {m}
>     3,                       !- Vertex 1 Z-coordinate {m}
>     0,                       !- Vertex 2 X-coordinate {m}
>     0,                       !- Vertex 2 Y-coordinate {m}
>     3,                       !- Vertex 2 Z-coordinate {m}
>     0,                       !- Vertex 3 X-coordinate {m}
>     8,                       !- Vertex 3 Y-coordinate {m}
>     3,                       !- Vertex 3 Z-coordinate {m}
>     10,                      !- Vertex 4 X-coordinate {m}
>     8,                       !- Vertex 4 Y-coordinate {m}
>     3;                       !- Vertex 4 Z-coordinate {m}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SURFACE:HEATTRANSFER:SUB 
> ===========
> 
> Surface:HeatTransfer:Sub,
>     Zone Este WIN,           !- User Supplied Surface Name
>     WINDOW,                  !- Surface Type
>     VIDRO SIMPLES,           !- Construction Name of the Surface
>     surface east,            !- Base Surface Name
>     ,                        !- OutsideFaceEnvironment Object
>     0.5,                     !- View Factor to Ground
>     ,                        !- Name of shading control
>     ,                        !- WindowFrameAndDivider Name
>     1,                       !- Multiplier
>     4,                       !- Number of Surface Vertex Groups -- 
> Number of (X,Y,Z) groups in this surface
>     10,                      !- Vertex 1 X-coordinate {m}
>     3,                       !- Vertex 1 Y-coordinate {m}
>     2,                       !- Vertex 1 Z-coordinate {m}
>     10,                      !- Vertex 2 X-coordinate {m}
>     5,                       !- Vertex 2 Y-coordinate {m}
>     2,                       !- Vertex 2 Z-coordinate {m}
>     10,                      !- Vertex 3 X-coordinate {m}
>     5,                       !- Vertex 3 Y-coordinate {m}
>     1,                       !- Vertex 3 Z-coordinate {m}
>     10,                      !- Vertex 4 X-coordinate {m}
>     3,                       !- Vertex 4 Y-coordinate {m}
>     1;                       !- Vertex 4 Z-coordinate {m}
> 
> Surface:HeatTransfer:Sub,
>     Zone Oeste WIN,          !- User Supplied Surface Name
>     WINDOW,                  !- Surface Type
>     VIDRO SIMPLES,           !- Construction Name of the Surface
>     surface west,            !- Base Surface Name
>     ,                        !- OutsideFaceEnvironment Object
>     0.5,                     !- View Factor to Ground
>     ,                        !- Name of shading control
>     ,                        !- WindowFrameAndDivider Name
>     1,                       !- Multiplier
>     4,                       !- Number of Surface Vertex Groups -- 
> Number of (X,Y,Z) groups in this surface
>     0,                       !- Vertex 1 X-coordinate {m}
>     5,                       !- Vertex 1 Y-coordinate {m}
>     2,                       !- Vertex 1 Z-coordinate {m}
>     0,                       !- Vertex 2 X-coordinate {m}
>     3,                       !- Vertex 2 Y-coordinate {m}
>     2,                       !- Vertex 2 Z-coordinate {m}
>     0,                       !- Vertex 3 X-coordinate {m}
>     3,                       !- Vertex 3 Y-coordinate {m}
>     1,                       !- Vertex 3 Z-coordinate {m}
>     0,                       !- Vertex 4 X-coordinate {m}
>     5,                       !- Vertex 4 Y-coordinate {m}
>     1;                       !- Vertex 4 Z-coordinate {m}
> 
> Surface:HeatTransfer:Sub,
>     ZoneSWIN,                !- User Supplied Surface Name
>     WINDOW,                  !- Surface Type
>     VIDRO SIMPLES,           !- Construction Name of the Surface
>     surface south,           !- Base Surface Name
>     ,                        !- OutsideFaceEnvironment Object
>     0.5,                     !- View Factor to Ground
>     ,                        !- Name of shading control
>     ,                        !- WindowFrameAndDivider Name
>     1,                       !- Multiplier
>     4,                       !- Number of Surface Vertex Groups -- 
> Number of (X,Y,Z) groups in this surface
>     3.5,                     !- Vertex 1 X-coordinate {m}
>     0,                       !- Vertex 1 Y-coordinate {m}
>     2,                       !- Vertex 1 Z-coordinate {m}
>     6.5,                     !- Vertex 2 X-coordinate {m}
>     0,                       !- Vertex 2 Y-coordinate {m}
>     2,                       !- Vertex 2 Z-coordinate {m}
>     6.5,                     !- Vertex 3 X-coordinate {m}
>     0,                       !- Vertex 3 Y-coordinate {m}
>     1,                       !- Vertex 3 Z-coordinate {m}
>     3.5,                     !- Vertex 4 X-coordinate {m}
>     0,                       !- Vertex 4 Y-coordinate {m}
>     1;                       !- Vertex 4 Z-coordinate {m}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SCHEDULETYPE ===========
> 
> ScheduleType,
>     fraction,                !- ScheduleType Name
>     0,                       !- range
>     0:1;                     !- Numeric Type
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: DAYSCHEDULE ===========
> 
> DAYSCHEDULE,
>     pessoas semana,          !- Name
>     fraction,                !- ScheduleType
>     0,                       !- Hour 1
>     0,                       !- Hour 2
>     0,                       !- Hour 3
>     0,                       !- Hour 4
>     0,                       !- Hour 5
>     0.05,                    !- Hour 6
>     0.05,                    !- Hour 7
>     0.9,                     !- Hour 8
>     0.75,                    !- Hour 9
>     0.25,                    !- Hour 10
>     0.25,                    !- Hour 11
>     0.9,                     !- Hour 12
>     1,                       !- Hour 13
>     1,                       !- Hour 14
>     0.7,                     !- Hour 15
>     0.25,                    !- Hour 16
>     0.3,                     !- Hour 17
>     0.35,                    !- Hour 18
>     0.55,                    !- Hour 19
>     1,                       !- Hour 20
>     1,                       !- Hour 21
>     0.51,                    !- Hour 22
>     0.35,                    !- Hour 23
>     0.3;                     !- Hour 24
> 
> DAYSCHEDULE,
>     pessoas sabado,          !- Name
>     fraction,                !- ScheduleType
>     0,                       !- Hour 1
>     0,                       !- Hour 2
>     0,                       !- Hour 3
>     0,                       !- Hour 4
>     0,                       !- Hour 5
>     0.05,                    !- Hour 6
>     0.05,                    !- Hour 7
>     0.9,                     !- Hour 8
>     0.75,                    !- Hour 9
>     0.25,                    !- Hour 10
>     0.25,                    !- Hour 11
>     0.9,                     !- Hour 12
>     1,                       !- Hour 13
>     1,                       !- Hour 14
>     0.7,                     !- Hour 15
>     0.25,                    !- Hour 16
>     0.3,                     !- Hour 17
>     0.35,                    !- Hour 18
>     0.55,                    !- Hour 19
>     1,                       !- Hour 20
>     1,                       !- Hour 21
>     0.85,                    !- Hour 22
>     0.35,                    !- Hour 23
>     0.3;                     !- Hour 24
> 
> DAYSCHEDULE,
>     lights weekend,          !- Name
>     fraction,                !- ScheduleType
>     0,                       !- Hour 1
>     0,                       !- Hour 2
>     0,                       !- Hour 3
>     0,                       !- Hour 4
>     0,                       !- Hour 5
>     0.05,                    !- Hour 6
>     0.05,                    !- Hour 7
>     0.9,                     !- Hour 8
>     0.75,                    !- Hour 9
>     0.25,                    !- Hour 10
>     0.25,                    !- Hour 11
>     0.9,                     !- Hour 12
>     1,                       !- Hour 13
>     1,                       !- Hour 14
>     0.7,                     !- Hour 15
>     0.25,                    !- Hour 16
>     0.3,                     !- Hour 17
>     0.35,                    !- Hour 18
>     0.55,                    !- Hour 19
>     1,                       !- Hour 20
>     1,                       !- Hour 21
>     0.85,                    !- Hour 22
>     0.35,                    !- Hour 23
>     0.3;                     !- Hour 24
> 
> DAYSCHEDULE,
>     lights week,             !- Name
>     fraction,                !- ScheduleType
>     0,                       !- Hour 1
>     0,                       !- Hour 2
>     0,                       !- Hour 3
>     0,                       !- Hour 4
>     0,                       !- Hour 5
>     0.05,                    !- Hour 6
>     0.05,                    !- Hour 7
>     0.9,                     !- Hour 8
>     0.75,                    !- Hour 9
>     0.25,                    !- Hour 10
>     0.25,                    !- Hour 11
>     0.9,                     !- Hour 12
>     1,                       !- Hour 13
>     1,                       !- Hour 14
>     0.7,                     !- Hour 15
>     0.25,                    !- Hour 16
>     0.3,                     !- Hour 17
>     0.35,                    !- Hour 18
>     0.55,                    !- Hour 19
>     1,                       !- Hour 20
>     1,                       !- Hour 21
>     0.51,                    !- Hour 22
>     0.35,                    !- Hour 23
>     0.3;                     !- Hour 24
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: WEEKSCHEDULE ===========
> 
> WEEKSCHEDULE,
>     pessoas,                 !- Name
>     pessoas semana,          !- Sunday DAYSCHEDULE Name
>     pessoas semana,          !- Monday DAYSCHEDULE Name
>     pessoas semana,          !- Tuesday DAYSCHEDULE Name
>     pessoas semana,          !- Wednesday DAYSCHEDULE Name
>     pessoas semana,          !- Thursday DAYSCHEDULE Name
>     pessoas semana,          !- Friday DAYSCHEDULE Name
>     pessoas sabado,          !- Saturday DAYSCHEDULE Name
>     pessoas sabado,          !- Holiday DAYSCHEDULE Name
>     pessoas sabado,          !- SummerDesignDay DAYSCHEDULE Name
>     pessoas sabado,          !- WinterDesignDay DAYSCHEDULE Name
>     pessoas semana,          !- CustomDay1 DAYSCHEDULE Name
>     pessoas semana;          !- CustomDay2 DAYSCHEDULE Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: WEEKSCHEDULE:COMPACT 
> ===========
> 
> WEEKSCHEDULE:COMPACT,
>     pessoas,                 !- Name
>     Weekdays,                !- For #1
>     pessoas semana;          !- DayScheduleName #1
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: PEOPLE ===========
> 
> PEOPLE,
>     ocupação,                !- Name
>     zone,                    !- Zone Name
>     20,                      !- Number of People
>     pessoas semana,          !- Number of People SCHEDULE Name
>     0,                       !- Fraction Radiant
>     ,                        !- Activity level SCHEDULE Name
>     ZoneAveraged,            !- MRT Calculation Type
>     ,                        !- Surface Name/Angle Factor List Name
>     ,                        !- Work Efficiency SCHEDULE Name
>     ,                        !- Clothing Insulation SCHEDULE Name
>     ,                        !- Air Velocity SCHEDULE Name
>     Fanger,                  !- Thermal Comfort Report Type #1
>     ,                        !- Thermal Comfort Report Type #2
>     ,                        !- Thermal Comfort Report Type #3
>     autocalculate,           !- user specified sensible fraction
>     No;                      !- Enable ASHRAE 55 comfort warnings
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: CONTROLLED ZONE EQUIP 
> CONFIGURATION ===========
> 
> CONTROLLED ZONE EQUIP CONFIGURATION,
>     zone,                    !- Zone Name
>     Zone one equipment,      !- List Name: Zone Equipment
>     Zone one suply inlet,    !- Node List or Node Name: Zone Air 
> Inlet Node(s)
>     ,                        !- Node List or Node Name: Zone Air 
> Exhaust Node(s)
>     zone one Zone air node,  !- Zone Air Node Name
>     zone one Return Outlet;  !- Zone Return Air Node Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: ZONE EQUIPMENT LIST 
> ===========
> 
> ZONE EQUIPMENT LIST,
>     Zone one equipment,      !- Name
>     PURCHASED AIR,           !- KEY--Zone Equipment Type 1
>     ZONE ONE purchased air,  !- Type Name 1
>     1,                       !- Cooling Priority 1
>     1;                       !- Heating Priority 1
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: PURCHASED AIR ===========
> 
> PURCHASED AIR,
>     ZONE ONE Purchased Air,  !- Purchased Air Name
>     Zone ONE Suply inlet,    !- Zone Supply Air Node Name
>     50,                      !- Heating Supply Air Temp {C}
>     13,                      !- Cooling Supply Air Temp {C}
>     0.015,                   !- Heating Supply Air Humidity Ratio {kg-
> H2O/kg-air}
>     0.01,                    !- Cooling Supply Air Humidity Ratio {kg-
> H2O/kg-air}
>     NO LIMIT,                !- heating limit
>     autosize,                !- Maximum heating air flow rate {m3/s}
>     NO LIMIT,                !- cooling limit
>     autosize,                !- Maximum cooling air flow rate {m3/s}
>     NO OUTSIDE AIR,          !- outside air
>     autosize;                !- Outside air flow rate {m3/s}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: ZONE CONTROL:THERMOSTATIC 
> ===========
> 
> ZONE CONTROL:THERMOSTATIC,
>     ZONE ONE Thermostat,     !- Thermostat Name
>     zone,                    !- Zone Name
>     ALWAYS 4,                !- Control Type SCHEDULE Name
>     Dual Setpoint with Deadband,  !- Control Type #1
>     Office Thermostat Dual SP Control;  !- Control Type Name #1
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: DUAL SETPOINT WITH DEADBAND 
> ===========
> 
> DUAL SETPOINT WITH DEADBAND,
>     Office Thermostat Dual SP Control,  !- Name
>     ALWAYS 20,               !- Heating Setpoint Temperature SCHEDULE 
> Name
>     ALWAYS 24;               !- Cooling Setpoint Temperature SCHEDULE 
> Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: REPORT VARIABLE ===========
> 
> Report Variable,
>     *,                       !- Key_Value
>     Outdoor Dry Bulb ,       !- Variable_Name
>     hourly;                  !- Reporting_Frequency
> 
> Report Variable,
>     *,                       !- Key_Value
>     Zone/Sys Sensible Cooling Energy,  !- Variable_Name
>     hourly;                  !- Reporting_Frequency
> 
> Report Variable,
>     *,                       !- Key_Value
>     Zone/Sys Sensible Heating Energy,  !- Variable_Name
>     hourly;                  !- Reporting_Frequency
> 
> Report Variable,
>     *,                       !- Key_Value
>     Zone/Sys Air Temperature,!- Variable_Name
>     hourly;                  !- Reporting_Frequency
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: REPORT METER ===========
> 
> Report Meter,
>     PurchasedHeating:Facility ,  !- Meter_Name
>     hourly;                  !- Reporting_Frequency
> 
> Report Meter,
>     PurchasedCooling:Facility ,  !- Meter_Name
>     hourly;                  !- Reporting_Frequency
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: REPORT ===========
> 
> Report,
>     Surfaces,                !- Type_of_Report
>     DXF;                     !- Name_of_Report
> 
> Report,
>     Construction;            !- Type_of_Report
> 
> Report,
>     Variable Dictionary;     !- Type_of_Report
> 
> Report,
>     Schedules,               !- Type_of_Report
>     hourly;                  !- Name_of_Report
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/