[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] trouble with defining blinds
hi
I am trying to make cooling load calculation of a zone having two
opening one of which has exterior blind in front of it. Windows are
always open.
I can not create the right idf file. It always shows 3 severe
errors.
I don't know creating schedules so I copy schedules from example
files. Can anyone give some help to define my blinds. I will attach
my file
thank you
!-Generator IDFEditor 1.27 'current version of IDFEditor - less than
1 is a beta
!-NOTE: All comments with '!-' are ignored by the IDFEditor and are
generated automatically.
!- Use '!' comments if they need to be retained when using the
IDFEditor.
!- =========== ALL OBJECTS IN CLASS: VERSION ===========
VERSION,
1.4; !- Version Identifier
!- =========== ALL OBJECTS IN CLASS: BUILDING ===========
BUILDING,
Ofis , !- Building Name
0, !- North Axis {deg}
City, !- Terrain
0.04, !- Loads Convergence Tolerance Value
0.4, !- Temperature Convergence Tolerance
Value {deltaC}
FullInteriorAndExteriorWithReflections, !- Solar Distribution
30; !- Maximum Number of Warmup Days
!- =========== ALL OBJECTS IN CLASS: TIMESTEP IN HOUR ===========
TIMESTEP IN HOUR,
4; !- Time Step in Hour
!- =========== ALL OBJECTS IN CLASS: INSIDE CONVECTION ALGORITHM
===========
INSIDE CONVECTION ALGORITHM,
Detailed; !- Algorithm
!- =========== ALL OBJECTS IN CLASS: OUTSIDE CONVECTION ALGORITHM
===========
OUTSIDE CONVECTION ALGORITHM,
Detailed; !- Algorithm
!- =========== ALL OBJECTS IN CLASS: SOLUTION ALGORITHM
===========
SOLUTION ALGORITHM,
CTF; !- SolutionAlgo
!- =========== ALL OBJECTS IN CLASS: SHADOWING CALCULATIONS
===========
SHADOWING CALCULATIONS,
20; !- Period_for_calculations
!- =========== ALL OBJECTS IN CLASS: ZONE VOLUME CAPACITANCE
MULTIPLIER ===========
ZONE VOLUME CAPACITANCE MULTIPLIER,
1; !- Capacitance Multiplier
!- =========== ALL OBJECTS IN CLASS: RUN CONTROL ===========
RUN CONTROL,
No, !- Do the zone sizing calculation
No, !- Do the system sizing calculation
No, !- Do the plant sizing calculation
No, !- Do the design day simulations
Yes; !- Do the weather file simulation
!- =========== ALL OBJECTS IN CLASS: RUNPERIOD ===========
RunPeriod,
8, !- Begin Month
21, !- Begin Day Of Month
8, !- End Month
21, !- End Day Of Month
, !- Day Of Week For Start Day
, !- Use WeatherFile Holidays/Special Days
, !- Use WeatherFile DaylightSavingPeriod
, !- Apply Weekend Holiday Rule
, !- Use WeatherFile Rain Indicators
, !- Use WeatherFile Snow Indicators
1; !- Number of years of simulation
RunPeriod,
2, !- Begin Month
21, !- Begin Day Of Month
2, !- End Month
21, !- End Day Of Month
, !- Day Of Week For Start Day
, !- Use WeatherFile Holidays/Special Days
, !- Use WeatherFile DaylightSavingPeriod
, !- Apply Weekend Holiday Rule
, !- Use WeatherFile Rain Indicators
, !- Use WeatherFile Snow Indicators
1; !- Number of years of simulation
!- =========== ALL OBJECTS IN CLASS: LOCATION ===========
Location,
ISTANBUL_TUR Design_Conditions, !- LocationName
40.97, !- Latitude {deg}
28.82, !- Longitude {deg}
2.00, !- TimeZone {hr}
37.00; !- Elevation {m}
!- =========== ALL OBJECTS IN CLASS: DESIGNDAY ===========
DesignDay,
ISTANBUL Ann Htg Wind 99% Condns WS=>MCDB, !- DesignDayName
2, !- Maximum Dry-Bulb Temperature {C}
0.0, !- Daily Temperature Range {deltaC}
2, !- Humidity Indicating Conditions at
Max Dry-Bulb
100881., !- Barometric Pressure {Pa}
11.3, !- Wind Speed {m/s}
0, !- Wind Direction {deg}
0.00, !- Sky Clearness
0, !- Rain Indicator
0, !- Snow Indicator
21, !- Day Of Month
2, !- Month
WinterDesignDay, !- Day Type
0, !- Daylight Saving Time Indicator
Wet-Bulb; !- Humidity Indicating Type
DesignDay,
ISTANBUL Ann Clg .4% Condns DB=>MWB, !- DesignDayName
31.1, !- Maximum Dry-Bulb Temperature {C}
7.9, !- Daily Temperature Range {deltaC}
21.5, !- Humidity Indicating Conditions at
Max Dry-Bulb
100881., !- Barometric Pressure {Pa}
6, !- Wind Speed {m/s}
30, !- Wind Direction {deg}
1.00, !- Sky Clearness
0, !- Rain Indicator
0, !- Snow Indicator
21, !- Day Of Month
8, !- Month
SummerDesignDay, !- Day Type
0, !- Daylight Saving Time Indicator
Wet-Bulb; !- Humidity Indicating Type
!- =========== ALL OBJECTS IN CLASS: MATERIAL:REGULAR ===========
MATERIAL:REGULAR,
PLASTER - CEMENT SA 3 / 8 IN, !- Name
Smooth, !- Roughness
0.002, !- Thickness {m}
0.7200000, !- Conductivity {W/m-K}
1858.140, !- Density {kg/m3}
830.0000, !- Specific Heat {J/kg-K}
0.9000000, !- Absorptance:Thermal
0.7800000, !- Absorptance:Solar
0.7800000; !- Absorptance:Visible
MATERIAL:REGULAR,
BRICK - COMMON 8 IN, !- Name
Rough, !- Roughness
0.19, !- Thickness {m}
0.7200000, !- Conductivity {W/m-K}
1922.210, !- Density {kg/m3}
830.0000, !- Specific Heat {J/kg-K}
0.9000000, !- Absorptance:Thermal
0.7000000, !- Absorptance:Solar
0.7000000; !- Absorptance:Visible
MATERIAL:REGULAR,
IN76 - 2 IN PREFORMED MINERAL BOARD, !- Name
Smooth, !- Roughness
0.060000001, !- Thickness {m}
3.9999999E-02, !- Conductivity {W/m-K}
240.2700, !- Density {kg/m3}
710.0000, !- Specific Heat {J/kg-K}
0.9000000, !- Absorptance:Thermal
0.5000000, !- Absorptance:Solar
0.5000000; !- Absorptance:Visible
MATERIAL:REGULAR,
E10 - 1 IN GYP PLASTER SAND AGG, !- Name
Smooth, !- Roughness
2.0000000E-02, !- Thickness {m}
0.8200000, !- Conductivity {W/m-K}
800.9200, !- Density {kg/m3}
830.0000, !- Specific Heat {J/kg-K}
0.9000000, !- Absorptance:Thermal
0.9200000, !- Absorptance:Solar
0.9200000; !- Absorptance:Visible
MATERIAL:REGULAR,
FINISH FLOORING - TILE 1 / 16 IN, !- Name
Smooth, !- Roughness
0.005, !- Thickness {m}
0.1700000, !- Conductivity {W/m-K}
1922.210, !- Density {kg/m3}
1250.000, !- Specific Heat {J/kg-K}
0.9000000, !- Absorptance:Thermal
0.5000000, !- Absorptance:Solar
0.5000000; !- Absorptance:Visible
MATERIAL:REGULAR,
B6 - 2 IN DENSE INSULATION, !- Name
VeryRough, !- Roughness
0.08, !- Thickness {m}
3.9999999E-02, !- Conductivity {W/m-K}
91.30000, !- Density {kg/m3}
830.0000, !- Specific Heat {J/kg-K}
0.9000000, !- Absorptance:Thermal
0.5000000, !- Absorptance:Solar
0.5000000; !- Absorptance:Visible
MATERIAL:REGULAR,
C18 - 1.25 IN LIGHT WEIGHT CONCRETE, !- Name
MediumRough, !- Roughness
0.03, !- Thickness {m}
0.1200000, !- Conductivity {W/m-K}
480.5500, !- Density {kg/m3}
830.0000, !- Specific Heat {J/kg-K}
0.9000000, !- Absorptance:Thermal
0.2000000, !- Absorptance:Solar
0.2000000; !- Absorptance:Visible
MATERIAL:REGULAR,
C14 - 4 IN LW CONCRETE, !- Name
MediumRough, !- Roughness
0.1000000, !- Thickness {m}
0.1700000, !- Conductivity {W/m-K}
640.7300, !- Density {kg/m3}
830.0000, !- Specific Heat {J/kg-K}
0.9000000, !- Absorptance:Thermal
0.6500000, !- Absorptance:Solar
0.6500000; !- Absorptance:Visible
MATERIAL:REGULAR,
C5 - 4 IN HW CONCRETE, !- Name
MediumRough, !- Roughness
0.15, !- Thickness {m}
1.720000, !- Conductivity {W/m-K}
2242.580, !- Density {kg/m3}
830.0000, !- Specific Heat {J/kg-K}
0.9000000, !- Absorptance:Thermal
0.6500000, !- Absorptance:Solar
0.6500000; !- Absorptance:Visible
MATERIAL:REGULAR,
C13 - 6 IN HW CONCRETE, !- Name
MediumRough, !- Roughness
0.1500000, !- Thickness {m}
1.720000, !- Conductivity {W/m-K}
2242.580, !- Density {kg/m3}
830.0000, !- Specific Heat {J/kg-K}
0.9000000, !- Absorptance:Thermal
0.6500000, !- Absorptance:Solar
0.6500000; !- Absorptance:Visible
!- =========== ALL OBJECTS IN CLASS: MATERIAL:WINDOWGLASS
===========
MATERIAL:WINDOWGLASS,
GLASS - CLEAR PLATE 1 / 4 IN, !- Name
SpectralAverage, !- Optical Data Type
, !- Name of Window Glass Spectral Data
Set
6.0000001E-03, !- Thickness {m}
0.7750000, !- Solar Transmittance at Normal
Incidence
7.1000002E-02, !- Solar Reflectance at Normal
Incidence: Front Side
7.1000002E-02, !- Solar Reflectance at Normal
Incidence: Back Side
0.8810000, !- Visible Transmittance at Normal
Incidence
7.9999998E-02, !- Visible Reflectance at Normal
Incidence: Front Side
7.9999998E-02, !- Visible Reflectance at Normal
Incidence: Back Side
0, !- IR Transmittance at Normal Incidence
0.8400000, !- IR Hemispherical Emissivity: Front
Side
0.8400000, !- IR Hemispherical Emissivity: Back
Side
0.9000000; !- Conductivity {W/m-K}
!- =========== ALL OBJECTS IN CLASS: MATERIAL:WINDOWBLIND
===========
MATERIAL:WINDOWBLIND,
BLIND WITH LOW REFLECTIVITY SLATS, !- Name
HORIZONTAL, !- Slat orientation
0.38625, !- Slat width {m}
0.386, !- Slat separation {m}
0.00025, !- Slat thickness {m}
90, !- Slat angle {deg}
221, !- Slat conductivity {W/m-K}
0.0, !- Slat beam solar transmittance
0.2, !- Slat beam solar reflectance, front
side
0.2, !- Slat beam solar reflectance, back
side
0.0, !- Slat diffuse solar transmittance
0.2, !- Slat diffuse solar reflectance,
front side
0.2, !- Slat diffuse solar reflectance, back
side
0.0, !- Slat beam visible transmittance
0.2, !- Slat beam visible reflectance, front
side
0.2, !- Slat beam visible reflectance, back
side
0.0, !- Slat diffuse visible transmittance
0.2, !- Slat diffuse visible reflectance,
front side
0.2, !- Slat diffuse visible reflectance,
back side
0.0, !- Slat IR (thermal) hemispherical
transmittance
0.9, !- Slat IR (thermal) hemispherical
emissivity, front side
0.9, !- Slat IR (thermal) hemispherical
emissivity, back side
0.327953, !- Blind-to-glass distance {m}
0.5, !- Blind top opening multiplier
0.5, !- Blind bottom opening multiplier
0.5, !- Blind left-side opening multiplier
0.5, !- Blind right-side opening multiplier
0, !- Minimum Slat Angle {deg}
90; !- Maximum Slat Angle {deg}
!- =========== ALL OBJECTS IN CLASS: CONSTRUCTION ===========
CONSTRUCTION,
DUVAR, !- Name
PLASTER - CEMENT SA 3 / 8 IN, !- Outside Layer
IN76 - 2 IN PREFORMED MINERAL BOARD, !- Layer #2
BRICK - COMMON 8 IN, !- Layer #3
E10 - 1 IN GYP PLASTER SAND AGG; !- Layer #4
CONSTRUCTION,
ZEMÝN DOSEME, !- Name
C5 - 4 IN HW CONCRETE, !- Outside Layer
C14 - 4 IN LW CONCRETE, !- Layer #2
C18 - 1.25 IN LIGHT WEIGHT CONCRETE, !- Layer #3
B6 - 2 IN DENSE INSULATION, !- Layer #4
C18 - 1.25 IN LIGHT WEIGHT CONCRETE, !- Layer #5
FINISH FLOORING - TILE 1 / 16 IN; !- Layer #6
CONSTRUCTION,
CATI, !- Name
B6 - 2 IN DENSE INSULATION, !- Outside Layer
C13 - 6 IN HW CONCRETE, !- Layer #2
E10 - 1 IN GYP PLASTER SAND AGG; !- Layer #3
CONSTRUCTION,
ARA KAT TAVAN, !- Name
FINISH FLOORING - TILE 1 / 16 IN, !- Outside Layer
C13 - 6 IN HW CONCRETE, !- Layer #2
E10 - 1 IN GYP PLASTER SAND AGG; !- Layer #3
CONSTRUCTION,
ARA KAT DOSEME, !- Name
E10 - 1 IN GYP PLASTER SAND AGG, !- Outside Layer
C13 - 6 IN HW CONCRETE, !- Layer #2
FINISH FLOORING - TILE 1 / 16 IN; !- Layer #3
CONSTRUCTION,
DUVAR2, !- Name
E10 - 1 IN GYP PLASTER SAND AGG, !- Outside Layer
BRICK - COMMON 8 IN, !- Layer #2
E10 - 1 IN GYP PLASTER SAND AGG; !- Layer #3
CONSTRUCTION,
WIN-CON-SINGLEPANE, !- Name
GLASS - CLEAR PLATE 1 / 4 IN; !- Outside Layer
CONSTRUCTION,
WIN-CON-SINGLEPANE WITH EXTERIOR BLIND, !- Name
GLASS - CLEAR PLATE 1 / 4 IN, !- Outside Layer
BLIND WITH LOW REFLECTIVITY SLATS; !- Layer #2
!- =========== ALL OBJECTS IN CLASS: ZONE ===========
ZONE,
ofis-zone1, !- Zone Name
0, !- Relative North (to building) {deg}
0, !- X Origin {m}
0, !- Y Origin {m}
0, !- Z Origin {m}
1, !- Type
1, !- Multiplier
0, !- Ceiling Height {m}
0; !- Volume {m3}
!- =========== ALL OBJECTS IN CLASS: SURFACEGEOMETRY ===========
SurfaceGeometry,
LowerLeftCorner, !- SurfaceStartingPosition
CW, !- VertexEntry
WorldCoordinateSystem; !- CoordinateSystem
!- =========== ALL OBJECTS IN CLASS: SURFACE:HEATTRANSFER
===========
Surface:HeatTransfer,
ARKA DUVAR, !- User Supplied Surface Name
WALL, !- Surface Type
DUVAR2, !- Construction Name of the Surface
ofis-zone1, !- InsideFaceEnvironment
OtherZoneSurface, !- OutsideFaceEnvironment
ARKA DUVAR, !- OutsideFaceEnvironment Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.5, !- View Factor to Ground
4, !- Number of Surface Vertex Groups --
Number of (X,Y,Z) groups in this surface
4.56, !- Vertex 1 X-coordinate {m}
5.05, !- Vertex 1 Y-coordinate {m}
0, !- Vertex 1 Z-coordinate {m}
4.56, !- Vertex 2 X-coordinate {m}
5.05, !- Vertex 2 Y-coordinate {m}
4.05, !- Vertex 2 Z-coordinate {m}
0, !- Vertex 3 X-coordinate {m}
5.05, !- Vertex 3 Y-coordinate {m}
4.05, !- Vertex 3 Z-coordinate {m}
0, !- Vertex 4 X-coordinate {m}
5.05, !- Vertex 4 Y-coordinate {m}
0; !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
SOL YAN DUVAR, !- User Supplied Surface Name
WALL, !- Surface Type
DUVAR2, !- Construction Name of the Surface
ofis-zone1, !- InsideFaceEnvironment
OtherZoneSurface, !- OutsideFaceEnvironment
SOL YAN DUVAR, !- OutsideFaceEnvironment Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.5, !- View Factor to Ground
4, !- Number of Surface Vertex Groups --
Number of (X,Y,Z) groups in this surface
0, !- Vertex 1 X-coordinate {m}
5.05, !- Vertex 1 Y-coordinate {m}
0, !- Vertex 1 Z-coordinate {m}
0, !- Vertex 2 X-coordinate {m}
5.05, !- Vertex 2 Y-coordinate {m}
4.05, !- Vertex 2 Z-coordinate {m}
0, !- Vertex 3 X-coordinate {m}
0, !- Vertex 3 Y-coordinate {m}
4.05, !- Vertex 3 Z-coordinate {m}
0, !- Vertex 4 X-coordinate {m}
0, !- Vertex 4 Y-coordinate {m}
0; !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
SAG YAN DUVAR, !- User Supplied Surface Name
WALL, !- Surface Type
DUVAR2, !- Construction Name of the Surface
ofis-zone1, !- InsideFaceEnvironment
OtherZoneSurface, !- OutsideFaceEnvironment
SAG YAN DUVAR, !- OutsideFaceEnvironment Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.5, !- View Factor to Ground
4, !- Number of Surface Vertex Groups --
Number of (X,Y,Z) groups in this surface
4.56, !- Vertex 1 X-coordinate {m}
0, !- Vertex 1 Y-coordinate {m}
0, !- Vertex 1 Z-coordinate {m}
4.56, !- Vertex 2 X-coordinate {m}
0, !- Vertex 2 Y-coordinate {m}
4.05, !- Vertex 2 Z-coordinate {m}
4.56, !- Vertex 3 X-coordinate {m}
5.05, !- Vertex 3 Y-coordinate {m}
4.05, !- Vertex 3 Z-coordinate {m}
4.56, !- Vertex 4 X-coordinate {m}
5.05, !- Vertex 4 Y-coordinate {m}
0; !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
ON DUVAR, !- User Supplied Surface Name
WALL, !- Surface Type
DUVAR, !- Construction Name of the Surface
ofis-zone1, !- InsideFaceEnvironment
ExteriorEnvironment, !- OutsideFaceEnvironment
ON DUVAR DIS YUZEY, !- OutsideFaceEnvironment Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
0.5, !- View Factor to Ground
4, !- Number of Surface Vertex Groups --
Number of (X,Y,Z) groups in this surface
0, !- Vertex 1 X-coordinate {m}
0, !- Vertex 1 Y-coordinate {m}
0, !- Vertex 1 Z-coordinate {m}
0, !- Vertex 2 X-coordinate {m}
0, !- Vertex 2 Y-coordinate {m}
4.05, !- Vertex 2 Z-coordinate {m}
4.56, !- Vertex 3 X-coordinate {m}
0, !- Vertex 3 Y-coordinate {m}
4.05, !- Vertex 3 Z-coordinate {m}
4.56, !- Vertex 4 X-coordinate {m}
0, !- Vertex 4 Y-coordinate {m}
0; !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
DOSEME, !- User Supplied Surface Name
FLOOR, !- Surface Type
ARA KAT DOSEME, !- Construction Name of the Surface
ofis-zone1, !- InsideFaceEnvironment
OtherZoneSurface, !- OutsideFaceEnvironment
DOSEME, !- OutsideFaceEnvironment Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
1, !- View Factor to Ground
4, !- Number of Surface Vertex Groups --
Number of (X,Y,Z) groups in this surface
0, !- Vertex 1 X-coordinate {m}
5.05, !- Vertex 1 Y-coordinate {m}
0.0, !- Vertex 1 Z-coordinate {m}
0.000000, !- Vertex 2 X-coordinate {m}
0, !- Vertex 2 Y-coordinate {m}
0.0, !- Vertex 2 Z-coordinate {m}
4.56, !- Vertex 3 X-coordinate {m}
0, !- Vertex 3 Y-coordinate {m}
0.0, !- Vertex 3 Z-coordinate {m}
4.56, !- Vertex 4 X-coordinate {m}
5.05, !- Vertex 4 Y-coordinate {m}
0.0; !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
TAVAN, !- User Supplied Surface Name
CEILING, !- Surface Type
ARA KAT TAVAN, !- Construction Name of the Surface
ofis-zone1, !- InsideFaceEnvironment
OtherZoneSurface, !- OutsideFaceEnvironment
TAVAN, !- OutsideFaceEnvironment Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0, !- View Factor to Ground
4, !- Number of Surface Vertex Groups --
Number of (X,Y,Z) groups in this surface
0.000000, !- Vertex 1 X-coordinate {m}
0, !- Vertex 1 Y-coordinate {m}
4.05, !- Vertex 1 Z-coordinate {m}
0.000000, !- Vertex 2 X-coordinate {m}
5.05, !- Vertex 2 Y-coordinate {m}
4.05, !- Vertex 2 Z-coordinate {m}
4.56, !- Vertex 3 X-coordinate {m}
5.05, !- Vertex 3 Y-coordinate {m}
4.05, !- Vertex 3 Z-coordinate {m}
4.56, !- Vertex 4 X-coordinate {m}
0, !- Vertex 4 Y-coordinate {m}
4.05; !- Vertex 4 Z-coordinate {m}
!- =========== ALL OBJECTS IN CLASS: SURFACE:HEATTRANSFER:SUB
===========
Surface:HeatTransfer:Sub,
Zn001:Arkaduvar-pencere, !- User Supplied Surface Name
WINDOW, !- Surface Type
WIN-CON-SINGLEPANE, !- Construction Name of the Surface
ARKA DUVAR, !- Base Surface Name
, !- OutsideFaceEnvironment Object
0.5, !- View Factor to Ground
, !- Name of shading control
, !- WindowFrameAndDivider Name
1, !- Multiplier
4, !- Number of Surface Vertex Groups --
Number of (X,Y,Z) groups in this surface
4.32999, !- Vertex 1 X-coordinate {m}
5.05, !- Vertex 1 Y-coordinate {m}
2.175, !- Vertex 1 Z-coordinate {m}
4.32999, !- Vertex 2 X-coordinate {m}
5.05, !- Vertex 2 Y-coordinate {m}
2.675, !- Vertex 2 Z-coordinate {m}
0.23001, !- Vertex 3 X-coordinate {m}
5.05, !- Vertex 3 Y-coordinate {m}
2.675, !- Vertex 3 Z-coordinate {m}
0.23001, !- Vertex 4 X-coordinate {m}
5.05, !- Vertex 4 Y-coordinate {m}
2.175; !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer:Sub,
Zn001:Onduvarpencere, !- User Supplied Surface Name
WINDOW, !- Surface Type
WIN-CON-SINGLEPANE WITH EXTERIOR BLIND, !- Construction Name of
the Surface
ON DUVAR, !- Base Surface Name
, !- OutsideFaceEnvironment Object
0.5000000, !- View Factor to Ground
INCIDENT SOLAR ON BLIND, !- Name of shading control
, !- WindowFrameAndDivider Name
1.0, !- Multiplier
4, !- Number of Surface Vertex Groups --
Number of (X,Y,Z) groups in this surface
0.548000, !- Vertex 1 X-coordinate {m}
0, !- Vertex 1 Y-coordinate {m}
2.5000, !- Vertex 1 Z-coordinate {m}
0.548000, !- Vertex 2 X-coordinate {m}
0, !- Vertex 2 Y-coordinate {m}
0.5000, !- Vertex 2 Z-coordinate {m}
5.548000, !- Vertex 3 X-coordinate {m}
0, !- Vertex 3 Y-coordinate {m}
0.5000, !- Vertex 3 Z-coordinate {m}
5.548000, !- Vertex 4 X-coordinate {m}
0, !- Vertex 4 Y-coordinate {m}
2.5000; !- Vertex 4 Z-coordinate {m}
!- =========== ALL OBJECTS IN CLASS: WINDOWSHADINGCONTROL
===========
WindowShadingControl,
INCIDENT SOLAR ON BLIND, !- User Supplied Shading Control Name
ExteriorBlind, !- Shading Type
WIN-CON-SINGLEPANE WITH EXTERIOR BLIND, !- Name of construction
with shading
AlwaysOn, !- Shading Control Type
ShadeTransSch, !- Schedule Name
20, !- SetPoint {W/m2, W or deg C}
Yes, !- Shading Control Is Scheduled
NO, !- Glare Control Is Active
BLIND WITH LOW REFLECTIVITY SLATS, !- Material Name of Shading
Device
ScheduledSlatAngle, !- Type of Slat Angle Control for Blinds
90; !- Slat Angle Schedule Name
!- =========== ALL OBJECTS IN CLASS: UCSD CROSS VENTILATION MODEL
CONTROLS ===========
UCSD CROSS VENTILATION MODEL CONTROLS,
ofis-zone1, !- Zone Name
WindowVentSched, !- Gain Distribution Schedule
JET; !- Airflow region used for thermal
comfort evaluation
!- =========== ALL OBJECTS IN CLASS: SCHEDULETYPE ===========
ScheduleType,
Control Type, !- ScheduleType Name
0:4, !- range
DISCRETE; !- Numeric Type
ScheduleType,
On/Off, !- ScheduleType Name
0:1, !- range
DISCRETE; !- Numeric Type
ScheduleType,
FlowRate, !- ScheduleType Name
0.0:10, !- range
CONTINUOUS; !- Numeric Type
ScheduleType,
Any Number; !- ScheduleType Name
ScheduleType,
Fraction, !- ScheduleType Name
0.0 : 1.0, !- range
CONTINUOUS; !- Numeric Type
ScheduleType,
Temperature, !- ScheduleType Name
-60:200, !- range
CONTINUOUS; !- Numeric Type
!- =========== ALL OBJECTS IN CLASS: SCHEDULE:COMPACT ===========
SCHEDULE:COMPACT,
ShadeTransSch, !- Name
Fraction, !- ScheduleType
Through: 12/31, !- Complex Field #1
For: AllDays, !- Complex Field #2
Until: 24:00, !- Complex Field #3
0.0; !- Complex Field #4
SCHEDULE:COMPACT,
WindowVentSched, !- Name
Any Number, !- ScheduleType
Through: 3/31, !- Complex Field #1
For: AllDays, !- Complex Field #2
Until: 24:00, !- Complex Field #3
25.55, !- Complex Field #4
Through: 9/30, !- Complex Field #5
For: AllDays, !- Complex Field #6
Until: 24:00, !- Complex Field #7
21.11, !- Complex Field #8
Through: 12/31, !- Complex Field #9
For: AllDays, !- Complex Field #10
Until: 24:00, !- Complex Field #11
25.55; !- Complex Field #12
!- =========== ALL OBJECTS IN CLASS: NODE LIST ===========
NODE LIST,
Zone1Inlets, !- Node List Name
NODE_1; !- Node_ID_1
!- =========== ALL OBJECTS IN CLASS: CONTROLLED ZONE EQUIP
CONFIGURATION ===========
CONTROLLED ZONE EQUIP CONFIGURATION,
ofis-zone1, !- Zone Name
Zone1Equipment, !- List Name: Zone Equipment
Zone1Inlets, !- Node List or Node Name: Zone Air
Inlet Node(s)
, !- Node List or Node Name: Zone Air
Exhaust Node(s)
NODE_4, !- Zone Air Node Name
NODE_5; !- Zone Return Air Node Name
!- =========== ALL OBJECTS IN CLASS: ZONE EQUIPMENT LIST
===========
ZONE EQUIPMENT LIST,
Zone1Equipment, !- Name
PURCHASED AIR, !- KEY--Zone Equipment Type 1
Zone1Air, !- Type Name 1
1, !- Cooling Priority 1
1; !- Heating Priority 1
!- =========== ALL OBJECTS IN CLASS: PURCHASED AIR ===========
PURCHASED AIR,
Zone1Air, !- Purchased Air Name
NODE_1, !- Zone Supply Air Node Name
50, !- Heating Supply Air Temp {C}
13, !- Cooling Supply Air Temp {C}
0.015, !- Heating Supply Air Humidity Ratio
{kg-H2O/kg-air}
0.010, !- Cooling Supply Air Humidity Ratio
{kg-H2O/kg-air}
NO LIMIT, !- heating limit
autosize, !- Maximum heating air flow rate {m3/s}
NO LIMIT, !- cooling limit
autosize, !- Maximum cooling air flow rate {m3/s}
NO OUTSIDE AIR, !- outside air
autosize; !- Outside air flow rate {m3/s}
!- =========== ALL OBJECTS IN CLASS: ZONE CONTROL:THERMOSTATIC
===========
ZONE CONTROL:THERMOSTATIC,
Zone 1 Thermostat, !- Thermostat Name
RESISTIVE ZONE, !- Zone Name
Zone Control Type Sched, !- Control Type SCHEDULE Name
SINGLE HEATING SETPOINT, !- Control Type #1
Heating Setpoint with SB,!- Control Type Name #1
SINGLE COOLING SETPOINT, !- Control Type #2
Cooling Setpoint with SB;!- Control Type Name #2
!- =========== ALL OBJECTS IN CLASS: SINGLE HEATING SETPOINT
===========
SINGLE HEATING SETPOINT,
Heating Setpoint with SB,!- Name
Heating Setpoints; !- Setpoint Temperature SCHEDULE Name
!- =========== ALL OBJECTS IN CLASS: SINGLE COOLING SETPOINT
===========
SINGLE COOLING SETPOINT,
Cooling Setpoint with SB,!- Name
Cooling Setpoints; !- Setpoint Temperature SCHEDULE Name
!- =========== ALL OBJECTS IN CLASS: REPORT VARIABLE ===========
Report Variable,
*, !- Key_Value
Wind Speed, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Wind Direction, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Zone Mean Air Temperature, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
AirflowNetwork Zone Infiltration Volume, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Outdoor Dry Bulb, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Zone Mean Air Temperature, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Zone Mean Radiant Temperature, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
Zn001:Wall001:Win001, !- Key_Value
Surface Ext Solar Incident, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Fraction of Time Shading Device Is On, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Window Blind Slat Angle, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Window Transmitted Solar,!- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Window Solar Absorbed:All Glass Layers, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Window Heat Gain, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Window Heat Loss, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Window Solar Absorbed:Shading Device, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Window System Solar Transmittance, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Window System Solar Reflectance, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Window System Solar Absorptance, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Zone/Sys Sensible Cooling Rate, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Zone/Sys Sensible Heating Rate, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Zone/Sys Air Temperature,!- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
Zone Air Humidity Ratio, !- Variable_Name
timestep; !- Reporting_Frequency
Report Variable,
*, !- Key_Value
FangerPMV, !- Variable_Name
timestep; !- Reporting_Frequency
!- =========== ALL OBJECTS IN CLASS: REPORT METERFILEONLY
===========
Report MeterFileOnly,
Electricity:Facility, !- Meter_Name
monthly; !- Reporting_Frequency
Report MeterFileOnly,
Electricity:Building, !- Meter_Name
monthly; !- Reporting_Frequency
Report MeterFileOnly,
InteriorLights:Electricity, !- Meter_Name
monthly; !- Reporting_Frequency
Report MeterFileOnly,
Electricity:Facility, !- Meter_Name
runperiod; !- Reporting_Frequency
Report MeterFileOnly,
Electricity:Building, !- Meter_Name
runperiod; !- Reporting_Frequency
Report MeterFileOnly,
InteriorLights:Electricity, !- Meter_Name
runperiod; !- Reporting_Frequency
!- =========== ALL OBJECTS IN CLASS: REPORT ===========
Report,
Variable Dictionary; !- Type_of_Report
Report,
surfaces, !- Type_of_Report
dxf; !- Name_of_Report
Report,
construction; !- Type_of_Report
!- =========== ALL OBJECTS IN CLASS: REPORT:TABLE:MONTHLY
===========
Report:Table:Monthly,
Zone Cooling Summary, !- Name
, !- DigitsAfterDecimal
Zone/Sys Sensible Cooling Energy, !- VariableOrMeterName01
SumOrAverage, !- AggregationType01
Zone/Sys Sensible Cooling Rate, !- VariableOrMeterName02
Maximum, !- AggregationType02
Outdoor Dry Bulb, !- VariableOrMeterName03
ValueWhenMaxMin, !- AggregationType03
Outdoor Wet Bulb, !- VariableOrMeterName04
ValueWhenMaxMin, !- AggregationType04
Zone Total Internal Latent Gain, !- VariableOrMeterName05
SumOrAverage, !- AggregationType05
Zone Total Internal Latent Gain, !- VariableOrMeterName06
Maximum, !- AggregationType06
Outdoor Dry Bulb, !- VariableOrMeterName07
ValueWhenMaxMin, !- AggregationType07
Outdoor Wet Bulb, !- VariableOrMeterName08
ValueWhenMaxMin; !- AggregationType08
Report:Table:Monthly,
Space Gains, !- Name
, !- DigitsAfterDecimal
Zone People Total Heat Gain, !- VariableOrMeterName01
SumOrAverage, !- AggregationType01
Zone Lights Total Heat Gain, !- VariableOrMeterName02
SumOrAverage, !- AggregationType02
Zone Electric Equipment Total Heat Gain, !-
VariableOrMeterName03
SumOrAverage, !- AggregationType03
Zone Gas Equipment Total Heat Gain, !- VariableOrMeterName04
SumOrAverage, !- AggregationType04
Zone Hot Water Equipment Total Heat Gain, !-
VariableOrMeterName05
SumOrAverage, !- AggregationType05
Zone Steam Equipment Total Heat Gain, !- VariableOrMeterName06
SumOrAverage, !- AggregationType06
Zone Other Equipment Total Heat Gain, !- VariableOrMeterName07
SumOrAverage, !- AggregationType07
Zone Infiltration Sensible Heat Gain, !- VariableOrMeterName08
SumOrAverage, !- AggregationType08
Zone Infiltration Sensible Heat Loss, !- VariableOrMeterName09
SumOrAverage; !- AggregationType09
Report:Table:Monthly,
Peak Space Gains, !- Name
, !- DigitsAfterDecimal
Zone People Total Heat Gain, !- VariableOrMeterName01
Maximum, !- AggregationType01
Zone Lights Total Heat Gain, !- VariableOrMeterName02
Maximum, !- AggregationType02
Zone Electric Equipment Total Heat Gain, !-
VariableOrMeterName03
Maximum, !- AggregationType03
Zone Gas Equipment Total Heat Gain, !- VariableOrMeterName04
Maximum, !- AggregationType04
Zone Hot Water Equipment Total Heat Gain, !-
VariableOrMeterName05
Maximum, !- AggregationType05
Zone Steam Equipment Total Heat Gain, !- VariableOrMeterName06
Maximum, !- AggregationType06
Zone Other Equipment Total Heat Gain, !- VariableOrMeterName07
Maximum, !- AggregationType07
Zone Infiltration Sensible Heat Gain, !- VariableOrMeterName08
Maximum, !- AggregationType08
Zone Infiltration Sensible Heat Loss, !- VariableOrMeterName09
Maximum; !- AggregationType09
Report:Table:Monthly,
Space Gain Components at Cooling Peak, !- Name
, !- DigitsAfterDecimal
Zone/Sys Sensible Cooling Rate, !- VariableOrMeterName01
Maximum, !- AggregationType01
Zone People Total Heat Gain, !- VariableOrMeterName02
ValueWhenMaxMin, !- AggregationType02
Zone Lights Total Heat Gain, !- VariableOrMeterName03
ValueWhenMaxMin, !- AggregationType03
Zone Electric Equipment Total Heat Gain, !-
VariableOrMeterName04
ValueWhenMaxMin, !- AggregationType04
Zone Gas Equipment Total Heat Gain, !- VariableOrMeterName05
ValueWhenMaxMin, !- AggregationType05
Zone Hot Water Equipment Total Heat Gain, !-
VariableOrMeterName06
ValueWhenMaxMin, !- AggregationType06
Zone Steam Equipment Total Heat Gain, !- VariableOrMeterName07
ValueWhenMaxMin, !- AggregationType07
Zone Other Equipment Total Heat Gain, !- VariableOrMeterName08
ValueWhenMaxMin, !- AggregationType08
Zone Infiltration Sensible Heat Gain, !- VariableOrMeterName09
ValueWhenMaxMin, !- AggregationType09
Zone Infiltration Sensible Heat Loss, !- VariableOrMeterName10
ValueWhenMaxMin; !- AggregationType10
Report:Table:Monthly,
Setpoints Not Met With Temperatures, !- Name
2, !- DigitsAfterDecimal
Time Heating Setpoint Not Met, !- VariableOrMeterName01
HoursNonZero, !- AggregationType01
Zone Mean Air Temperature, !- VariableOrMeterName02
SumOrAverageDuringHoursShown, !- AggregationType02
Time Heating Setpoint Not Met While Occupied, !-
VariableOrMeterName03
HoursNonZero, !- AggregationType03
Zone Mean Air Temperature, !- VariableOrMeterName04
SumOrAverageDuringHoursShown, !- AggregationType04
Time Cooling Setpoint Not Met, !- VariableOrMeterName05
HoursNonZero, !- AggregationType05
Zone Mean Air Temperature, !- VariableOrMeterName06
SumOrAverageDuringHoursShown, !- AggregationType06
Time Cooling Setpoint Not Met While Occupied, !-
VariableOrMeterName07
HoursNonZero, !- AggregationType07
Zone Mean Air Temperature, !- VariableOrMeterName08
SumOrAverageDuringHoursShown; !- AggregationType08
Report:Table:Monthly,
Comfort Report - Simple 55, !- Name
2, !- DigitsAfterDecimal
Time Not Comfortable Summer Clothes, !- VariableOrMeterName01
HoursNonZero, !- AggregationType01
Zone Mean Air Temperature, !- VariableOrMeterName02
SumOrAverageDuringHoursShown, !- AggregationType02
Time Not Comfortable Winter Clothes, !- VariableOrMeterName03
HoursNonZero, !- AggregationType03
Zone Mean Air Temperature, !- VariableOrMeterName04
SumOrAverageDuringHoursShown, !- AggregationType04
Time Not Comfortable Summer Or Winter Clothes, !-
VariableOrMeterName05
HoursNonZero, !- AggregationType05
Zone Mean Air Temperature, !- VariableOrMeterName06
SumOrAverageDuringHoursShown; !- AggregationType06
Report:Table:Monthly,
Zone Temperature Oscillation Report, !- Name
, !- DigitsAfterDecimal
Time Zone Temperature Oscillating, !- VariableOrMeterName01
HoursNonZero, !- AggregationType01
Zone People Number Of Occupants, !- VariableOrMeterName02
SumOrAverageDuringHoursShown; !- AggregationType02
Report:Table:Monthly,
Zone Cooling Summary, !- Name
, !- DigitsAfterDecimal
Zone/Sys Sensible Cooling Energy, !- VariableOrMeterName01
SumOrAverage, !- AggregationType01
Zone/Sys Sensible Cooling Rate, !- VariableOrMeterName02
Maximum, !- AggregationType02
Outdoor Dry Bulb, !- VariableOrMeterName03
ValueWhenMaxMin, !- AggregationType03
Outdoor Wet Bulb, !- VariableOrMeterName04
ValueWhenMaxMin, !- AggregationType04
Zone Total Internal Latent Gain, !- VariableOrMeterName05
SumOrAverage, !- AggregationType05
Zone Total Internal Latent Gain, !- VariableOrMeterName06
Maximum, !- AggregationType06
Outdoor Dry Bulb, !- VariableOrMeterName07
ValueWhenMaxMin, !- AggregationType07
Outdoor Wet Bulb, !- VariableOrMeterName08
ValueWhenMaxMin; !- AggregationType08
Report:Table:Monthly,
Space Gains, !- Name
, !- DigitsAfterDecimal
Zone People Total Heat Gain, !- VariableOrMeterName01
SumOrAverage, !- AggregationType01
Zone Lights Total Heat Gain, !- VariableOrMeterName02
SumOrAverage, !- AggregationType02
Zone Electric Equipment Total Heat Gain, !-
VariableOrMeterName03
SumOrAverage, !- AggregationType03
Zone Gas Equipment Total Heat Gain, !- VariableOrMeterName04
SumOrAverage, !- AggregationType04
Zone Hot Water Equipment Total Heat Gain, !-
VariableOrMeterName05
SumOrAverage, !- AggregationType05
Zone Steam Equipment Total Heat Gain, !- VariableOrMeterName06
SumOrAverage, !- AggregationType06
Zone Other Equipment Total Heat Gain, !- VariableOrMeterName07
SumOrAverage, !- AggregationType07
Zone Infiltration Sensible Heat Gain, !- VariableOrMeterName08
SumOrAverage, !- AggregationType08
Zone Infiltration Sensible Heat Loss, !- VariableOrMeterName09
SumOrAverage; !- AggregationType09
Report:Table:Monthly,
Peak Space Gains, !- Name
, !- DigitsAfterDecimal
Zone People Total Heat Gain, !- VariableOrMeterName01
Maximum, !- AggregationType01
Zone Lights Total Heat Gain, !- VariableOrMeterName02
Maximum, !- AggregationType02
Zone Electric Equipment Total Heat Gain, !-
VariableOrMeterName03
Maximum, !- AggregationType03
Zone Gas Equipment Total Heat Gain, !- VariableOrMeterName04
Maximum, !- AggregationType04
Zone Hot Water Equipment Total Heat Gain, !-
VariableOrMeterName05
Maximum, !- AggregationType05
Zone Steam Equipment Total Heat Gain, !- VariableOrMeterName06
Maximum, !- AggregationType06
Zone Other Equipment Total Heat Gain, !- VariableOrMeterName07
Maximum, !- AggregationType07
Zone Infiltration Sensible Heat Gain, !- VariableOrMeterName08
Maximum, !- AggregationType08
Zone Infiltration Sensible Heat Loss, !- VariableOrMeterName09
Maximum; !- AggregationType09
Report:Table:Monthly,
Space Gain Components at Cooling Peak, !- Name
, !- DigitsAfterDecimal
Zone/Sys Sensible Cooling Rate, !- VariableOrMeterName01
Maximum, !- AggregationType01
Zone People Total Heat Gain, !- VariableOrMeterName02
ValueWhenMaxMin, !- AggregationType02
Zone Lights Total Heat Gain, !- VariableOrMeterName03
ValueWhenMaxMin, !- AggregationType03
Zone Electric Equipment Total Heat Gain, !-
VariableOrMeterName04
ValueWhenMaxMin, !- AggregationType04
Zone Gas Equipment Total Heat Gain, !- VariableOrMeterName05
ValueWhenMaxMin, !- AggregationType05
Zone Hot Water Equipment Total Heat Gain, !-
VariableOrMeterName06
ValueWhenMaxMin, !- AggregationType06
Zone Steam Equipment Total Heat Gain, !- VariableOrMeterName07
ValueWhenMaxMin, !- AggregationType07
Zone Other Equipment Total Heat Gain, !- VariableOrMeterName08
ValueWhenMaxMin, !- AggregationType08
Zone Infiltration Sensible Heat Gain, !- VariableOrMeterName09
ValueWhenMaxMin, !- AggregationType09
Zone Infiltration Sensible Heat Loss, !- VariableOrMeterName10
ValueWhenMaxMin; !- AggregationType10
Report:Table:Monthly,
Setpoints Not Met With Temperatures, !- Name
2, !- DigitsAfterDecimal
Time Heating Setpoint Not Met, !- VariableOrMeterName01
HoursNonZero, !- AggregationType01
Zone Mean Air Temperature, !- VariableOrMeterName02
SumOrAverageDuringHoursShown, !- AggregationType02
Time Heating Setpoint Not Met While Occupied, !-
VariableOrMeterName03
HoursNonZero, !- AggregationType03
Zone Mean Air Temperature, !- VariableOrMeterName04
SumOrAverageDuringHoursShown, !- AggregationType04
Time Cooling Setpoint Not Met, !- VariableOrMeterName05
HoursNonZero, !- AggregationType05
Zone Mean Air Temperature, !- VariableOrMeterName06
SumOrAverageDuringHoursShown, !- AggregationType06
Time Cooling Setpoint Not Met While Occupied, !-
VariableOrMeterName07
HoursNonZero, !- AggregationType07
Zone Mean Air Temperature, !- VariableOrMeterName08
SumOrAverageDuringHoursShown; !- AggregationType08
Report:Table:Monthly,
Comfort Report - Simple 55, !- Name
2, !- DigitsAfterDecimal
Time Not Comfortable Summer Clothes, !- VariableOrMeterName01
HoursNonZero, !- AggregationType01
Zone Mean Air Temperature, !- VariableOrMeterName02
SumOrAverageDuringHoursShown, !- AggregationType02
Time Not Comfortable Winter Clothes, !- VariableOrMeterName03
HoursNonZero, !- AggregationType03
Zone Mean Air Temperature, !- VariableOrMeterName04
SumOrAverageDuringHoursShown, !- AggregationType04
Time Not Comfortable Summer Or Winter Clothes, !-
VariableOrMeterName05
HoursNonZero, !- AggregationType05
Zone Mean Air Temperature, !- VariableOrMeterName06
SumOrAverageDuringHoursShown; !- AggregationType06
Report:Table:Monthly,
Zone Temperature Oscillation Report, !- Name
, !- DigitsAfterDecimal
Time Zone Temperature Oscillating, !- VariableOrMeterName01
HoursNonZero, !- AggregationType01
Zone People Number Of Occupants, !- VariableOrMeterName02
SumOrAverageDuringHoursShown; !- AggregationType02
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/