Re: [EnergyPlus_Support] curved blinds
It would not be exact, but you could use the "slat thickness" to model
the curvature of the blind slat. In this case the slat thickness could
be found by laying the slat on a flat surface and measure the distance
from the slat midpoint to the flat surface. Refer to the
InputOutputReference document for a complete discussion of
Material:WindowBlind.
solarmech wrote:
>
> Hi everyone!
>
> Is there a way to model curved blinds with E+?
> Page 98 of the input-output Reference manual (4/9/07) states "Slat
> curvature, if present, is ignored".
> Any ideas how to model the curve, sideways?
>
> thank you.
>
> My healing wishes from Greece
>
> Ch. V.
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/