[EnergyPlus_Support] Re: Node Connection Errors
I would not know what to make because the settings of the zone
43501 is the same ones of the others.
You have some suggestion?
Thanks in advance payment!!!
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie <linda@...> wrote:
>
> You are getting the Node connection errors as a result of your other
> errors, specifically:
>
> ** Severe ** Air Primary Loop 43501 AHU has no air flow
> ** ~~~ ** Check flow rate inputs for components in this air loop and,
> ** ~~~ ** if autosized, check ZONE SIZING and SYSTEM SIZING
> and related inputs.
> ** Fatal ** Previous condition causes termination.
>
>
> Linda
>
> EnergyPlus WebSite: http://www.energyplus.gov
> Owner: EnergyPlus_Support list
> Member: EnergyPlus Development Team
>
>
>
> [Non-text portions of this message have been removed]
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/