For the Chiller EIR input, below is the equation to calculate the EIR
based on the Part Load Ratio. I am modeling air cooled chillers.
What is "r1" and "dT" refer to? I'm assuming that "r1" is the actual
cooling load divided by the maximum cooling capacity based on the
condenser temperature (ambient dry bulb temperature) and "dT" is the
difference between the chilled water supply and return temperature
(which is 10 with 44 supply and 54 return). I'm getting numbers that
are extremely low especially for low PLRs. I would think that the
maximum efficiency would be around 40-60% PLR but am not seeing this.
BI-QUADRATIC-RATIO&dT The curve is bi-quadratic in 2 independent
variables. It has the form
f(r1,dT) = c1 + c2*r1 + c3*r12 + c4*dT
+ c5*dT2 + c6*r1*dT,
where c1, c2, c3, c4, c5, and c6 are
coefficients. R1 is a dimensionless variable. dT is a variable with
units of delta temperature.
Ian
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/