Re: [EnergyPlus_Support] inputs for EIR performance cureve
Where is this equation from? I am not finding it in the documentation.
CHILLER:ELECTRIC:EIR does not use delta temperature in its equations.
Mike
On 10 Sep 2007 at 22:59, Ian Doebber wrote:
> For the Chiller EIR input, below is the equation to calculate the EIR
> based on the Part Load Ratio. I am modeling air cooled chillers.
>
>
>
> What is "r1" and "dT" refer to? I'm assuming that "r1" is the actual
> cooling load divided by the maximum cooling capacity based on the
> condenser temperature (ambient dry bulb temperature) and "dT" is the
> difference between the chilled water supply and return temperature
> (which is 10 with 44 supply and 54 return). I'm getting numbers that
> are extremely low especially for low PLRs. I would think that the
> maximum efficiency would be around 40-60% PLR but am not seeing this.
>
>
>
> BI-QUADRATIC-RATIO&dT The curve is bi-quadratic in 2 independent
> variables. It has the form
>
>
>
> f(r1,dT) = c1 + c2*r1 + c3*r12 + c4*dT
> + c5*dT2 + c6*r1*dT,
>
>
>
> where c1, c2, c3, c4, c5, and c6 are
> coefficients. R1 is a dimensionless variable. dT is a variable with
> units of delta temperature.
>
>
>
> Ian
>
> ____________________________________________________________
> Electronic mail messages entering and leaving Arup business
> systems are scanned for acceptability of content and viruses
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/