Re: [EnergyPlus_Support] VAV:NoReheat and indoor air quality
The VENTILATION:MECHANICAL object can provide outside air based on a
ventilation rate per occupant or ventilation rate per floor area. See
documentation for Controller:Outside Air and Demand Controlled
Ventilation in the Engineering Reference. You will find the input
requirements for Controller:Outside Air and Ventilation:Mechanical in
the Input Output Reference. You can also review the example file named
HeatPumpSimpleDCV.idf.
alexandrevarela2000 wrote:
>
> Dear all,
>
> I need to use a VAV system and to ensure a variable minimum outside
> air flow rate. The outside air flow rate is to be varied according to
> the number of people in the zone.
>
> The VAV model only allows to have a fixed outside air flow fraction.
> Is it possible to have this minimum outside air fraction changing over
> time, with the number of people in the zone?
>
> Thanks. Best regards,
> Alexandre
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/