Re: [EnergyPlus_Support] Ground Temperatures and
If the OutsideFaceEnvironment = Ground, then the surface is in direct contact
with the soil, and "View Factor to Ground" does not apply, so the value entered
does not matter. I suspect this is why the two examples do not agree, yet are
both "correct" simply because the value is not relevant.
If the OutsideFaceEnvironment = ExteriorEnvironment, then "View Factor to
Ground" would be 1.0 for a horizontal exposed floor which is facing downward.
Mike
On 20 Sep 2007 at 17:12, Daniel Solís wrote:
> First, what´s a ground view factor? I ask because the tutorial online
> says the floor has a GVF of 0, but an example in the program says it
> should be 1. So? (both were examples of a box-shaped room).
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/