[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] how to input the width of strip of under slab insulation
The insulation width is 2*APRatio.
The dimensions of the slab are reported in the *.out output file from the Slab
program. Look at the example files in
\EnergyPlusV2-0-0\PreProcess\GrndTempCalc\
SlabExample.idf and SlabExample.out
The input for APRatio in this example is 10.
In SlabExample.out:
FLOOR AREA (M**2): 1600.
PERIMETER (M): 160.0
MIN X (M): -20.00 MAX X: 20.00
MIN Y (M): -20.00 MAX Y: 20.00
The equivalent slab is always a square, in this case, the length of each side
is 40m (X=-20 to X=+20). Area=40*40=1600, and Perimeter=40*4=160
Area/Perimeter = 1600/160 = 10
So, for a fully insulated slab, the perimeter insulation width would be 20, or
2*APRatio.
This can also be shown algebraically:
A=L*L, P=4*L, APRatio=A/P=(L*L)/(4*L)=L/4
So, full insulation width is L/2 = 2*APRatio
We will add some explanation of this to the documentation.
Mike
On 26 Sep 2007 at 16:49, wanglei wrote:
> Thank you very much for your reply I think you are right, the width is the value
> from the perimeter of the use to interior. If I want all the slab to be
> insulated,the width value should be half of the slab length,but there aren't
> slab length field in the input file,there only is a ratio of Area/perimeter
> field.So I think there should be a slab length field, or there are default
> length in the calculated program. ÔÚ2007-09-26£¬"Edwin Lee"
> <leeed2001@xxxxxxxxx> дµÀ£º I believe this will simulate 0.61m along the entire
> perimeter of the house. I think this will place the outer edge of the insulation
> at the very perimeter of the house, then 0.61m toward the interior of the plan
> area. I hope this helps. I am not sure if you have looked at the documentation.
> If not, check out the AuxillaryPrograms.pdf within the 'documentation' subfolder
> of the main install folder. On page 81 of the pdf there is a nice drawing of the
> insulation configuration. Good Luck ----- Original Message ---- From: wanglei
> <wangleihello@xxxxxxx> To:EnergyPlus_Support@xxxxxxxxxxxxxxx Sent: Tuesday,
> September 25, 2007 7:44:36 PM Subject: [EnergyPlus_Support] how to input the
> width of strip of under slab insulation Dear Edwin You are right, I can input
> the width in that field, but I don't know which value I should Input. In your
> example, the value is 0.61m. This value means which region is insulated ? I
> don't know how to define the width value? Could you tell me? Thanks very much
> ÔÚ2007-09-25£¬"Edwin Lee" <leeed2001@xxxxxxxxx> дµÀ£º I think the width is
> there, in the insulation section. Here's what one of my previous files looks
> like: !- =========== ALL OBJECTS IN CLASS: INSULATION =========== Insulation,
> 1.056, !- RINS: R value of under slab insulation {m2-K/W} 0.61, !- DINS: Width
> of strip of under slab insulation {m} 0, !- RVINS: R value of vertical
> insulation {m2-K/W} 0, !- ZVINS: Depth of vertical insulation {m} 0; !- IVINS:
> Flag: Is there vertical insulation This is for 2 feet of horizontal insulation
> around the perimeter. Edwin ----- Original Message ---- From: wanglei
> <wangleihello@xxxxxxx> To:EnergyPlus_Support@xxxxxxxxxxxxxxx Sent: Monday,
> September 24, 2007 10:53:15 PM Subject: [EnergyPlus_Support] how to input the
> width of strip of under slab insulation Dear all I'm using the slab program to
> calculate the ground temperature. when I inputs the vaule of the width of strip
> of under slab insulation, I doesn't know how to input the width of under slab
> insulation. My studing model is low floor radiator heating system, the whole
> under floor is insulated. There only are SlABDEPTH(Thickness of slab on
> grade),CLEARANGE( Distance from edge of slab to domain edge),ZCLEARANGE( Depth
> of range below slab),pRatio( The area to perimeter ratio for this slab ) objects
> in the input file. There aren't the width and leght of slab in this input file.
> So I doesn't know how to input the width of strip of under slab insulation
> Thanks for you attention Lei Wang [Non-text portions of this message have been
> removed] <!-- #ygrp-mkp{ border:1px solid #d8d8d8;font-family:Arial;margin:14px
> 0px;padding:0px 14px;} #ygrp-mkp hr{ border:1px solid #d8d8d8;} #ygrp-mkp #hd{
> color:#628c2a;font-size:85%;font-weight:bold;line-height:122%;margin:10px 0px;}
> #ygrp-mkp #ads{ margin-bottom:10px;} #ygrp-mkp .ad{ padding:0 0;} #ygrp-mkp .ad
> a{ color:#0000ff;text-decoration:none;} --> <!-- #ygrp-sponsor #ygrp-lc{
> font-family:Arial;} #ygrp-sponsor #ygrp-lc #hd{ margin:10px
> 0px;font-weight:bold;font-size:78%;line-height:122%;} #ygrp-sponsor #ygrp-lc
> .ad{ margin-bottom:10px;padding:0 0;} --> <!-- #ygrp-mlmsg
> {font-size:13px;font-family:arial, helvetica, clean, sans-serif;} #ygrp-mlmsg
> table {font-size:inherit;font:100%;} #ygrp-mlmsg select, input, textarea
> {font:99% arial, helvetica, clean, sans-serif;} #ygrp-mlmsg pre, code {font:115%
> monospace;} #ygrp-mlmsg * {line-height:1.22em;} #ygrp-text{ font-family:Georgia;
> } #ygrp-text p{ margin:0 0 1em 0;} #ygrp-tpmsgs{ font-family:Arial; clear:both;}
> #ygrp-vitnav{ padding-top:10px;font-family:Verdana;font-size:77%;margin:0;}
> #ygrp-vitnav a{ padding:0 1px;} #ygrp-actbar{ clear:both;margin:25px
> 0;white-space:nowrap;color:#666;text-align:right;} #ygrp-actbar .left{
> float:left;white-space:nowrap;} .bld{font-weight:bold;} #ygrp-grft{
> font-family:Verdana;font-size:77%;padding:15px 0;} #ygrp-ft{
> font-family:verdana;font-size:77%;border-top:1px solid #666; padding:5px 0; }
> #ygrp-mlmsg #logo{ padding-bottom:10px;} #ygrp-vital{
> background-color:#e0ecee;margin-bottom:20px;padding:2px 0 8px 8px;} #ygrp-vital
> #vithd{
> font-size:77%;font-family:Verdana;font-weight:bold;color:#333;text-transform:upp
> ercase;} #ygrp-vital ul{ padding:0;margin:2px 0;} #ygrp-vital ul li{
> list-style-type:none;clear:both;border:1px solid #e0ecee; } #ygrp-vital ul li
> .ct{
> font-weight:bold;color:#ff7900;float:right;width:2em;text-align:right;padding-ri
> ght:.5em;} #ygrp-vital ul li .cat{ font-weight:bold;} #ygrp-vital a{
> text-decoration:none;} #ygrp-vital a:hover{ text-decoration:underline;}
> #ygrp-sponsor #hd{ color:#999;font-size:77%;} #ygrp-sponsor #ov{ padding:6px
> 13px;background-color:#e0ecee;margin-bottom:20px;} #ygrp-sponsor #ov ul{
> padding:0 0 0 8px;margin:0;} #ygrp-sponsor #ov li{
> list-style-type:square;padding:6px 0;font-size:77%;} #ygrp-sponsor #ov li a{
> text-decoration:none;font-size:130%;} #ygrp-sponsor #nc{
> background-color:#eee;margin-bottom:20px;padding:0 8px;} #ygrp-sponsor .ad{
> padding:8px 0;} #ygrp-sponsor .ad #hd1{
> font-family:Arial;font-weight:bold;color:#628c2a;font-size:100%;line-height:122%
> ;} #ygrp-sponsor .ad a{ text-decoration:none;} #ygrp-sponsor .ad a:hover{
> text-decoration:underline;} #ygrp-sponsor .ad p{ margin:0;} o{font-size:0;}
> .MsoNormal{ margin:0 0 0 0;} #ygrp-text tt{ font-size:120%;} blockquote{margin:0
> 0 0 4px;} .replbq{margin:4;} -->
> __________________________________________________________ Catch up on fall's
> hot new shows on Yahoo! TV. Watch previews, get listings, and more!
> http://tv.yahoo.com/collections/3658 [Non-text portions of this message have
> been removed] <!-- #ygrp-mkp{ border: 1px solid #d8d8d8; font-family: Arial;
> margin: 14px 0px; padding: 0px 14px; } #ygrp-mkp hr{ border: 1px solid #d8d8d8;
> } #ygrp-mkp #hd{ color: #628c2a; font-size: 85%; font-weight: bold; line-height:
> 122%; margin: 10px 0px; } #ygrp-mkp #ads{ margin-bottom: 10px; } #ygrp-mkp .ad{
> padding: 0 0; } #ygrp-mkp .ad a{ color: #0000ff; text-decoration: none; }
> --><!-- #ygrp-sponsor #ygrp-lc{ font-family: Arial; } #ygrp-sponsor #ygrp-lc
> #hd{ margin: 10px 0px; font-weight: bold; font-size: 78%; line-height: 122%; }
> #ygrp-sponsor #ygrp-lc .ad{ margin-bottom: 10px; padding: 0 0; } --><!--
> #ygrp-mlmsg {font-size:13px; font-family:
> arial,helvetica,clean,sans-serif;*font-size:small;*font:x-small;} #ygrp-mlmsg
> table {font-size:inherit;font:100%;} #ygrp-mlmsg select, input, textarea
> {font:99% arial,helvetica,clean,sans-serif;} #ygrp-mlmsg pre, code {font:115%
> monospace;*font-size:100%;} #ygrp-mlmsg * {line-height:1.22em;} #ygrp-text{
> font-family: Georgia; } #ygrp-text p{ margin: 0 0 1em 0; } #ygrp-tpmsgs{
> font-family: Arial; clear: both; } #ygrp-vitnav{ padding-top: 10px; font-family:
> Verdana; font-size: 77%; margin: 0; } #ygrp-vitnav a{ padding: 0 1px; }
> #ygrp-actbar{ clear: both; margin: 25px 0; white-space:nowrap; color: #666;
> text-align: right; } #ygrp-actbar .left{ float: left; white-space:nowrap; }
> .bld{font-weight:bold;} #ygrp-grft{ font-family: Verdana; font-size: 77%;
> padding: 15px 0; } #ygrp-ft{ font-family: verdana; font-size: 77%; border-top:
> 1px solid #666; padding: 5px 0; } #ygrp-mlmsg #logo{ padding-bottom: 10px; }
> #ygrp-vital{ background-color: #e0ecee; margin-bottom: 20px; padding: 2px 0 8px
> 8px; } #ygrp-vital #vithd{ font-size: 77%; font-family: Verdana; font-weight:
> bold; color: #333; text-transform: uppercase; } #ygrp-vital ul{ padding: 0;
> margin: 2px 0; } #ygrp-vital ul li{ list-style-type: none; clear: both; border:
> 1px solid #e0ecee; } #ygrp-vital ul li .ct{ font-weight: bold; color: #ff7900;
> float: right; width: 2em; text-align:right; padding-right: .5em; } #ygrp-vital
> ul li .cat{ font-weight: bold; } #ygrp-vital a{ text-decoration: none; }
> #ygrp-vital a:hover{ text-decoration: underline; } #ygrp-sponsor #hd{ color:
> #999; font-size: 77%; } #ygrp-sponsor #ov{ padding: 6px 13px; background-color:
> #e0ecee; margin-bottom: 20px; } #ygrp-sponsor #ov ul{ padding: 0 0 0 8px;
> margin: 0; } #ygrp-sponsor #ov li{ list-style-type: square; padding: 6px 0;
> font-size: 77%; } #ygrp-sponsor #ov li a{ text-decoration: none; font-size:
> 130%; } #ygrp-sponsor #nc{ background-color: #eee; margin-bottom: 20px; padding:
> 0 8px; } #ygrp-sponsor .ad{ padding: 8px 0; } #ygrp-sponsor .ad #hd1{
> font-family: Arial; font-weight: bold; color: #628c2a; font-size: 100%;
> line-height: 122%; } #ygrp-sponsor .ad a{ text-decoration: none; } #ygrp-sponsor
> .ad a:hover{ text-decoration: underline; } #ygrp-sponsor .ad p{ margin: 0; }
> o{font-size: 0; } .MsoNormal{ margin: 0 0 0 0; } #ygrp-text tt{ font-size: 120%;
> } blockquote{margin: 0 0 0 4px;} .replbq{margin:4} --> [Non-text portions of
> this message have been removed] The primary EnergyPlus web site is found at:
> http://www.energyplus.gov The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed --
> please post any files to the appropriate folder in the Files area of the Support
> Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under
> the Documentation link and press the "search" button. Yahoo! Groups Links
> __________________________________________________________ Pinpoint customers
> who are looking for what you sell. http://searchmarketing.yahoo.com/ [Non-text
> portions of this message have been removed] <!-- #ygrp-mkp{ border: 1px solid
> #d8d8d8; font-family: Arial; margin: 14px 0px; padding: 0px 14px; } #ygrp-mkp
> hr{ border: 1px solid #d8d8d8; } #ygrp-mkp #hd{ color: #628c2a; font-size: 85%;
> font-weight: bold; line-height: 122%; margin: 10px 0px; } #ygrp-mkp #ads{
> margin-bottom: 10px; } #ygrp-mkp .ad{ padding: 0 0; } #ygrp-mkp .ad a{ color:
> #0000ff; text-decoration: none; } --><!-- #ygrp-sponsor #ygrp-lc{ font-family:
> Arial; } #ygrp-sponsor #ygrp-lc #hd{ margin: 10px 0px; font-weight: bold;
> font-size: 78%; line-height: 122%; } #ygrp-sponsor #ygrp-lc .ad{ margin-bottom:
> 10px; padding: 0 0; } --><!-- #ygrp-mlmsg {font-size:13px; font-family:
> arial,helvetica,clean,sans-serif;*font-size:small;*font:x-small;} #ygrp-mlmsg
> table {font-size:inherit;font:100%;} #ygrp-mlmsg select, input, textarea
> {font:99% arial,helvetica,clean,sans-serif;} #ygrp-mlmsg pre, code {font:115%
> monospace;*font-size:100%;} #ygrp-mlmsg * {line-height:1.22em;} #ygrp-text{
> font-family: Georgia; } #ygrp-text p{ margin: 0 0 1em 0; } #ygrp-tpmsgs{
> font-family: Arial; clear: both; } #ygrp-vitnav{ padding-top: 10px; font-family:
> Verdana; font-size: 77%; margin: 0; } #ygrp-vitnav a{ padding: 0 1px; }
> #ygrp-actbar{ clear: both; margin: 25px 0; white-space:nowrap; color: #666;
> text-align: right; } #ygrp-actbar .left{ float: left; white-space:nowrap; }
> .bld{font-weight:bold;} #ygrp-grft{ font-family: Verdana; font-size: 77%;
> padding: 15px 0; } #ygrp-ft{ font-family: verdana; font-size: 77%; border-top:
> 1px solid #666; padding: 5px 0; } #ygrp-mlmsg #logo{ padding-bottom: 10px; }
> #ygrp-vital{ background-color: #e0ecee; margin-bottom: 20px; padding: 2px 0 8px
> 8px; } #ygrp-vital #vithd{ font-size: 77%; font-family: Verdana; font-weight:
> bold; color: #333; text-transform: uppercase; } #ygrp-vital ul{ padding: 0;
> margin: 2px 0; } #ygrp-vital ul li{ list-style-type: none; clear: both; border:
> 1px solid #e0ecee; } #ygrp-vital ul li .ct{ font-weight: bold; color: #ff7900;
> float: right; width: 2em; text-align:right; padding-right: .5em; } #ygrp-vital
> ul li .cat{ font-weight: bold; } #ygrp-vital a{ text-decoration: none; }
> #ygrp-vital a:hover{ text-decoration: underline; } #ygrp-sponsor #hd{ color:
> #999; font-size: 77%; } #ygrp-sponsor #ov{ padding: 6px 13px; background-color:
> #e0ecee; margin-bottom: 20px; } #ygrp-sponsor #ov ul{ padding: 0 0 0 8px;
> margin: 0; } #ygrp-sponsor #ov li{ list-style-type: square; padding: 6px 0;
> font-size: 77%; } #ygrp-sponsor #ov li a{ text-decoration: none; font-size:
> 130%; } #ygrp-sponsor #nc{ background-color: #eee; margin-bottom: 20px; padding:
> 0 8px; } #ygrp-sponsor .ad{ padding: 8px 0; } #ygrp-sponsor .ad #hd1{
> font-family: Arial; font-weight: bold; color: #628c2a; font-size: 100%;
> line-height: 122%; } #ygrp-sponsor .ad a{ text-decoration: none; } #ygrp-sponsor
> .ad a:hover{ text-decoration: underline; } #ygrp-sponsor .ad p{ margin: 0; }
> o{font-size: 0; } .MsoNormal{ margin: 0 0 0 0; } #ygrp-text tt{ font-size: 120%;
> } blockquote{margin: 0 0 0 4px;} .replbq{margin:4} -->
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/