What type of HVAC system are you using? If a cycling fan system is
used and the average system flow rate is less than the minimum
outside air flow rate, you will get 100% outside air and the flow
rate may drop below the minimum you expect. The outside air flow rate
can not be greater than the mixed air flow rate. Compare the outdoor
air flow rate to the mixed air (or HVAC system) flow rate and see if
they are equal during these times. If you can not find a reason for
this problem, please upload your file to the Files/Problem_Submittals
folder so an EnergyPlus team member can take a closer look.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Judith Peters
<jdth_peters@...> wrote:
>
> Dear EnergyPlus Group,
>
> When I adjust the minimum outdoor air level, I do not see a
corresponding change in my heating and cooling rates/consumption.
>
> I followed your suggestion and set the controller to "fixed"
instead of "proportional", but I am still having the problem.
>
> Any suggestions?
>
> Thank you for your help!
>
> Judy Peters
>
>
> ---------------------------------
> Don't let your dream ride pass you by. Make it a reality with
Yahoo! Autos.
>
> [Non-text portions of this message have been removed]
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/