Re: [EnergyPlus_Support] Re: Minimum O.A.



Hi Richard,
   
  Thank you for your reply.  I am using a variable fan with a VAV system.  The file is an adaptation of the 5ZoneVAV Example File.  My overall maximum air flow is  10.709 m^3/s.  For outside air, the eio file states a minimum of 1.8125 m^3/s to a maximum of 10.709 m^3/s.
   
  I have uploaded the file.  Thank you very much for your help.
   
  Judy Peters

Richard Raustad <RRaustad@xxxxxxxxxxxx> wrote:
          What type of HVAC system are you using? If a cycling fan system is 
used and the average system flow rate is less than the minimum 
outside air flow rate, you will get 100% outside air and the flow 
rate may drop below the minimum you expect. The outside air flow rate 
can not be greater than the mixed air flow rate. Compare the outdoor 
air flow rate to the mixed air (or HVAC system) flow rate and see if 
they are equal during these times. If you can not find a reason for 
this problem, please upload your file to the Files/Problem_Submittals 
folder so an EnergyPlus team member can take a closer look.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Judith Peters 
<jdth_peters@...> wrote:
>
> Dear EnergyPlus Group,
> 
> When I adjust the minimum outdoor air level, I do not see a 
corresponding change in my heating and cooling rates/consumption. 
> 
> I followed your suggestion and set the controller to "fixed" 
instead of "proportional", but I am still having the problem.
> 
> Any suggestions?
> 
> Thank you for your help!
> 
> Judy Peters
> 
> 
> ---------------------------------
> Don't let your dream ride pass you by. Make it a reality with 
Yahoo! Autos. 
> 
> [Non-text portions of this message have been removed]
>



                         

       
---------------------------------
Take the Internet to Go: Yahoo!Go puts the Internet in your pocket: mail, news, photos & more. 

[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/