Re: [EnergyPlus_Support] A question about the center-of-glass conductance
I suspect that radiant heat transfer inside and outside are affecting your
results. Repeat your test with a simple single-pane construction and set the
IR Hemispherical Emissivity: Front Side (and Back Side) to 0.00001 to supress
radiant transfer. Does this compare better?
For a double-pane system, you will need to define two instances of the glass,
one with IR Hemispherical Emissivity: Front Side set to 0.00001 and another
with IR Hemispherical Emissivity: Back Side set to 0.00001. You need to keep
the radiant transfer across the window gas active.
Mike
On 30 Oct 2007 at 10:19, wanglei wrote:
> Dear Linda
>
>
> Now I create a single zone model with a south window without Frame and
> Divide. The window area is 4.5m2.
>
> According to the ASHARE winter conditions, I create a HeatDesign Day:
> The outside temperature is -17.8C
> The wind speed is 6.71m/s
>
> The indoor temperature is 21.
>
> After calculating, the Window Heat Loss is 490.7W ; the Ext Convection Coeff is
> 23.68W/m2-K; the Int Convection Coeff is 3.076W/m2-K.
>
> I use the formula k=Q/(tin -tout)/A to calculate the window u value
>
> The result is 2.8 W/m2-K. In eio file, this value is 3.785 W/m2-K
>
> Could you tell me why these two value isn't equal
>
> Thank you
>
> Lei wang
>
>
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/