Re: [EnergyPlus_Support] Earthtube schedule simulation.
1. Run the simulation and report Outdoor Dry Bulb, hourly.
2. Create a spreadsheet using the hourly values of Outdoor Dry Bulb, and
compute a column of hourly values of 1 or 0 based on your operation rules.
3. Save the results as a csv (comma separated) file.
4. Use SCHEDULE:FILE:COMMA to read this file as a schedule.
Mike
On 29 Oct 2007 at 4:20, peteryjlin wrote:
> Dear Sir or Madam to whom is concerned:
>
> We are running an earthtube simulation case in Taiwan and like to apply
> this system in a house of three floors when the ambient environment is
> under 15 degree C or above 27 degree C. When the ambient temperature is
> between 15 to 27 degree C, we are planning to use natural ventilation
> to maintain indoor environment condition. However, we do not know how
> to set up this kind of conditional schedule for earthtube system so
> far. ON when it is under 15 degree C or above 27 degree C, and OFF when
> it is between 15 and 27 degree C. If any one of you have idea on
> setting up this kind of schedule, please let me know at your
> convenience.
>
> Best Regards
>
>
> Peter
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/