Re: [EnergyPlus_Support] Comparison loads of E+ and Doe2.1E due to windows



Yes, DOE-2.1e cooling results tend to be sigificantly higher than EnergyPlus. 
Please see the bar charts in the following testing report to see some 
comparisons of different programs, including EnergyPlus and DOE-2.1E:

EnergyPlus Testing with Building Thermal Envelope and Fabric Load Tests from 
ANSI/ASHRAE Standard 140-2004

http://www.eere.energy.gov/buildings/energyplus/pdfs/energyplus_ashrae_140_envel
ope.pdf


Mike


On 29 Oct 2007 at 18:36, tjutw wrote:

> Hi All,
> 
> In my project, I used DOE2.1e and EnergyPlus to get simulation
> results. I found that heating energy is almost same. But the cooling
> energy are quite different.  It seems the main reason is  because of
> windows. It is hard to have the same parameters for windows in doe2.1e
> and EnergyPlus. So I created a very simple model to compare
> heating/cooling loads due to windows.
> 
> There are no internal heat (people, equipment, lighting) and no
> infiltration in space. The indoor temperature is taken as 22.2 degree
> C. The window is single panel without frame. From DOE2.1E,
> GLASS-TYPE-CODE is 1000 (U-SI 6.31, SHGC 0.86, SC 1, Tsol 0.84, Rfsol
> 0.08, Tvis 0.9, Rfvis 0.08, thickness 3mm).  Then I entered these
> parameters to EnergyPlus input file.  
> 
> The following are results.
> 
> zone without window (loads due to wall): 
> heating : 20.23 GJ (E+), 21.04 GJ (Doe2)  
> sens cooling: 0.07 GJ (E+), 0.28 GJ (Doe2)
> 
> zone with window (window-to-wall ratio is 16%)
> heating : 44.53 GJ (E+), 51.4 GJ (Doe2)
> sens cooling: 25.55 GJ (E+), 33.27 GJ (Doe2)
> 
> zone with window (window-to-wall ratio is 97%)
> heating: 210.68 GJ (E+), 228.2 GJ (Doe2)
> sens cooling: 143.72 GJ (E+), 223.76 GJ (Doe2)
> 
> From the above results, there are obvious differences in sensible
> cooling load.  I am not sure the differences are because of the
> different calculation methods of two software or I made some mistakes
>  in my simulation.  
> 
> Anyone can give me some advice about this?
> Thanks a lot in advance. 
> 
> Tj Ywh
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/