Nuno, you have a comma in the surface name of your windows. This acts as
if these were on two lines and represent 2 inputs. Get rid of the comma
(Window 5.974m2). Also check your error file..
Surface:HeatTransfer:Sub,
Window, 5.974m2, !- User Supplied Surface Name
WINDOW, !- Surface Type
brandao_nuno wrote:
>
> Dear Support Group,
>
> I´m studying the BESTEST case number 620. I have a problem with the
> sensible cooling rate, when using the PURCHASED AIR option. The total
> annual heating rate seems to be very consistent but the annual cooling
> rate has a strange low value. This is a quite simple simulation and i
> didn´t expect to encounter problems but i´ve reviewed the idf file and
> couldn´t find what´s wrong. Also the two windows are not appearing in
> the dxf file.
>
> I´m going to upload the file, can you take
> a look at it? I´m naming it 620_nbrandao.
>
> Thank you in advance
> Regards
> Nuno Brandão
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/