Re: [EnergyPlus_Support] Unmet load hours?
The following report variables are applicable:
Time Heating Setpoint Not Met Any Zone[hr]
Time Cooling Setpoint Not Met Any Zone[hr]
Time Heating Setpoint Not Met While Occupied Any Zone[hr]
Time Cooling Setpoint Not Met While Occupied Any Zone[hr]
These can be reported using REPORT VARIABLE, or REPORT:TABLE:MONTHLY.
A predefined report object may be found in Datasets\StandardReports.idf
Report:Table:Monthly,
Setpoints Not Met With Temperatures, !- Name
. . .
And in version 2.1 (to be released very soon), there is a new option
REPORT:TABLE:PREDEFINED, System Summary;
which will report these variables for the entire run period.
Mike
On 5 Nov 2007 at 2:40, mingming_zuo wrote:
> Hi all, when i modeled a large building for comforming to ASHRAE 90.1
> Appendix G. After conpleting the model, how can I get the unmet load
> hours from energyplus? Should I add some variable report? If so, what
> variable should I choose? Thanks in advance!
>
> regards
>
> Zuo Mingming
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/