the instructions below fixed the problem, but i am still having
trouble making it run. The airflow network is making E+ crash. I have
uploaded the file. Please take a look.
thank you for your help.
Haider.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> This file fails with the following error:
>
> ** Severe ** Invalid Number in Numeric Field#2 (Limit Value on
Multiplier
> for Modulating Venting Open Factor), value=OPENCLOSESCH, in
> AIRFLOWNETWORK:MULTIZONE:SURFACE=ZN_1_FLR_1_SEC_1_WALL_1_DOOR_1
>
> If you open the file in IDF Editor, a 0 (zero) is displayed in this
field. But
> if you open the file in a text editor, you can see that the
schedule name
> appears twice, once here and once in the schedule field. If you
replace this
> with a 1, this error will be fixed.
>
> Mike
>
>
> On 12 Nov 2007 at 18:55, muhammadhaiderkhan wrote:
>
> > i tried running my ES files by following your instructions below,
but
> > i am running into some problems. I have uploaded the
> > file "1000SqftSanFran.idf" to the files sections. can you please
take
> > a look at it to see if you can figure out what might be done
wrong.
> >
> > thanks,
> > Haider.
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
> > <mjwitte@> wrote:
> > >
> > > There are two approaches to modeling airflow from windows and
doors.
> > >
> > > The simple approach uses VENTILATION and INFILTRATION objects.
> > >
> > > The more complex approach uses AIRFLOWNETWORK objects. The
> > specific object
> > > which controls window and door opening is
> > AIRFLOWNETWORK:MULTIZONE:ZONE and/or
> > > AIRFLOWNETWORK:MULTIZONE:SURFACE. Set "Ventilation Control
> > Mode"=CONSTANT, and
> > > use the "Venting Availability Schedule Name" to control whether
the
> > opening
> > > (window or door) is open (sched value = 1) or closed (sched
value =
> > 0).
> > > "Window/Door Opening Factor, or Crack Factor" controls how much
the
> > window/door
> > > is opened.
> > >
> > > Mike
> > >
> > >
> > > On 31 Oct 2007 at 19:10, muhammadhaiderkhan wrote:
> > >
> > > > i am trying to figure out how to put windows/doors to open
and
> > close
> > > > on a schedule.
> > >
> > >
> > > ========================================================
> > > Michael J. Witte, GARD Analytics, Inc.
> > > EnergyPlus Testing and Support
> > > EnergyPlus-Support@
> > >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
under the
> > Documentation link and press the "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@...
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/