Hi Fred;

Thanks in advance for taking a look at it. I uploaded the .idf to the
Problem_Submittals folder. It's called "DV_test."

Thanks,

Josh


On Nov 20, 2007 3:56 PM, Fred Buhl <wfbuhl@xxxxxxx> wrote:
>
>
>
>
>
>
>
>
>
>  josh_miarch wrote:
>  > I'm attempting to model a cold climate system in which heating is
>  > provided by a combination of centrally conditioned air (delivered via
>  > displacement ventilation) and a radiant panel. The zone in question
>  > has a constant setpoint of 21 C. Air is delivered from the central AHU
>  > at 19 C, with the balance of the heating load being made up by the
>  > radiant panel.
>  >
>  > I've modeled this with a DIRECT AIR object given heating priority 1
>  > and a LOW TEMP RADIANT SYSTEM:HYDRONIC object (heating control
>  > temperature = 18 C, throttling range = 3 C) given heating priority 2.
>  >
>  > The problem I'm having is that the autosizable fields of several
>  > objects are being filled incorrectly. For example, the maximum hot
>  > water flow of the radiant panel is being autosized to 0. Strangely, I
>  > noticed that when I increase the "zone heating design supply air
>  > temperature" field in the ZONE SIZING object from its original value
>  > of 19 C, at a certain point the maximum hot water flow of the radiant
>  > panel starts getting autosized to numbers greater than 0.
>  >
>  > Investigating this further, I noticed that the "DesLoad" outputted in
>  > the "Zone Sizing Information" section of the .eio output file changed
>  > when I changed the zone heating design supply air temperature in the
>  > ZONE SIZING object. For example, when the design supply air temp was
>  > set to 19 C, the "DesLoad" was 0.20703 W, and when it was set to 80 C,
>  > the "DesLoad" was 13194 W.
>  >
>  > I'm guessing that this is the source of my problems. It seems strange
>  > to me that the design load would change based on the supply air
>  > temperature -- shouldn't these variables be independent of one another?
>  >
>  Yes; in theory anyway. But other design constraints might be affecting
>  the initially calculated, pure
>  design load. Why don't you upload your input and we will take a look.
>
>  Fred Buhl
>
>  > I know that EnergyPlus can sometimes struggle with hybrid systems like
>  > this; I'm wondering if there is an error on my part, or if this an
>  > example of EnergyPlus' limitations in this area. Any advice that
>  > anyone could give me that would get me closer to an accurate
>  > simulation would be greatly appreciated.
>  >
>  > Thanks,
>  >
>  > Josh
>  >
>  > --
>  > Josh Kjenner, EIT, LEED AP
>  > Manasc Isaac Architects Ltd.
>  > 10225 100 Avenue :: Edmonton, AB T5J 0A1
>  > 780.429.3977
>  >
>  >
>  >
>  >
>  >
>  > The primary EnergyPlus web site is found at:
>  > http://www.energyplus.gov
>  >
>  > The group web site is:
>  > http://groups.yahoo.com/group/EnergyPlus_Support/
>  >
>  > Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>  >
>  > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>  >
>  > Yahoo! Groups Links
>  >
>  >
>  >
>  >
>  



-- 
Josh Kjenner, EIT, LEED AP
Manasc Isaac Architects Ltd.
10225 100 Avenue :: Edmonton, AB T5J 0A1
780.429.3977


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/