[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Absorption chiller model
Hi!
Need help identifying source of error in my model for absorption chiller.
Below is the error. I tried editing the condenser pump, chiller parameters,
equipment sizes, loop temperatures, etc. but can't seem to arrive at the
source of error. I uploaded the idf file named
AbsorptionChillerModified.idf
Thank you in advance!
Best Regards,
Jun
** Warning ** SizeCondDemandSide: Calculated Plant Sizing Design Volume Flow
Rate=[0.00] is too small. Set to 0.0
** ~~~ ** ..occurs for Condenser Loop=CHILLED WATER LOOP CONDENSER
WATER LOOP
** Warning ** SizeCondSupplySide: Calculated Plant Sizing Design Volume
Flow Rate=[0.00] is too small. Set to 0.0
** ~~~ ** ..occurs for Condenser Loop=CHILLED WATER LOOP CONDENSER
WATER LOOP
** Warning ** SizePump: Calculated Pump Nominal Volume Flow Rate=[0.00]
is too small. Set to 0.0
** ~~~ ** ..occurs for Pump=CHILLED WATER LOOP CNDW SUPPLY PUMP
** Warning ** Check input. Pump nominal power or motor efficiency is set
to 0, for pump=CHILLED WATER LOOP CNDW SUPPLY PUMP
** Warning ** Check input. Pump nominal volumetric flow rate is set or
calculated = 0, for pump=CHILLED WATER LOOP CNDW SUPPLY PUMP
** Severe ** CalcBLASTAbsorberModel: Condenser flow = 0, for
Absorber=CHILLER
** Fatal ** Program Terminates due to previous error condition.
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=CalcBLASTAbsorberModel: Condenser flow = 0, for
Absorber=CHILLER
************* Fatal error -- final processing. More error messages may
appear.
************* Testing Individual Branch Integrity
************* All Branches passed integrity testing
************* Testing Individual Supply Air Path Integrity
************* All Supply Air Paths passed integrity testing
************* Testing Individual Return Air Path Integrity
************* All Return Air Paths passed integrity testing
************* No node connection errors were found.
************* EnergyPlus Terminated--Fatal Error Detected. 8 Warning; 1
Severe Errors; Elapsed Time=00hr 00min 2.91sec
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/