Re: [EnergyPlus_Support] Changing Setpoint Temperatures
Search for "Thermostatic". Here's an example:
ZONE CONTROL:THERMOSTATIC,
Zone 2 Thermostat, !- Thermostat Name
EAST ZONE, !- Zone Name
Zone Control Type Sched, !- Control Type SCHEDULE Name
DUAL SETPOINT WITH DEADBAND, !- Control Type #1
Dual Setpoint with DB; !- Control Type Name #1
DUAL SETPOINT WITH DEADBAND,
Dual Setpoint with DB, !- Name
Heating Setpoints, !- Heating Setpoint Temperature SCHEDULE Name
Cooling Setpoints; !- Cooling Setpoint Temperature SCHEDULE Name
SCHEDULE:COMPACT,
Cooling Setpoints, !- Name
Temperature, !- ScheduleType
Through: 12/31, !- Complex Field #1
For: AllDays, !- Complex Field #2
Until: 7:00, !- Complex Field #3
30.0, !- Complex Field #4
Until: 18:00, !- Complex Field #5
24.0, !- Complex Field #6
Until: 24:00, !- Complex Field #7
30.0; !- Complex Field #8
Abeer M. Eisa wrote:
>
> Thanks, HVAC is simple, anyway, I've searched EnergyPlus documentation
> and found the only mention is under "DEMAND MANAGER THERMOSTAT" But
> this is empty in the idf, (though setpoint temperatures are already
> set in Designbuilder) so how to change it???
> Waiting your reply with gratitude.
> Abeer
>
> Linda Lawrie <linda@xxxxxxxxxx <mailto:linda%40lawrie.com>> wrote:
> It is probably using Compact HVAC objects for the HVAC system. Look
> them up in the Input Output Reference. The field names should tell
> you as well.
>
> At 09:36 AM 11/26/2007, abeermme wrote:
> >I've exported a model to EnergyPlus fro DesignBuilder, I need to
> >change the cooling setpoint temperature but cannot find it in the idf
> >where to find it?
>
> Linda
>
> EnergyPlus WebSite: http://www.energyplus.gov <http://www.energyplus.gov>
> Owner: EnergyPlus_Support list
> Member: EnergyPlus Development Team
>
> [Non-text portions of this message have been removed]
>
> Abeer M. Eisa
> Assistant Lecturer - PhD Student
> Department of Architecture
> Ain-Shams University
> Cairo Egypt
> 010 678 52 59
>
>
> ---------------------------------
> Be a better sports nut! Let your teams follow you with Yahoo Mobile.
> Try it now.
>
> [Non-text portions of this message have been removed]
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/