Re: [EnergyPlus_Support] A question about Solar distribution
I cannot reproduce your result. I get zeros as expected for everything but the
floor when using FullExterior. Please check your input, and check that the
wall surfaces are classified as WALL (and not FLOOR) in the surface input.
If you cannot resolve this, please upload the input file to the yahoo group
files area or send as a zipped attachment to energyplus-support@xxxxxxxx
Mike
On 19 Nov 2007 at 9:51, wanglei wrote:
> Dear all
>
> I want to change the value of the solar distribution field and to see if there
> is change of the beam Solar absorbed by the inside surface.
>
> Based on the document of InputOutputReference, when the FullExterior is input,
> the value of Opaque surface inside Face Beam Solar absorbed radiation is
> non-zero only for floor surfaces. But In my simulation file when I input the
> FullExterior in this field, the quantity is non-zero for east and west wall
> surfaces.
>
> I want to know why?
>
>
>
> lei
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/