Re: [EnergyPlus_Support] Electric radiators question
BASEBOARD HEATER:ELECTRIC:Convective is 100% convective gain to the zone. If
the equipment you are modeling is small-area with air-flow openings, such as
along a baseboard, then use this equipment type. It sounds like this is what
you want to model.
LOW TEMP RADIANT SYSTEM:ELECTRIC is intended to model electric heating elements
embedded in a floor or ceiling (or wall). It's output is primarily radiant,
with some convection from the warm surface.
Mike
On 16 Nov 2007 at 16:44, katerina fragaki wrote:
> Hello all,
>
> I would like to simulate electric radiators (that is similar to hot water
> radiators, but operating with electricity) with EnergyPlus. Which is the way
> to do this simulation? I think I should use either BASEBOARD
> HEATER:ELECTRIC:Convective or LOW TEMP RADIANT SYSTEM:ELECTRIC Could you
> please tell me which is the difference between these two options and whether
> any of these is suitable for my simulation? If not, which option then is more
> suitable?
>
> With regards,
> Katerina
>
>
> ---------------------------------
> For ideas on reducing your carbon footprint visit Yahoo! For Good this month.
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/