By default, interior convection coefficients do not change with the presence of 
HVAC or natural ventilation airflow.  The "CeilingDiffuser" option for inside 
convection (global or zone-level) does respond to HVAC system airflow.  This is 
probably not going to be the same as your real greenhouse, but it is a step in 
the right direction.

An alternate approach is to estimate the air velocities on the various surfaces 
(or types of surfaces such as walls, roofs, floor) and estimate the interior 
convection coefficients.  These can be set using the ConvectionCoefficients 
object.  The values can even be scheduled if the fan will run only at certain 
times.  

Mike


On 27 Nov 2007 at 0:56, JV Dirkes II wrote:

> Dear Kristin,
> 
> 46% sounds reasonable to me; most smaller fans don't have very high
> efficiency.  If, however, EPlus is not able to model the breeze
> created by your fans, it begs the question of whether it's not simpler
> just to add electrical load to the zone...
> 
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Kristin Field"
> <fieldkm@...> wrote:
> >
> > Thanks for the response!  From the manufacturer and mech. schedule
> > data, it looks like the fans are about 46% total efficiency.  Feel
> > free to tell me if that doesn't sound reasonable.  To answer your
> > question, I'm not using the airflow network for this model.
> > 
> > --Kristin
> > 
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "JV Dirkes II" <jvd2pe@>
> > wrote:
> > >
> > > Dear Kristin,
> > > 
> > > If you model the fans as unit heaters (which seems like a reasonable
> > > choice to me), make sure that you've got the fan efficiency properly
> > > defined so that the KW calculated by the Fan object is appropriate.  I
> > > don't know typical efficiency for the circulation fans you're
> > > modeling, but it can be derived from the air flow rate, delta Pressure
> > > and motor data.
> > > 
> > > Although not very familiar with the EPlus algorithms, I wonder if it
> > > even "cares" about airflow from fans in any of its convection
> > > calculations; there's not enough information provided in the IDF
> > > objects such as Unit Heaters, to describe airflow patterns....  Maybe
> > > you're using Airflow Network for that (which I'm unfamiliar with)
> > > 
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Kristin Field"
> > > <fieldkm@> wrote:
> > > >
> > > > Hi, I'm trying to model a set of greenhouses that are heated
> only with
> > > > fin tube radiators.  The only "cooling" is through natural
> ventilation
> > > > and intake fans, which I have modeled using AirFlow objects.  I
> don't
> > > > have a question about this part of the model, just providing this
> > > > info. as background.
> > > > 
> > > > The question I have is about modeling the circulation fans that run
> > > > continuously in the greenhouse.  I thought of doing them as zone
> > > > equipment, but the I/O Reference lists the types of zone equipment
> > > > allowed, and plain "fans" are not among them.  Another option I
> > > > considered is modeling them as unit heaters with the heating cool
> > > > never enabled, but I was hoping for an easier solution.  The cfm is
> > > > high and, I would think, will have a big effect of the
> convection part
> > > > of the heat balance.  Without the effect on convection, I would
> > > > otherwise just input the fan heat as an electric internal gain.
> > > > 
> > > > Any thoughts?
> > > > 
> > > > Thanks,
> > > > Kristin Field
> > > >
> > >
> >
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/