For perimeter hot water convectors, use BASEBOARD HEATER:WATER:CONVECTIVE. If
you are using a standard unitary or VAV system, you can specify these as part
of the COMPACT HVAC:ZONE:* object.
Chilled beams are more difficult. The LOW TEMP RADIANT SYSTEM is a starting
point, but it will not produce the same level of convective heat transfer as a
chilled beam would typically have. You could increase this by setting a high
convection coefficient on the low temp radiant heat transfer surface. If it is
an active chilled beam with some forced airflow, the induction unit (SINGLE
DUCT:CONST VOLUME:4 PIPE INDUC) might be more appropriate. The key difference
is whether the particular chiled beam configuration you are modeling is
primarily radiant or convective.
Mike
On 26 Nov 2007 at 19:15, Jun Calixihan wrote:
> Hello!
>
>
>
> I'm new to EnergyPlus idf file editing. Is there a way to model chilled
> beams in EnergyPlus? What E+ objects shall I use? Shall I use LOW TEMP
> RADIANT SYSTEM? Shall I use this also for hot water convectors in building
> perimeter? I read the documentation on this but just want to be sure.
>
>
>
> Thanks very much!
>
> Jun
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/