[EnergyPlus_Support] Re: Suspended radiant panels



Hi Mike;

I'm also doing a simulation with a suspended radiant panel, and I've
found that if I define another opposite-facing surface and connect it
as an "interzone" surface with the radiant surface, I either get a
bunch of "heat balance did not converge" warning messages, or an
"Interzone surfaces are usually in different zones" error message,
depending on how I specify the constructions of the hydronic surface
and its backing. 

However, if I specify the radiant surface as one would an adiabatic
surface (ie OtherZoneSurface = itself), I seem to get reasonable results. 

Any thoughts on this?

Thanks,

Josh


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> 1.  I suppose you could describe a surface which is positioned as
thought it is 
> supsended.  This would have to be a pair of surfaces (one facing up
and one 
> facing down) which are connected as "interzone" surfaces even though
both are 
> in the same zone.  But understand that the radiant view factor
calculations are 
> not full 3-D.  View factors are affected by azimuths and tilts, but
position in 
> the zone does not matter.  If the radiant panels are electric, you
could use 
> the high temperature radiant model (HIGH TEMP RADIANT SYSTEM) and
specify the 
> view factors directly.
> 
> 2.  Low temp radiant systems are only valid on base surfaces (not
subsurfaces, 
> no internal mass).  You would need to describe the ceiling as two or
more 
> SURFACE:HEATRANSFER objects, one with the area of the radiant panel,
and one 
> with the remaining ceiling area.
> 
> Mike
> 
> 
> On 5 Sep 2007 at 13:21, lorenzomattarolo wrote:
> 
> > Hi, 
> > I'm simulating an office with radiant panels on the ceiling.
> > 
> > 1. Is it possible to put the radiant panels as they were suspended
> > from the ceiling?
> > 
> > 2. The panels aren't as wide as the ceiling. How can I set this in the
> > surfaceHeatTransfer? Do I have to put one surface with a normal
> > construction for the ceiling and a smaller one with internal source
> > for the panel?
> > 
> > Many thanks,
> > 
> > Lorenzo
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf
under the
> > Documentation link and press the "search" button.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@...
>




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/