Hello Mike,
after your observations, I reviewed the inputs but I
still have many problems with air temperature control. I also checked
the message stated in the svg file (ERROR - COULD NOT COMPLETE DRAWING!
Examine ERR file for possible explanation. Last error message is: "No
node connection found after the following object: FAN COIL HW COIL"),
but I did not find any error related to this issue.
Here there are the main informations about HVAC system and controls.*
*
--------------------
*Hot water plant loop *(HW Loop)
_Supply side (active components)
_
HW Supply Pump - /PUMP:CONSTANT SPEED/
C1 (should be 150 kW, now is set to "autosize") /- BOILER:SIMPLE/
C2 (should be 300 kW, now is set to "autosize")/- BOILER:SIMPLE/
C3 (should be 300 kW, now is set to "autosize")/- BOILER:SIMPLE/
_Demand side __ (active components)_
Fan Coil HW Coil /- COIL:Water:SimpleHeating/
Radiant system /- LOW TEMP RADIANT SYSTEM:CONSTANT FLOW/
UTA1 HW Coil /- //COIL:Water:SimpleHeating/
UTA2 HW Coil /- //COIL:Water:SimpleHeating/
UTA3 HW Coil /- //COIL:Water:SimpleHeating/
UTA1 Post Coil /- //COIL:Water:SimpleHeating/
UTA2 Post Coil /- //COIL:Water:SimpleHeating/
UTA3 Post Coil /- //COIL:Water:SimpleHeating/
*Chilled water loop *(CW Loop)/
/
_Supply side __ (active components)_
__CW Supply Pump - /PUMP:CONSTANT SPEED/
GF1 (should be 600 kW, now is set to "autosize") /-
CHILLER:ELECTRIC:EIR, AIR COOLED
/GF2 (should be 600 kW, now is set to "autosize") /-
//CHILLER:ELECTRIC:EIR//, AIR COOLED/
_Demand side __ (active components)_
Fan Coil CW Coil /- // COIL:Water:Cooling/
Radiant system /- LOW TEMP RADIANT SYSTEM:CONSTANT FLOW/
UTA1 CW Coil /-// //COIL:Water:Cooling/
UTA2 CW Coil /- //COIL:Water:Cooling/
UTA3 CW Coil /- //COIL:Water:Cooling/
*
Air loops*
_UTA1 _(serves zone 3596)
=
UTA1 OA SYSTEM - /OUTSIDE AIR SYSTEM, PASSIVE/
UTA1 CW Coil /- COIL:Water:Cooling//, SERIESACTIVE/
UTA1 HW Coil/ - COIL:Water:SimpleHeating//, SERIESACTIVE/
UTA1 Humidifier - /HUMIDIFIER:STEAM:ELECTRICAL//, SERIESACTIVE/
UTA1 Post Coil /- COIL:Water:SimpleHeating//, SERIESACTIVE// /
UTA1 FAN mandata - /FAN:SIMPLE:ConstVolume//, ACTIVE/
=
There are two CONTROLLER:SIMPLE controllers, one for heating coil, and
one for cooling coil.
This is a constant volume airsystem. It supplies air between 20°C and
26°C ( SETPOINT MANAGER:SCHEDULE:DUALSETPOINT). It controls humidity in
the space, trying to set it close to a value of 50% of relative
humidity. Remaining load in the zone are met by zone equipment.
_UTA2_ (serves zone 3200)
=
UTA2 Fan Ripresa - /FAN:SIMPLE:ConstVolume//, ACTIVE/
/UTA2 OA SYSTEM/ - /OUTSIDE AIR SYSTEM, PASSIVE/
UTA2 CW Coil /- COIL:Water:Cooling//, SERIESACTIVE/
UTA2 HW Coil/- COIL:Water:SimpleHeating//, SERIESACTIVE/
UTA2 Humidifier - /HUMIDIFIER:STEAM:ELECTRICAL//, SERIESACTIVE/
UTA2 Post Coil /- COIL:Water:SimpleHeating//, SERIESACTIVE/
UTA2 Fan mandata - /FAN:SIMPLE:ConstVolume//, ACTIVE/
=
There are two CONTROLLER:SIMPLE controllers, one for heating coil, and
one for cooling coil.
This is a constant volume airsystem. It supplies air between 20°C and
26°C ( SETPOINT MANAGER:SCHEDULE:DUALSETPOINT). It controls humidity in
the space, trying to set it close to a value of 50% of relative
humidity. Remaining load in the zone are met by zone equipment.
_UTA3_ (serves zone 2952)
=
UTA3 Fan Ripresa - /FAN:SIMPLE:ConstVolume//, ACTIVE/
/UTA3 OA SYSTEM/ - /OUTSIDE AIR SYSTEM, PASSIVE/
UTA3 CW Coil /- COIL:Water:Cooling//, SERIESACTIVE/
UTA3 HW Coil/- COIL:Water:SimpleHeating//, SERIESACTIVE/
UTA3 Humidifier - /HUMIDIFIER:STEAM:ELECTRICAL//, SERIESACTIVE/
UTA3 Post Coil /- COIL:Water:SimpleHeating//, SERIESACTIVE/
UTA3 Fan mandata - /FAN:SIMPLE:ConstVolume//, ACTIVE/
=
There are two CONTROLLER:SIMPLE controllers, one for heating coil, and
one for cooling coil.
This is a constant volume system and supplies air between 15°C and 40°C
( SETPOINT MANAGER:SCHEDULE:DUALSETPOINT). It controls humidity in the
space, trying to set it close to a value of 50% of relative humidity.
There are not more equipment able to control the zone temperature, so
this system is the only one that can heat and cool the zone, reaching
the setpoint. Moreover, It has a VENTILATION:MECHANICAL object to
control the minimum outdoor air flow rate.
*Zone Equipment
*Air distribution unit for each air loop is DIRECT AIR object.
Zone 3596. In this zone there is a FAN COIL UNIT:4 PIPE, able to meet
all remaing load in the zone.
Zone 3200. In this zone there is a low temperature radiant system to
meet all other load not met by air loop.
Zone 2952. There's no other equipment.
*Setpoint*
Heating setpoint: 20 °C
Cooling setpoint: 26°C
Relative humidity in the zone should be near to 50%
Each zone has the same heating and cooling setpoint, as well for
humidity control. In every zone there is thermostat and humidistat.
*--------------------*
Thank you very much for your useful help.
Loba
PS: These are our messages on EnergyPlus support group:
/
Re: [EnergyPlus_Support] zone air temperature /
/ /
/Based on a brief review of the inputs, zone 3596 is the only zone with
valid
inputs. The other zones have different types of systems and each has
different
issues. For example, Zone 2952 is served by a DIRECT AIR (constant volume)
terminal unit and the air loop has a fixed supply temperature setpoint.
This
system has no capability to control space temperature. There are alos no
controllers for any of the chilled water coils; only the fan coil
chilled water
coil will operate. And the svg system diagram does not draw, which is
usually
an indication that there is some type of connection error. Please send
an e-
mail to energyplus-support describing the system types and controls, and
I will
help you fix the input file.
Mike
On 30 Nov 2007 at 19:51, davide.loba wrote:
HI All,
I have some problems with the air temperature of zones.
Only in one zone (zone 3596), the heating setpoint (20°C) is reached,
but in the other two ( 3200, 2952), the air temperature is always
lower than it. The opposite thing happens with cooling: in the zone
3200 and 2952, the air temperature goes beyond the cooling setpoint
(26°C).
I tried to increase the boilers and chillers' nominal capacity with a
higher value, but nothing changed.
Apparently, idf seems to be ok. After simulation, there are many
warnings of this type: " Base surface does not surround subsurface,
overlap status=no overlap":are they related with this temperature problem?
I don't know how to solve it. Could you help me?
My .IDF has been uploaded under Files/Problem Submittals/Loba air
temperature.idf .
Kind regards
>
> Loba/
____________________________________________________________________________________
Be a better friend, newshound, and
know-it-all with Yahoo! Mobile. Try it now. http://mobile.yahoo.com/;_ylt=Ahu06i62sR8HDtDypao8Wcj9tAcJ
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/