Re: [EnergyPlus_Support] Modelling BASEBOARD equipment with CompactHVAC objects
What you suggest will work, but it will add lots of extra clutter to your input
file. Using the unitary zone and system type (with no cooling coil) would be
cleaner, but still a bit messy. For either system type, if you set the "System
Availability Schedule" to always be zero in the Compact HVAC:SYSTEM object,
then the air handling system should never run. And also set the night cycle
controls to "Stay Off".
Mike
On 8 Dec 2007 at 14:48, brandao_nuno wrote:
> Dear All,
>
> I´m currently simulating a small school, with only Ventilation and
> Heating requirements. For heating, the school as hot water radiators,
> with water supplied by a boiler. Ventilation is assured by simple
> ventilators. I´m using the BASEBOARD HEATER:Water:Convective from the
> Radiative/Convective Units group. I´m also thinking about a
> possibility to model the radiators with the CompactHVAC objects.
>
> Is it possible to use the COMPACT HVAC:ZONE(and SYSTEM):VAV filling
> the BASEBOARD fields and "turning off" the AHU suplly fan? EPLUS
> creates objects in the BASEBOARD HEATER:Water:Convective, however, I´m
> a little bit unsafe about this procedure. Can you give me a hand about
> this issue?
>
> Thank you very much
> Nuno
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/