Re: [EnergyPlus_Support] Floor- ceiling
Yes, you may thermally connect surfaces that are not geometrically adjacent as
long as the surface areas are equal. However, you must be careful to make sure
that the full exterior wall area is modelled in order to account for the heat
loss/gain through the portion of the wall that is present from 10m to 11m. If
you choose not to model the plenum space as a separate thermal zone, you must
include this wall area in the upper or lower zone or split it between the two.
You may find it easiest to simply make the lower zone include the ceiling
plenum and place the ceiling at 11m high instead of 10m.
Mike
On 2 Jan 2008 at 16:46, e_matta81 wrote:
>
> Hi, I'm a new user and I have a question about connecting floor and
> ceiling.
>
> I have a multistorey bulding and I want to thermally connect a ceiling
> (whose height is 10m from the ground) with a floor (whose height is
> 11m from the ground). Can i connect them, no matter if there is a zone
> between?
>
> Thanks a lot
>
> JM
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/