Neslihan:
I looked at the input file and found two issues using the AirflowNetwork
model.
1 Parent surface facing
Any parent surface defined as an AIRFLOWNETWORK:MULTIZONE:SURFACE does not
allow the parent surface faces itself: the user supplied surface name =
OutsideFaceEnviroment object. The reason to reject this choice is that the
prarent surface has to face different interior and exterior boundary
conditions, so that the AirflowNetwork model can work. A severe error
message in the eplusout.err shows it.
2 Wind direction
Wind direction fields used in the AIRFLOWNETWORK:MULTIZONE:WIND PRESSURE
COEFFICIENT ARRAY object do not allow the repeated values. The object is
enclosed.
As long as you make the above two issues correct, the AirflowNetwork model
should work. However, you still have other warning issues.
Best regards,
Lixing
!- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:WIND PRESSURE
COEFFICIENT ARRAY ===========
AIRFLOWNETWORK:MULTIZONE:WIND PRESSURE COEFFICIENT ARRAY,
basinc-array-ön, !- WPC Array Name
10, !- Reference Height for WPC Data {m}
180, !- Wind Direction #1 {deg}
180, !- Wind Direction #2 {deg}
180, !- Wind Direction #3 {deg}
180, !- Wind Direction #4 {deg}
180, !- Wind Direction #5 {deg}
180, !- Wind Direction #6 {deg}
180, !- Wind Direction #7 {deg}
180, !- Wind Direction #8 {deg}
180, !- Wind Direction #9 {deg}
180, !- Wind Direction #10 {deg}
180, !- Wind Direction #11 {deg}
180, !- Wind Direction #12 {deg}
180, !- Wind Direction #13 {deg}
180, !- Wind Direction #14 {deg}
180; !- Wind Direction #15 {deg}
----- Original Message -----
From: "neslihan turkmenoglu" <neslihanturkmenoglu@xxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Monday, January 07, 2008 9:33 AM
Subject: Re: [EnergyPlus_Support] combined effect of shading devices on
interior temperatures
> hi I uploaded my file;
>
> I Want to get interior surface temperatures of the
> zone with blinds in front of open large window
> -considering the effects of solar radiation and
> airflow penetration to the zone. My problems are;
>
> 1-when I enter my pressure coefficiens program
> crashes.I had my pressure measurements on middle axis
> of front facade and at the back facade of my model.
> The airflow came to facade perpendicular . So I wrote
> 180 according to north.
>
> 2- other thing is I cannot get information of sunlit
> areas, solar intensities of interior surfaces. In the
> manual it says that program calculates the amount of
> The beam radiation falling on each surface in the
> zone, including floor,walls and windows,by projecting
> the sun's rays through the exterior windows, taking
> into account the effect of exterior shadowing surfaces
> and window shading devices.
>
> thank you very much for your help
>
> --- Lixing Gu <gu@xxxxxxxxxxxx> wrote:
>
>> Neslihan:
>>
>> Please upload the input file. I am going to take a
>> look.
>>
>> Lixing
>> ----- Original Message -----
>> From: "neslihan turkmenoglu"
>> <neslihanturkmenoglu@xxxxxxxxx>
>> To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
>> Sent: Friday, January 04, 2008 7:36 PM
>> Subject: Re: [EnergyPlus_Support] combined effect of
>> shading devices on
>> interior temperatures
>>
>>
>> >I tried to rearrange my idf file according to
>> > AirflowNetwork3zVent.idf
>> > Until I put my own pressure coefficients, there
>> were
>> > no severe errors(my surface temperatures were
>> > unlogical).After that program crashed. What do I
>> > wrong? or what is missing?
>> > thank you very much:)
>> >
>> > I will attach my file;
>> >
>> > !-Generator IDFEditor 1.27 'current version of
>> > IDFEditor - less than 1 is a beta
>> >
>> > !-NOTE: All comments with '!-' are ignored by the
>> > IDFEditor and are generated automatically.
>> > !- Use '!' comments if they need to be
>> retained
>> > when using the IDFEditor.
>> >
>> >
>> > !- =========== ALL OBJECTS IN CLASS: VERSION
>> > ===========
>> >
>> > VERSION,
>> > 1.4; !- Version Identifier
>> >
>> >
>> > !- =========== ALL OBJECTS IN CLASS: BUILDING
>> > ===========
>> >
>> > BUILDING,
>> > Ofis , !- Building Name
>> > 0, !- North Axis {deg}
>> > Suburbs, !- Terrain
>> > 0.04, !- Loads Convergence
>> > Tolerance Value
>> > 0.4, !- Temperature
>> > Convergence Tolerance Value {deltaC}
>> > FullInteriorAndExteriorWithReflections, !-
>> Solar
>> > Distribution
>> > 30; !- Maximum Number of
>> > Warmup Days
>> >
>> >
>> > !- =========== ALL OBJECTS IN CLASS: TIMESTEP
>> IN
>> > HOUR ===========
>> >
>> > TIMESTEP IN HOUR,
>> > 4; !- Time Step in Hour
>> >
>> >
>> > !- =========== ALL OBJECTS IN CLASS: INSIDE
>> > CONVECTION ALGORITHM ===========
>> >
>> > INSIDE CONVECTION ALGORITHM,
>> > Detailed; !- Algorithm
>> >
>> >
>> > !- =========== ALL OBJECTS IN CLASS: OUTSIDE
>> > CONVECTION ALGORITHM ===========
>> >
>> > OUTSIDE CONVECTION ALGORITHM,
>> > Detailed; !- Algorithm
>> >
>> >
>> > !- =========== ALL OBJECTS IN CLASS: SOLUTION
>> > ALGORITHM ===========
>> >
>> > SOLUTION ALGORITHM,
>> > CTF; !- SolutionAlgo
>> >
>> >
>> > !- =========== ALL OBJECTS IN CLASS: SHADOWING
>> > CALCULATIONS ===========
>> >
>> > SHADOWING CALCULATIONS,
>> > 20; !-
>> > Period_for_calculations
>> >
>> >
>> > !- =========== ALL OBJECTS IN CLASS: ZONE
>> VOLUME
>> > CAPACITANCE MULTIPLIER ===========
>> >
>> > ZONE VOLUME CAPACITANCE MULTIPLIER,
>> > 1; !- Capacitance
>> Multiplier
>> >
>> >
>> > !- =========== ALL OBJECTS IN CLASS: RUN
>> CONTROL
>> > ===========
>> >
>> > RUN CONTROL,
>> > No, !- Do the zone sizing
>> > calculation
>> > No, !- Do the system
>> sizing
>> > calculation
>> > No, !- Do the plant sizing
>> > calculation
>> > Yes, !- Do the design day
>> > simulations
>> > Yes; !- Do the weather file
>> > simulation
>> >
>> >
>> > !- =========== ALL OBJECTS IN CLASS: RUNPERIOD
>> > ===========
>> >
>> > RunPeriod,
>> > 8, !- Begin Month
>> > 21, !- Begin Day Of Month
>> > 8, !- End Month
>> > 21, !- End Day Of Month
>> > , !- Day Of Week For
>> Start
>> > Day
>> > , !- Use WeatherFile
>> > Holidays/Special Days
>> > , !- Use WeatherFile
>> > DaylightSavingPeriod
>> > , !- Apply Weekend
>> Holiday
>> > Rule
>> > , !- Use WeatherFile
>> Rain
>> > Indicators
>> > , !- Use WeatherFile
>> Snow
>> > Indicators
>> > 1; !- Number of years of
>> > simulation
>> >
>> > RunPeriod,
>> > 2, !- Begin Month
>> > 21, !- Begin Day Of Month
>> > 2, !- End Month
>> > 21, !- End Day Of Month
>> > , !- Day Of Week For
>> Start
>> > Day
>> > , !- Use WeatherFile
>> > Holidays/Special Days
>> > , !- Use WeatherFile
>> > DaylightSavingPeriod
>> > , !- Apply Weekend
>> Holiday
>> > Rule
>> > , !- Use WeatherFile
>> Rain
>> > Indicators
>> > , !- Use WeatherFile
>> Snow
>> > Indicators
>> > 1; !- Number of years of
>> > simulation
>> >
>> >
>> > !- =========== ALL OBJECTS IN CLASS: LOCATION
>> > ===========
>> >
>> > Location,
>> > ISTANBUL_TUR Design_Conditions, !-
>> LocationName
>> > 40.97, !- Latitude {deg}
>> > 28.82, !- Longitude {deg}
>> > 2.00, !- TimeZone {hr}
>> > 37.00; !- Elevation {m}
>> >
>> >
>> > !- =========== ALL OBJECTS IN CLASS: DESIGNDAY
>> > ===========
>> >
>> > DesignDay,
>> > ISTANBUL Ann Clg .4% Condns DB=>MWB, !-
>> > DesignDayName
>> > 31.5, !- Maximum Dry-Bulb
>> > Temperature {C}
>> > 13.7, !- Daily Temperature
>> > Range {deltaC}
>> > 22, !- Humidity Indicating
>>
> === message truncated ===
>
>
>
>
> ____________________________________________________________________________________
> Looking for last minute shopping deals?
> Find them fast with Yahoo! Search.
> http://tools.search.yahoo.com/newsearch/category.php?category=shopping
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/