Thank you for the "nodes" view of the model. It was enlightening.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
<RRaustad@...> wrote:
>
> Only the inlet/exhaust nodes entered in the Controlled Zone Equip
> Configuration object are used to calculate the Return Air mass flow
> rate. Note that the mixing and cross-mixing objects only use "zone"
node
> information. This node is not the same as the inlet/outlet nodes of
a
> zone. For the actual inlet/outlet nodes, the return air node mass
flow
> rate is equal to the sum of the supply (inlet) mass flow rates
minus the
> sum of the exhaust (outlet) mass flow rates. You can check this by
> setting the mixing object mass flow rate to a constant. Then
reporting
> all the supply inlet and exhaust outlet mass flow rates and the
return
> air node mass flow rate. You can set the exhaust air mass flow
rates to
> 0 to make this easier. Calculate the total zone return air flow
rate by
> summing the supply (inlet) and subtracting the exhaust (outlet)
node
> mass flow rates. Then subtract this value from the return node mass
flow
> rate. Is this calculated value ever greater than zero? Since the
return
> air mass flow rate is not allowed to be negative, you may see some
> negative values when the exhaust air mass flow rate is greater than
the
> supply air mass flow rate. Also verify that the sum of the supply
> (inlet) node mass flow rate is 0 at some point in the simulation.
>
> anarui.oliveira wrote:
> >
> > I understand now about the source zone.
> >
> > But what about the RECEIVING zone of a MIXING object? This inlet
flow
> > is accounted for to balance the supply and return air flows of an
ATU?
> >
> > In this case, could I have a zero supply air flow and a non-zero
> > return air flow, based on the inlet flow of the MIXING object?
> >
> > Always thankful for your help,
> > Ana Rui.
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, "Michael J. Witte"
> > <mjwitte@> wrote:
> > >
> > > Cross mixing simply exchanges and equal amount of air between
two
> > zones. It is
> > > a zone heat balance function and the air handling system knows
> > nothing of it.
> > >
> > > On 11 Jan 2008 at 17:52, anarui.oliveira wrote:
> > >
> > > > Thanks a lot for all your answers.
> > > >
> > > > Regarding option 4:
> > > > - If I use Cross-mixing instead, doesn't the program account
for
> > the
> > > > corresponding outgoing flow in the source zone?
> > > >
> > > > Thanks again,
> > > > Ana Rui.
> > > >
> > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, "Michael J. Witte"
> > > > <mjwitte@> wrote:
> > > > >
> > > > > 1. First, I will clarify some terminology:
> > > > > Return air flow - air leaving the zone and returning to the
> > HVAC
> > > > system
> > > > >
> > > > > Exhaust air flow - air leaving the zone and exhausted to
> > outdoors
> > > > >
> > > > > Return air flow rate is computed as Supply air flow minus
> > Exhast
> > > > air flow
> > > > >
> > > > > I am not sure when you say "exhaust" if you mean return or
> > exahust
> > > > as defined
> > > > > above. I will use my definitions below.
> > > > >
> > > > > 2. The systems created by Compact HVAC assume that return
air
> > flow
> > > > is equal to
> > > > > supply air flow.
> > > > >
> > > > > 3. If you want to add exhaust air flow, you can add ZONE
> > EXHAUST
> > > > FAN objects by
> > > > > editing the expidf file.
> > > > >
> > > > > 4. If you want to model a constant (or scheduled) flow from
one
> > > > zone to
> > > > > another, you can use a MIXING object to move air from one
zone
> > to
> > > > another.
> > > > > However, the HVAC system has no knowledge of this and the
user
> > must
> > > > balance the
> > > > > airflows by adding a dummy ZONE EXHAUST FAN to the source
zone
> > to
> > > > cause a
> > > > > reduction in return air flow from the source zone.
> > > > >
> > > > > 5. For constant volume systems, you can use
> > > > AIRFLOWNETWORK:DISTRIBUTION:*
> > > > > objects to model the pressure-indcued flows, but this
feature
> > does
> > > > not yet
> > > > > support VAV systems.
> > > > >
> > > > > Mike
> > > > >
> > > > >
> > > > > On 9 Jan 2008 at 16:23, anarui.oliveira wrote:
> > > > >
> > > > > > Hi.
> > > > > >
> > > > > > The parameters for ATU, such as those cretated by
> > > > > > - Compact HVAC:Zone:VAV,
> > > > > > - Compact HVAC:System:VAV,
> > > > > > only allow the user to define the insufflated air flows
> > (Supply
> > > > air
> > > > > > flow), right?
> > > > > >
> > > > > > What does the simulation assume, in this case, for the
> > exhaust
> > > > air
> > > > > > flows, and how does it deal with the corresponding effect
on
> > the
> > > > > > inside pressures?
> > > > > >
> > > > > > If the case to model has different insufflated and exhaust
> > flows,
> > > > how
> > > > > > does it affect my model? Wow can I implement this in E+?
> > > > > >
> > > > > > And if a certain zone only has forced exhaust flow, and
the
> > inlet
> > > > > > flow is assumed to be drawn from adjacent areas by
pressure
> > > > > > difference?
> > > > > >
> > > > > > Thanks in advanced.
> > > > > >
> > > > > > Best regards,
> > > > > > Ana Rui.
> > > > > >
> > > > > >
> > > > > >
> > > > > > The primary EnergyPlus web site is found at:
> > > > > > http://www.energyplus.gov <http://www.energyplus.gov>
> > > > > >
> > > > > > The group web site is:
> > > > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > <http://groups.yahoo.com/group/EnergyPlus_Support/>
> > > > > >
> > > > > > Attachments are not allowed -- please post any files to
the
> > > > appropriate folder
> > > > > > in the Files area of the Support Web Site.
> > > > > >
> > > > > > EnergyPlus Documentation is searchable. Open
> > EPlusMainMenu.pdf
> > > > under the
> > > > > > Documentation link and press the "search" button.
> > > > > >
> > > > > > Yahoo! Groups Links
> > > > > >
> > > > > >
> > > > > >
> > > > > >
> > > > > >
> > > > >
> > > > >
> > > > > ========================================================
> > > > > Michael J. Witte, GARD Analytics, Inc.
> > > > > EnergyPlus Testing and Support
> > > > > EnergyPlus-Support@
> > > > >
> > > >
> > > >
> > > >
> > > >
> > > > The primary EnergyPlus web site is found at:
> > > > http://www.energyplus.gov <http://www.energyplus.gov>
> > > >
> > > > The group web site is:
> > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > <http://groups.yahoo.com/group/EnergyPlus_Support/>
> > > >
> > > > Attachments are not allowed -- please post any files to the
> > appropriate folder
> > > > in the Files area of the Support Web Site.
> > > >
> > > > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
> > under the
> > > > Documentation link and press the "search" button.
> > > >
> > > > Yahoo! Groups Links
> > > >
> > > >
> > > >
> > > >
> > > >
> > >
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/