1. If you anticipate all of the zones to be conditioned to nearly the same 
temperatures, mixing of air across the open plan or within the common shaft 
will have little impact on the results.  

2.  Since you are combining rooms vertically to form thermal zones, I would not 
add the complexity of separate plenum spaces.  But you must remember to include 
the exterior wall areas of the 1.3m space as part of the total exterior wall 
area for the thermal zones.

3.  In the ExampleFiles folder, look at ExampleFiles.xls for a listing of the 
key features of each example file.

Mike


On 13 Jan 2008 at 17:40, ooi wrote:

> Dear all, 
> 
> 
> 
> I managed to answer my first question on zoning, and run to success for one zone
> surfaces. I am still not sure if I need to use AirFlow Network and create a zone
> for the 1.3m high space between the ceilings and the floors above.
> 
> 
> 
> I have yet to study the example files on VAV, so any suggestions would be
> appreciated. 
> 
> 
> 
> Regards
> 
> ooi
> 
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/