Re: [EnergyPlus_Support] temperature set points
I think your error is not related with your question.
To fix error, you need to change the report variable name. Check .rdd file
and you will find the correct variable name should be:
INFILTRATION SENSIBLE HEAT LOSS
There is no "'" between INFILTRATION and SENSIBLE
You may check the setpoint in ECOTECT.
Allen
On Jan 17, 2008 11:28 PM, bish.dj61 <bish.dj@xxxxxxxxx> wrote:
> hi All
> I have a model that I am exporting to E+ from ecotect. The problem I
> have is that E+ seems to be setting the temperature set points to
> 0degC, and is so taking a huge cooling load. I do get this error
> message, but still can't rectify it:
>
> ** Warning ** The following Report Variables were requested but not
> generated
> ** ~~~ ** because IDF did not contain these elements or
> misspelled variable name -- check .rdd file
> ************* Key=*, VarName=MEAN AIR TEMPERATURE, Frequency=Hourly
> ************* Key=*, VarName=MEAN RADIANT TEMPERATURE,
> Frequency=Hourly
> ************* Key=*, VarName=INFILTRATION-SENSIBLE HEAT LOSS,
> Frequency=Hourly
> ************* Key=*, VarName=INFILTRATION-SENSIBLE HEAT GAIN,
> Frequency=Hourly
> ************* Key=*, VarName=LIGHTS-TOTAL HEAT GAIN,
> Frequency=Hourly
> ************* Key=*, VarName=ELECTRIC EQ-TOTAL HEAT GAIN,
> Frequency=Hourly
> ************* Key=*, VarName=PEOPLE-TOTAL HEAT GAIN,
> Frequency=Hourly
> ************* EnergyPlus Completed Successfully-- 6 Warning; 0
> Severe Errors; Elapsed Time=00hr 00min 14.57sec
>
> cheers
> Bisho
>
>
>
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/