RE: [EnergyPlus_Support] DesignBuilder to EnergyPlus errors



Temperature Out of Bounds errors are one of the toughest to solve.  Too
high temperatures (eg. 522.13C) mean that the zone has run-away heat
gains in the zone that are not being removed, often because of problems
with the HVAC system.  If there is no HVAC or purchased air system for
the zone with the surface error, then add one.  If there is a system,
then it could be any number of problems related to controls,
availability, sizing, node connections, branch control types, etc.  If
you are trying to model floating conditions without HVAC, then you
probably need to include at least some infiltration. 

 

________________________________

From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of anarui.oliveira
Sent: Monday, January 21, 2008 3:15 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] DesignBuilder to EnergyPlus errors

 

Hi all.

I tried to create a somewhat complex building geometry by putting 
together more than one DesignBuilder block (I put them together using 
Snap Points, so they should fit exactly), but when I export this 
geometry to EnergyPlus I get several erros like the following:

** Warning ** DXFOut: Could not triangulate surface="W_10631_3_0_1", 
type="Wall", check surface vertex order(entry)

for this and several other surfaces, and then a severe error:

** Severe ** Temperature out of bounds (522.13) for 
surface=W_10631_2_0_0
** ~~~ ** in Zone=10631
** ~~~ ** During Warmup, Occurrence info=COVILHA PRT INETI 
DATA WMO#=085360, 01/20 10:00 - 10:02

that stops the simulation.
I'm not sure if the 2 errors are related?

I already excluded the obvious Regular-R issues (all materials are 
defined as detailed, with proper density and heat storage).

Can anyone help me figure out reasons for this errors and ways to 
solve it?

Thanks,
Ana Rui.

 



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/