Allen,
>Hot Water Radiators on the wall: in Design Builder v1.2, when I choose
>this equipment should I select on the HVAC tab: a) convective, b)
>convective/radiant (this option makes the simulation to slow)
You should ideally use the convective/radiant system (uses EnergyPlus high
temp radiant system), but as you say simulations do run slowly especially
for large models. You may find that using a standard convective system is
sufficiently accurate for many hot water radiators, especially modern finned
systems which in practice have radiant heat emission fractions less than
0.2.
>Does the Design Builder v2.0 simulates Air Handling Units with Heat
Recovery?
Yes, DesignBuilder version 2 with the detailed HVAC module will simulate air
handling units with heat recovery. In fact DesignBuilder version 1.4 also
provides a basic heat recovery system using Compact HVAC VAV and Unitary
systems.
Regards,
Andy Tindale
DesignBuilder Software
-----Original Message-----
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]On Behalf Of André Lopes
Sent: 23 January 2008 09:48
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] EPlus vs Design Builder - Modelling Air
Handling Units and Hot Water Radiators
Mr. Mahabir
Thank you for your answer
Hot Water Radiators on the wall: in Design Builder v1.2, when I choose this
equipment should I select on the HVAC tab:
a) convective
b) convective/radiant
(this option makes the simulation to slow)
Does the Design Builder v2.0 simulates Air Handling Units with Heat
Recovery?
Regards
A L
----- Original Message ----
From: Mahabir Bhandari <bhandari@xxxxxxxxxxxxxxxxxxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Tuesday, January 22, 2008 4:49:53 PM
Subject: RE: [EnergyPlus_Support] EPlus vs Design Builder - Modelling Air
Handling Units with Heat Recovery
Allen,
Here is the definition of purchased air from E+ Input Output Reference
Manual..
Purchased Air
The simplest piece of zone equipment is the Purchased Air component. The
name ?
Purchased Air ? is an analogy with Purchased:Chilled Water and Purchased:Hot
Water. Of
course one can?t normally buy conditioned air. Purchased air is used in
situations where the
user wishes to study the performance of a building with an ideal system. In
such a case,
purchased air is usually the sole conditioning component: the user does not
need to specify
air loops, water loops, etc. All that is needed for the ideal system are
zone controls, zone
equipment configurations, and the purchased air components.
It is not correct that DesignBuilder only uses purchased air . Purchased air
(Simple HVAC) is one of the options. Another option is Compact HVAC. For
more information on Compact HVAC systems, please visit:
http://www.designbu ilder.co. uk/programhelp/ hvac_system_ type.htm
Currently in DesignBuilder, you can't simulate heat recovery with fan coil
units. Heat recovery is used only centralized systems such as VAV with
terminal reheat. This option will be available in version 2.0 (expected to
be released this summer) which will have detailed HVAC option as well.
Regards,
Mahabir Bhandari
_____
From: EnergyPlus_Support@ yahoogroups. com
[mailto:EnergyPlus_Support@ yahoogroups. com] On Behalf Of Maria Agustin
Sent: Tuesday, January 22, 2008 11:20 AM
To: EnergyPlus_Support@ yahoogroups. com
Subject: Re: [EnergyPlus_ Support] EPlus vs Design Builder - Modelling Air
Handling Units with Heat Recovery
Can you please provide definition of purchased air.
Bing Dong <bingcat2007@ <mailto:bingcat2007 %40gmail. com> gmail.com> wrote:
No airloop, plant and water loop.
Only purchased air if I was not wrong
Allen
On Jan 22, 2008 9:41 AM, André Lopes <andr_lopes2000@
<mailto:andr_ lopes2000% 40yahoo.com> yahoo.com> wrote:
> Hello
>
> What do you mean by: "There is real HVAC system in there."
>
> Regards
>
> A L
>
>
> ----- Original Message ----
> From: Bing Dong <bingcat2007@ <mailto:bingcat2007 %40gmail. com> gmail.com
<bingcat2007% 40gmail.com> >
> To: EnergyPlus_Support@ <mailto:EnergyPlus_ Support%40yahoog roups.com>
yahoogroups. com<EnergyPlus_ Support%40yahoog roups.com>
> Sent: Tuesday, January 22, 2008 2:31:29 PM
> Subject: Re: [EnergyPlus_ Support] EPlus vs Design Builder - Modelling Air
> Handling Units with Heat Recovery
>
> DesignBuilder will simulate the purchased air. There is real HVAC system
> in
> there.
>
> Allen
>
> On Jan 22, 2008 9:28 AM, André Lopes <andr_lopes2000@ yahoo.com> wrote:
>
> > Hello
> >
> > I am modelling a System that has:
> >
> > Heating: Boiler, Water Radiators
> >
> > Cooling: Chiller, Fan-Coil
> >
> > Fresh-Air:Air- Handling Units with Heat Recovery
> >
> > Using Design Builder and / or EnergyPlus, how should I Simulate the
> > Air-Handling Units with Heat Recovery?
> >
> > Best Regards
> >
> > A L
> >
> > ____________ _________ _________ _________ _________ _________ _
> > Never miss a thing. Make Yahoo your home page.
> > http://www.yahoo. com/r/hs
> >
> >
>
> [Non-text portions of this message have been removed]
>
> ____________ _________ _________ _________ _________ _________ _
> Never miss a thing. Make Yahoo your home page.
> http://www.yahoo. <http://www.yahoo. com/r/hs> com/r/hs
>
> [Non-text portions of this message have been removed]
>
>
>
[Non-text portions of this message have been removed]
------------ --------- --------- ---
Make the switch to the world's best email. Get the new Yahoo!7 Mail now.
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
______________________________________________________________________
______________
Be a better friend, newshound, and
know-it-all with Yahoo! Mobile. Try it now.
http://mobile.yahoo.com/;_ylt=Ahu06i62sR8HDtDypao8Wcj9tAcJ
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
Documentation link and press the "search" button.
Yahoo! Groups Links
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/