[EnergyPlus_Support] Re: High Temperatures in Vented Cavity
We are using regular materials but we have found the same problem in
some cases.
In our file, if we just change the the thickness of the outter layer
of the supporting wall by 0.01, the results changes from expected to
physicaly impossible (surface outside temperature bigger than the
exterior baffle temperature).
We are almost sure that this is a bug to be fixed, but in the
meanwhile I would like to know if can trust the results of the cases
that the simulation seems reasonable.
Thanks in advance.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Griffith, Brent"
<brent_griffith@...> wrote:
>
> OK, I looked at your file. Your input file doesn't have any serious
> problems and the program should be working better for this case.
We'll
> be filing this as a bug (change request).
>
>
>
> But the problem is that you have only "Regular-R" materials in the
> construction underneath the exterior cavity. When I change your
file to
> have a proper construction, the exterior cavity model behaves as one
> would expect. Constructions should have some "Regular" materials or
> else there is no mass (and no heat capacity) in the surface. This
can
> lead to thermal instability in some cases (eg. "temperature out of
> bounds" error); I think you found a new one. Until we can address
this
> in the next release of the program, when using the advanced surface
> model for exterior cavity you should also use full descriptions of
the
> construction's materials.
>
>
>
> Brent
>
> EnergyPlus Development Team
>
>
>
> ________________________________
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of
bbuenounzeta
> Sent: Monday, December 10, 2007 12:52 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Re: High Temperatures in Vented Cavity
>
>
>
> I have simulated the case with the 2.1 EnergyPlus and it performs
in
> the same way.
>
> Bruno
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> , Linda Lawrie
<linda@>
>
> wrote:
> >
> > This was one of the items that was addressed in the 2.1 release:
> >
> > You should upgrade and see if this is still an issue.
> >
> > Linda
> >
> > EnergyPlus WebSite: http://www.energyplus.gov
> <http://www.energyplus.gov>
> > Owner: EnergyPlus_Support list
> > Member: EnergyPlus Development Team
> >
> >
> >
> > [Non-text portions of this message have been removed]
> >
>
>
>
>
>
> [Non-text portions of this message have been removed]
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/