Inside EnergyPlus there are two separate ways that surface heat transfer
calculations are done, one for "quick" conduction and a second for
"slow" conduction.  It is the heat capacity in the surface's
construction that determines which will be used.  ("Quick" includes
terms that more directly use the opposite face temperature).  In current
and previous version of E+, the exterior vented cavity model was
implemented for only the "slow" conductions and it doesn't work properly
for "quick."  This incomplete implementation is now corrected and will
be in the next version (expected out in April).  

 

A construction with all Regular-R materials will always be "quick."  But
it is possible to have a construction made of Regular materials that is
lightweight enough to also be "quick."  I think this explains the
discontinuity you are seeing in some of your cases.  For version 2.1,
you'll have to use materials with a normal amount of mass and heat
capacity.  

 

________________________________

From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of mapascualb
Sent: Monday, January 28, 2008 10:41 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Re: High Temperatures in Vented Cavity

 

We are using regular materials but we have found the same problem in 
some cases.

In our file, if we just change the the thickness of the outter layer 
of the supporting wall by 0.01, the results changes from expected to 
physicaly impossible (surface outside temperature bigger than the 
exterior baffle temperature).

We are almost sure that this is a bug to be fixed, but in the 
meanwhile I would like to know if can trust the results of the cases 
that the simulation seems reasonable.

Thanks in advance. 

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx
<mailto:EnergyPlus_Support%40yahoogroups.com> , "Griffith, Brent" 
<brent_griffith@...> wrote:
>
> OK, I looked at your file. Your input file doesn't have any serious
> problems and the program should be working better for this case. 
We'll
> be filing this as a bug (change request). 
> 
> 
> 
> But the problem is that you have only "Regular-R" materials in the
> construction underneath the exterior cavity. When I change your 
file to
> have a proper construction, the exterior cavity model behaves as one
> would expect. Constructions should have some "Regular" materials or
> else there is no mass (and no heat capacity) in the surface. This 
can
> lead to thermal instability in some cases (eg. "temperature out of
> bounds" error); I think you found a new one. Until we can address 
this
> in the next release of the program, when using the advanced surface
> model for exterior cavity you should also use full descriptions of 
the
> construction's materials. 
> 
> 
> 
> Brent 
> 
> EnergyPlus Development Team
> 
> 
> 
> ________________________________
> 
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
<mailto:EnergyPlus_Support%40yahoogroups.com> 
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx
<mailto:EnergyPlus_Support%40yahoogroups.com> ] On Behalf Of 
bbuenounzeta
> Sent: Monday, December 10, 2007 12:52 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
<mailto:EnergyPlus_Support%40yahoogroups.com> 
> Subject: [EnergyPlus_Support] Re: High Temperatures in Vented Cavity
> 
> 
> 
> I have simulated the case with the 2.1 EnergyPlus and it performs 
in 
> the same way.
> 
> Bruno
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
<mailto:EnergyPlus_Support%40yahoogroups.com> 
> <mailto:EnergyPlus_Support%40yahoogroups.com> , Linda Lawrie 
<linda@>
> 
> wrote:
> >
> > This was one of the items that was addressed in the 2.1 release:
> > 
> > You should upgrade and see if this is still an issue.
> > 
> > Linda
> > 
> > EnergyPlus WebSite: http://www.energyplus.gov
<http://www.energyplus.gov> 
> <http://www.energyplus.gov <http://www.energyplus.gov> > 
> > Owner: EnergyPlus_Support list
> > Member: EnergyPlus Development Team
> > 
> > 
> > 
> > [Non-text portions of this message have been removed]
> >
> 
> 
> 
> 
> 
> [Non-text portions of this message have been removed]
>

 



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/