[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
RE: [EnergyPlus_Support] Water Use Equipment as mister simulation
If you are conditioning the zone, eg. with Purchased Air, then the zone
air drybulb temps are going to stay the same (because they are being
controlled). Check the change in purchased air power.
________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of bish.dj61
Sent: Wednesday, January 30, 2008 4:21 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Water Use Equipment as mister simulation
hi All
Well I have created the mister cooling simulation using the
recommendation that I got with the Water Use Equipment. I have got
everything working, and been able to observe the "latent heat rate to
zone" variable and "zone relative humidity" behave fairly well. What I
haven't been able to do is actually change the mean air temperature of
the zone which is what I am trying to do.
If I change the flow rate of the water use equipment from 0 to a high
number that pushes the rel humidity through the roof it doesn't change
the mean air temperature.
If anyone could tell me what I am doing wrong it would be great!
cheers
Danny
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/