Dear EnergyPlus Team:

I have noticed that, the Direct Solar profile from a a DesignDay shows
some unexpected bias:

I have done a test simulation with a 0º Longitude location, GTM+1
reference and  1 minute timestep. I choose April 14 as the DesignDay
so the Equation of Time is almost zero. Then: 

Both the Solar Altitude Angle and the Surface Ext Solar Beam Incident
over an horizontal surface peak at 13:00h,just as expected.

But the Direct Solar peaks at 13:29 aprox, and so does the Diffuse
Solar. This is very strange to me, is there any known problem with the
Direct and Diffuse Solar reports?  

On the other hand, I have tried to look for the ASHRAE ClearSky model,
 that is used in the DesignDays calculation. In the Input-Output
Reference say that there is more information in the Engineering
Reference but I couldn't find anything. Is it there?

Thank you 


Antonio Carrillo
ETS Ingenieros Industriales
University Of Malaga
Spain
tlf: +34-953132409





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/