Mike, I've only just seen this post, and it is the answer to the
perplexing problem that I've been witnessing. So I guess I need a
workaround (similar to what you suggested below) in order to transfer
the latent heat gain of the zone air to an actual drop in the air
temprature.
Unfortunately the latent heat gain variable output shows that it
varies wildly depending on the "actual" moisture transfer rate. I
would like to transfer the heat drop of the evaporation to the zone
air temp. The options I considered are:
1)use the drain water of the latent water use equipment to be an
input into another water use equipment that is sensible. Then the
reduction in temperature of the drain water will reach equilibrium
with the zone air and the heat drop of the evaporation will be
transferred to the air temp.
2) Use electric equipment to reduce the temperature based on
the "Water Use Equipment Latent Heat Rate to Zone" output variable.
This sounds like a good option to me.
The problem is I don't quite know how to implement either of the
above options. I would prefer option 2 -so can you tell me how I use
the output variable to drive the power of the electric equipment (or
other suitable object)?
If you can give me an actual example of the code I would use it would
be great!
cheers
Danny
\--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> I am not sure exactly what your Ecotect inputs translate to in
terms of
> EnergyPlus objects. My guess it that the latent internal gain is
described
> using ELECTRIC EQUIPMENT or OTHER EQUIPMENT. All of the "*
EQUIPMENT" objects
> for internal gains assume that the latent gain increases the
enthalpy of the
> room air mass. This means that the latent gain produces no
sensible cooling
> effect, as an adiabatic evaporation process would do. To model an
adiabatic
> addition of moisture to the zone using OTHER EQUIPMENT, you would
need two
> objects, one with a positive gain that is 100% latent, and another
with a
> negative gain which is 100% sensible. The two objects would use
the same
> design level {W} if the water is entering at room temperature. But
more
> likely, the water is cooler than the zone, so you would need to
calculate the
> energy rate required to heat the incoming water flow to room
temperature and
> make the negative sensible gain that much greater.
>
> My understanding of WATER USE EQUIPMENT (which Brent suggested a
few days ago)
> is that it will compute the cooling effect of cold water exposed to
the zone
> based on the current temperature difference. There are report
variables for
> the sensible heat gain (negative if a loss) and the moisture
addition so that
> you can confirm how the model is working.
>
> Mike
>
>
> On 23 Jan 2008 at 18:29, Danny Bishop wrote:
>
> > Hi All
> >
> > As a follow up to my previous post (I've been working on it today
seemingly in a
> > different time zone from most of you all), I just wanted to get
some more
> > feedback on the approach to modelling cooling effects of water
misters in a
> > fresh fruit market overnight.
> >
> >
> >
> > The recommendation I got for doing it in Ecotect was basically to
have an
> > appliance with a negative heat output. This sort of works (but
the calcs for the
> > power seem obscene, see footnote), but it obviously doesn't
account for the
> > following:
> >
> >
> >
> > 1) Effect on humidity
> >
> > 2) You need to assume some sort of percentage of
evaporation, and this
> > needs to be the amount that changes to and stays as vapour, ie
doesn't condense
> > anywhere.
> >
> >
> >
> > If I did this in E+ using the recommendations I've been given
(see below),
> > would they model the two above effects, instead of rely on me to
estimate
> > them?
> >
> >
> >
> > Secondly, another option that occurred to me (that should
minimise my
> > interaction with E+ as I am very green) is to include a large
latent
> > internal gain for each zone. However, when I export these to E+
(Ecotect
> > doesn't use the latent part in the calculation) I get only the
slightest
> > change in the temperature. I have uploaded these two files to the
online
> > file location, one named "Market export to E+-no latent", and the
other
> > "Market export to E+-latent". Perhaps the difference is the pesky
HVAC loads
> > which seemed to have activated themselves! If anyone can shed
some light on why
> > the difference is so small that would be great!
> >
> >
> >
> > Cheers and thanks
> >
> > Danny
> >
> > ____________________
> >
> > Footnote: latent power calculation of 1 litre of water vaporising
per
> > minute:
> >
> >
> >
> > Latent vapour heat of H20: 2270kJ/kg
> >
> >
> >
> > Power = 2270 (kJ/kg) x 1 min/60s x (1kg/min)/(1L/min)
> >
> > =2270kJ/60s per L/min
> >
> > =38kW per L/min
> >
> >
> >
> > This seems huge! Can anyone tell me if I've made a silly error?
> >
> >
> >
> > From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> > [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Josh K
> > Sent: Wednesday, 23 January 2008 4:29 AM
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> > Subject: Re: [EnergyPlus_Support] modelling misters
> >
> >
> >
> > I've used ECOTECT to create geometry for EnergyPlus simulations.
It doesn't do a
> > whole lot more than that; there are some options to create
schedules,
> > infiltration, and internal gains objects within ECOTECT, but
frankly I've found
> > it easier just to do these things within EnergyPlus.
> >
> > That being said, it does a reasonably good job of creating
geometry, as long as
> > the geometry isn't excessively complicated -- when it is, ECOTECT
sometimes has
> > a hard time calculating adjacency properly, which results in the
> > OutsideFaceEnvironment field of the SURFACE:HeatTransfer objects
sometimes being
> > specified incorrectly. In one instance, I created what was, in
retrospect,
> > excessively complicated geometry, and using the most sensitive
settings for
> > ECOTECT's inter-zonal adjacency calculations, I ended up with
about 8% of the
> > surfaces' OutsideFaceEnvironment field being specified
incorrectly. In my
> > opinion, if one were to simplify the geometry to the extent that
simulation
> > accuracy wouldn't be affected, this number would be pretty close
to 100%.
> > Unfortunately, I don't have enough experience at this point to
state
> > definitively if that's the case or not; what I can tell you is
that after using
> > the two systems together for a while, you definitely begin to get
a sense of
> > what geometric features ECOTECT will deal with correctly and
which ones might be
> > troublesome.
> >
> > The biggest annoyance when using ECOTECT to create EnergyPlus
geometry is
> > the surface naming conventions. To my knowledge, there is no way
to directly
> > name surfaces in ECOTECT; they are all automatically assigned
object numbers by
> > the software. This wouldn't even be too bad, but these object
numbers aren't
> > static. That is, if you go in and modify your geometry in ECOTECT
and re-export
> > it to ECOTECT, it's possible that an unmodified surface could
have a new object
> > name. If one is importing and exporting entire geometries en
masse, this isn't
> > really a problem, but it can be really annoying if you have a big
model and you
> > just want to export chunks of it.
> >
> > Anyways, if you learn to cope with the idiosyncrasies, ECOTECT is
a usable
> > tool for creating geometry for EnergyPlus. However, that's about
all it does --
> > no HVAC.
> >
> > Hope that helps,
> >
> > Josh
> >
> > On Jan 22, 2008 10:05 AM, Griffith, Brent <brent_griffith@...
> > <mailto:brent_griffith%40nrel.gov> > wrote:
> >
> > > If you know a water flow rate and schedule for the misters,
then it
> > > should work to use the Water Use Equipment input object with a
high
> > > latent fraction. I suggest using a Water Mains Temperatures
object for
> > > your location to model the mister's inlet water temperatures.
> > >
> > > Hopefully someone else out there knows more about Ecotect ...
> > >
> > > ________________________________
> > >
> > > From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > <EnergyPlus_Support%40yahoogroups.com>
> > > [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > <EnergyPlus_Support%40yahoogroups.com>]
> > > On Behalf Of Danny Bishop
> > > Sent: Monday, January 21, 2008 5:48 PM
> > > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > <EnergyPlus_Support%40yahoogroups.com>
> > > Subject: [EnergyPlus_Support] modelling misters
> > >
> > >
> > > Hi All
> > > I want to do a simulation modelling the use of misters to cool
a fresh
> > > food
> > > market overnight. I want to see the benefit to the temperature,
and also
> > > the
> > > effect on humidity. I would prefer to do import this to e+ via
Ecotect,
> > > but
> > > suspect that I may need to do some post processing on the IDF.
Can
> > > anyone
> > > tell me how to get my teeth into this, any examples perhaps?
> > > Cheers
> > > Danny
> > >
> > > [Non-text portions of this message have been removed]
> > >
> > > [Non-text portions of this message have been removed]
> > >
> > >
> > >
> >
> > --
> > Josh Kjenner, EIT, LEED AP
> > Manasc Isaac Architects Ltd.
> > 10225 100 Avenue :: Edmonton, AB T5J 0A1
> > 780.429.3977
> >
> > [Non-text portions of this message have been removed]
> >
> >
> >
> >
> >
> > [Non-text portions of this message have been removed]
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
under the
> > Documentation link and press the "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@...
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/