[EnergyPlus_Support] Fwd: Re: Cooling set-point not fully achieved



Differences go up to 1ºC. Does it fit the behaviour of the problem 
you describe?

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad 
<RRaustad@...> wrote:
>
> I have looked at this control issue before. I don't think it's the 
> mixing objects or other zone loads. And your offset from the set 
point 
> should be pretty small. Not to worry, the overall annual energy use 
> should be pretty close. Beside, if you run this building using a 
> different building simulation tool, your likely to get a different 
> answer. And I believe the difference in these answers will be 
greater 
> than the difference in annual energy use due to the set point 
offset. If 
> it happens all the time, adjust your set point so the "average" 
zone 
> temperature is near your target temperature.
> 
> anarui.oliveira wrote:
> >
> > Could the mixing objects or anything like that contribute to this
> > problem? Or some definitions such as humidity ratios or the 
like?...
> > Getting worried here... the aim was exactly to predict the energy
> > consumption of a building throughout a year (for official, legal
> > purposes)...
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, "anarui.oliveira"
> > <anarui.oliveira@> wrote:
> >
> > Is this problem equally likely to happen if I use a Purchased Air
> > approach?
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > <RRaustad@> wrote:
> > >
> > > You could try increasing the time step in hour. I have no other
> > > suggestions. This is a known issue and we are working to 
correct it.
> > >
> > > anarui.oliveira wrote:
> > > >
> > > > That field is already set to 1, and time step in hours is set 
to
> > 4.
> > > >
> > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > > > <RRaustad@> wrote:
> > > > >
> > > > > What you describe is not a capacity issue, it is related to 
the
> > > > > prediction of loads. If you add the report variable
> > for "Zone/Sys
> > > > > Sensible Load Predicted" and set the report variable 
frequency
> > to
> > > > > detailed, you will see why this is happening. Try reducing 
the
> > > > Minimum
> > > > > System Time Step in the System Convergence Limits object. 
You
> > > > probably
> > > > > will not eliminate the problem, but it should get better.
> > > > >
> > > > >
> > > > > anarui.oliveira wrote:
> > > > > >
> > > > > > What if, in a similar (heating) case, water flow doesn't
> > reach the
> > > > > > maximum when the problem occurs, and increasing the air 
flow
> > > > causes
> > > > > > further departure from temperature setpoint?...(Less than
> > about
> > > > 1.5
> > > > > > times the auto-sized air flow also leads to poorer 
setpoint
> > > > > > tracking); reported air flow is always equal to the 
constant
> > > > volume
> > > > > > fan flow, and ouside air flow rate is (and must be) user
> > > > specified.
> > > > > >
> > > > > > Regards,
> > > > > > Ana.
> > > > > >
> > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard 
Raustad
> > > > > > <RRaustad@> wrote:
> > > > > > >
> > > > > > > Then try again to manually size the coil in the problem
> > zone to
> > > > > > twice
> > > > > > > the size reported in the eio file. Also increase the air
> > flow
> > > > rate
> > > > > > for
> > > > > > > that fan coil unit and fan to twice the autosized 
value. If
> > > > htis is
> > > > > > > happening in more than 1 zone, then just pick 1 for now 
to
> > test
> > > > > > this out.
> > > > > > >
> > > > > > > Then tell me what happens to the maximum zone 
temperature.
> > Did
> > > > the
> > > > > > > maximum zone temperature go down? Also tell me if the 
water
> > flow
> > > > > > rate is
> > > > > > > at a maximum when the zone temperature exceeds the set
> > point.
> > > > You
> > > > > > can
> > > > > > > report "System Node VolFlowRate" for the coil water 
inlet
> > node
> > > > and
> > > > > > fan
> > > > > > > coil air inlet node to easily match volumetric flow rate
> > with
> > > > your
> > > > > > inputs.
> > > > > > >
> > > > > > > This just sounds like a sizing issue and should be 
easily
> > > > resolved.
> > > > > > >
> > > > > > > anarui.oliveira wrote:
> > > > > > > >
> > > > > > > > Apparently, yes, but I set it to autosize (and I 
think I
> > > > already
> > > > > > did
> > > > > > > > a trial with a larger, user-defined, water flow 
rate)...
> > > > > > > >
> > > > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard
> > Raustad
> > > > > > > > <RRaustad@> wrote:
> > > > > > > > >
> > > > > > > > > I have not looked at your input file, can you tell 
me
> > if the
> > > > > > water
> > > > > > > > mass
> > > > > > > > > flow rate through the fan coil is at a maximum when 
the
> > > > cooling
> > > > > > set
> > > > > > > > > point is not met?
> > > > > > > > >
> > > > > > > > > anarui.oliveira wrote:
> > > > > > > > > >
> > > > > > > > > > Please forgive me for insisting, but I DO have 
some
> > > > urgency on
> > > > > > > > this
> > > > > > > > > > one...
> > > > > > > > > > Again, thanks for any help,
> > > > > > > > > > Ana.
> > > > > > > > > >
> > > > > > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > > > > > <mailto:EnergyPlus_Support%
> > > > > > 40yahoogroups.com>, "anarui.oliveira"
> > > > > > > > > > <anarui.oliveira@> wrote:
> > > > > > > > > > >
> > > > > > > > > > > Hi again.
> > > > > > > > > > >
> > > > > > > > > > > I'm uploading a new file 
(Zone36598_cFancoil_exp),
> > > > hoping
> > > > > > that
> > > > > > > > > > someone
> > > > > > > > > > > can help me figure out why the cooling setpoints
> > are not
> > > > > > being
> > > > > > > > > > achieved
> > > > > > > > > > > for all times when the controls are active 
(namely
> > in
> > > > Zone
> > > > > > > > 36598).
> > > > > > > > > > The
> > > > > > > > > > > model consists of Fancoil units created with 
Compact
> > > > HVAC,
> > > > > > and
> > > > > > > > then
> > > > > > > > > > > edited in the expanded file.
> > > > > > > > > > > I tried several user-defined and sizing 
options, but
> > > > > > couldn't
> > > > > > > > solve
> > > > > > > > > > the
> > > > > > > > > > > temperature peaks above 25ºC.
> > > > > > > > > > >
> > > > > > > > > > > Thanks in advance,
> > > > > > > > > > > Ana Rui.
> > > > > > > > > > >
> > > > > > > > > >
> > > > > > > > > >
> > > > > > > > >
> > > > > > > > > --
> > > > > > > > > Richard A. Raustad
> > > > > > > > > Senior Research Engineer
> > > > > > > > > Florida Solar Energy Center
> > > > > > > > > University of Central Florida
> > > > > > > > > 1679 Clearlake Road
> > > > > > > > > Cocoa, FL 32922-5703
> > > > > > > > > Phone: (321) 638-1454
> > > > > > > > > Fax: (321) 638-1439 or 1010
> > > > > > > > > Visit our web site at: http://www.fsec.ucf.edu 
> > <http://www.fsec.ucf.edu>
> > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu> 
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>
> > > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu> 
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu> 
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>>
> > > > > > > > >
> > > > > > > > > UCF - From Promise to Prominence: Celebrating 40 
Years
> > > > > > > > >
> > > > > > > >
> > > > > > > >
> > > > > > >
> > > > > > > --
> > > > > > > Richard A. Raustad
> > > > > > > Senior Research Engineer
> > > > > > > Florida Solar Energy Center
> > > > > > > University of Central Florida
> > > > > > > 1679 Clearlake Road
> > > > > > > Cocoa, FL 32922-5703
> > > > > > > Phone: (321) 638-1454
> > > > > > > Fax: (321) 638-1439 or 1010
> > > > > > > Visit our web site at: http://www.fsec.ucf.edu 
> > <http://www.fsec.ucf.edu>
> > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu> 
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>
> > > > > > >
> > > > > > > UCF - From Promise to Prominence: Celebrating 40 Years
> > > > > > >
> > > > > >
> > > > > >
> > > > >
> > > > > --
> > > > > Richard A. Raustad
> > > > > Senior Research Engineer
> > > > > Florida Solar Energy Center
> > > > > University of Central Florida
> > > > > 1679 Clearlake Road
> > > > > Cocoa, FL 32922-5703
> > > > > Phone: (321) 638-1454
> > > > > Fax: (321) 638-1439 or 1010
> > > > > Visit our web site at: http://www.fsec.ucf.edu 
> > <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > > >
> > > > > UCF - From Promise to Prominence: Celebrating 40 Years
> > > > >
> > > >
> > > >
> > >
> > > --
> > > Richard A. Raustad
> > > Senior Research Engineer
> > > Florida Solar Energy Center
> > > University of Central Florida
> > > 1679 Clearlake Road
> > > Cocoa, FL 32922-5703
> > > Phone: (321) 638-1454
> > > Fax: (321) 638-1439 or 1010
> > > Visit our web site at: http://www.fsec.ucf.edu 
<http://www.fsec.ucf.edu>
> > >
> > > UCF - From Promise to Prominence: Celebrating 40 Years
> > >
> >
> > --- End forwarded message ---
> >
> >  
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/