Re: [EnergyPlus_Support] a question about ground floor calculations
Slab is a single-zone model, it cannot handle more than one zone mean air
temperature object. Multiple objects should have resulted in errors from Slab.
Mike
On 5 Feb 2008 at 13:05, Simge Andolsun wrote:
> I tried entering the interior mean air temperatures of the 5 zones as 5 objects
> into slab.exe. Slab.exe calculated a sort of mean value as the ground
> temperatures....Do you think we may calculate the ground floor temperatures by
> entering the mean air temperatures of each zone into slab.exe as separate
> objects? If not, for the ground floor calculations, should we always enter a
> single object into slab.exe?
>
> Thanks,
> Simge Andolsun
>
> "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
> It is difficult to say for sure. It depends on how large the
> temperature
> difference is, and if the zones are controlled to different temperatures or
> free-floating. One approach would be to use the average of the zone
> temperatures.
>
> Mike
>
> On 27 Jan 2008 at 19:58, Simge Andolsun wrote:
>
> > I am simulating a 40mx40m, 10 story high building. Each floor is divided into
> > 5 zones. Each zone gives different mean air temperatures. In order to
> > calculate ground floor temperatures, the mean air temperature of which zone
> > should be entered into slab.exe ? Should it be the core zone?...or should I
> > decouple the ground floor from the ground by defining itself as the other zone
> > surface and run the simulations? if so, what should be entered as the ground
> > floor temperatures? Because the mean air temperature of each zone will be
> > different anyway. May anybody help me?
> >
> > Thanks in advance,
> >
> >
> > ---------------------------------
> > Be a better friend, newshound, and know-it-all with Yahoo! Mobile. Try it now.
> >
> > [Non-text portions of this message have been removed]
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> > Documentation link and press the "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
>
>
>
> ---------------------------------
> Be a better friend, newshound, and know-it-all with Yahoo! Mobile. Try it now.
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/