[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Fwd: Re: Cooling set-point not fully achieved
Thank you for the suggestions. For now I used a PA approach, because
I had to deliver results for yesterday, but I will try your
suggestions when I have a chance, to check the behaviour of the
simulation.
I only tried 4 and 6 steps in hour (15 and 10 min), always using 1
as minimum step in convergence limits.
Regards,
Ana.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
<RRaustad@...> wrote:
>
> Ana, change the frequency of the report variables to "detailed".
You
> will notice that the loss of set point control occurs when the
program
> is simulating at a reduced time step (shorter than 15 minutes).
And it
> doesn't happen for the entire duration of the shortened time step
> period. This is exactly the problem we have been seeing. When any
zone
> temperature changes by more than 0.03C, the simulation tries again
at a
> shorter time step (so some load changed quickly to make the zone
> temperature change quickly). When this occurs, the prediction of
zone
> loads are somewhat less accurate. We are working on this and hope
to
> have a resolution soon. I haven't looked at your input closely
enough to
> know why this only happens in 1 zone. Is it possible for you
to "smooth"
> out the people, equipment and lighting loads (to eliminate step
> functions in load) in zone 43515? For instance, it takes several
minutes
> for occupancy to change in a zone, and with diversity of
equipment,
> those loads could also be assumed to change over several minutes.
You
> could change to using compact schedules to provide a "smoother"
> transition from 1 minute to the next (or from 1 15-min period to
the
> next), maybe that would help. I still think your results are not
> impacted all that much, but I also know that when someone sees the
loss
> of set point, the results come into question.
>
> Here's an example of smoothing out a schedule, I'm not saying this
will
> work, but if you are really determined to eliminate this problem,
it's
> worth a try. You have schedules for occupancy, equipment,
lighting,
> infiltration, etc. Even if your schedules are "fixed" by some
standard,
> smoothing them out quickly (in 15 minute intervals) , while still
> conform to the intent of the schedule.
>
> Also, what happened when you tried to simulate at 1 hour time
steps?
>
> Your schedule:
> DAYSCHEDULE,
> School_People_WeekDay, !- Name
> Fraction, !- ScheduleType
> 0, !- Hour 1
> 0, !- Hour 2
> 0, !- Hour 3
> 0, !- Hour 4
> 0, !- Hour 5
> 0, !- Hour 6
> 0, !- Hour 7
> 0, !- Hour 8
> 0.05, !- Hour 9
> 0.9, !- Hour 10
> 1, !- Hour 11
> 1, !- Hour 12
> 1, !- Hour 13
> 0.9, !- Hour 14
> 0.9, !- Hour 15
> 1, !- Hour 16
> 1, !- Hour 17
> 1, !- Hour 18
> 0.8, !- Hour 19
> 0.1, !- Hour 20
> 0, !- Hour 21
> 0, !- Hour 22
> 0, !- Hour 23
> 0; !- Hour 24
>
> My suggestion:
> SCHEDULE:COMPACT,
> School_People_Yearly, !- Name
> Fraction, !- ScheduleType
> Through: 31 Dec, !- Complex Field #1
> For: Weekdays SummerDesignDay, !- Complex Field #2
> Until: 09:00, !- Complex Field #3
> 0, !- Complex Field #4
> Until: 09:15, !- Complex Field #5
> 0.05, !- Complex Field #6
> Until: 09:30, !- Complex Field #7
> 0.25, !- Complex Field #8
> Until: 09:45, !- Complex Field #9
> 0.75, !- Complex Field #10
> Until: 10:00, !- Complex Field #11
> 0.8, !- Complex Field #12
> Until: 10:15, !- Complex Field #13
> 0.9, !- Complex Field #14
> Until: 14:00, !- Complex Field #15
> 1, !- Complex Field #16
> Until: 14:15, !- Complex Field #17
> 0.95, !- Complex Field #18
> Until: 16:00, !- Complex Field #19
> 0.9, !- Complex Field #20
> Until: 16:15, !- Complex Field #13
> 0.95, !- Complex Field #14
> Until: 19:00, !- Complex Field #15
> 1, !- Complex Field #16
> Until: 19:15, !- Complex Field #17
> 0.9, !- Complex Field #18
> Until: 19:30, !- Complex Field #19
> 0.7, !- Complex Field #20
> Until: 19:45, !- Complex Field #15
> 0.5, !- Complex Field #16
> Until: 20:00, !- Complex Field #17
> 0.3, !- Complex Field #18
> Until: 21:00, !- Complex Field #19
> 0.1, !- Complex Field #20
> Until: 24:00, !- Complex Field #19
> 0.0, !- Complex Field #20
> For: Weekends, !- Complex Field #21
> Until: 24:00, !- Complex Field #22
> 0, !- Complex Field #23
> For: Holidays, !- Complex Field #24
> Until: 24:00, !- Complex Field #25
> 0, !- Complex Field #26
> For: WinterDesignDay AllOtherDays, !- Complex Field #27
> Until: 24:00, !- Complex Field #28
> 0; !- Complex Field #29
>
>
>
> Richard Raustad wrote:
> >
> > Well, I would rather see a graph, but from what you describe,
yes it does.
> >
> > If you wish, email a graph in the spreadsheet (save it as xls)
to:
> > rraustad@... <mailto:rraustad%40fsec.ucf.edu>
> >
> > anarui.oliveira wrote:
> > >
> > > Differences go up to 1ºC. Does it fit the behaviour of the
problem
> > > you describe?
> > >
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > > <RRaustad@> wrote:
> > > >
> > > > I have looked at this control issue before. I don't think
it's the
> > > > mixing objects or other zone loads. And your offset from the
set
> > > point
> > > > should be pretty small. Not to worry, the overall annual
energy use
> > > > should be pretty close. Beside, if you run this building
using a
> > > > different building simulation tool, your likely to get a
different
> > > > answer. And I believe the difference in these answers will be
> > > greater
> > > > than the difference in annual energy use due to the set point
> > > offset. If
> > > > it happens all the time, adjust your set point so
the "average"
> > > zone
> > > > temperature is near your target temperature.
> > > >
> > > > anarui.oliveira wrote:
> > > > >
> > > > > Could the mixing objects or anything like that contribute
to this
> > > > > problem? Or some definitions such as humidity ratios or the
> > > like?...
> > > > > Getting worried here... the aim was exactly to predict the
energy
> > > > > consumption of a building throughout a year (for official,
legal
> > > > > purposes)...
> > > > >
> > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > <mailto:EnergyPlus_Support%
40yahoogroups.com>, "anarui.oliveira"
> > > > > <anarui.oliveira@> wrote:
> > > > >
> > > > > Is this problem equally likely to happen if I use a
Purchased Air
> > > > > approach?
> > > > >
> > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard
Raustad
> > > > > <RRaustad@> wrote:
> > > > > >
> > > > > > You could try increasing the time step in hour. I have
no other
> > > > > > suggestions. This is a known issue and we are working to
> > > correct it.
> > > > > >
> > > > > > anarui.oliveira wrote:
> > > > > > >
> > > > > > > That field is already set to 1, and time step in hours
is set
> > > to
> > > > > 4.
> > > > > > >
> > > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard
Raustad
> > > > > > > <RRaustad@> wrote:
> > > > > > > >
> > > > > > > > What you describe is not a capacity issue, it is
related to
> > > the
> > > > > > > > prediction of loads. If you add the report variable
> > > > > for "Zone/Sys
> > > > > > > > Sensible Load Predicted" and set the report variable
> > > frequency
> > > > > to
> > > > > > > > detailed, you will see why this is happening. Try
reducing
> > > the
> > > > > > > Minimum
> > > > > > > > System Time Step in the System Convergence Limits
object.
> > > You
> > > > > > > probably
> > > > > > > > will not eliminate the problem, but it should get
better.
> > > > > > > >
> > > > > > > >
> > > > > > > > anarui.oliveira wrote:
> > > > > > > > >
> > > > > > > > > What if, in a similar (heating) case, water flow
doesn't
> > > > > reach the
> > > > > > > > > maximum when the problem occurs, and increasing
the air
> > > flow
> > > > > > > causes
> > > > > > > > > further departure from temperature setpoint?...
(Less than
> > > > > about
> > > > > > > 1.5
> > > > > > > > > times the auto-sized air flow also leads to poorer
> > > setpoint
> > > > > > > > > tracking); reported air flow is always equal to the
> > > constant
> > > > > > > volume
> > > > > > > > > fan flow, and ouside air flow rate is (and must
be) user
> > > > > > > specified.
> > > > > > > > >
> > > > > > > > > Regards,
> > > > > > > > > Ana.
> > > > > > > > >
> > > > > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>,
Richard
> > > Raustad
> > > > > > > > > <RRaustad@> wrote:
> > > > > > > > > >
> > > > > > > > > > Then try again to manually size the coil in the
problem
> > > > > zone to
> > > > > > > > > twice
> > > > > > > > > > the size reported in the eio file. Also increase
the air
> > > > > flow
> > > > > > > rate
> > > > > > > > > for
> > > > > > > > > > that fan coil unit and fan to twice the autosized
> > > value. If
> > > > > > > htis is
> > > > > > > > > > happening in more than 1 zone, then just pick 1
for now
> > > to
> > > > > test
> > > > > > > > > this out.
> > > > > > > > > >
> > > > > > > > > > Then tell me what happens to the maximum zone
> > > temperature.
> > > > > Did
> > > > > > > the
> > > > > > > > > > maximum zone temperature go down? Also tell me
if the
> > > water
> > > > > flow
> > > > > > > > > rate is
> > > > > > > > > > at a maximum when the zone temperature exceeds
the set
> > > > > point.
> > > > > > > You
> > > > > > > > > can
> > > > > > > > > > report "System Node VolFlowRate" for the coil
water
> > > inlet
> > > > > node
> > > > > > > and
> > > > > > > > > fan
> > > > > > > > > > coil air inlet node to easily match volumetric
flow rate
> > > > > with
> > > > > > > your
> > > > > > > > > inputs.
> > > > > > > > > >
> > > > > > > > > > This just sounds like a sizing issue and should
be
> > > easily
> > > > > > > resolved.
> > > > > > > > > >
> > > > > > > > > > anarui.oliveira wrote:
> > > > > > > > > > >
> > > > > > > > > > > Apparently, yes, but I set it to autosize (and
I
> > > think I
> > > > > > > already
> > > > > > > > > did
> > > > > > > > > > > a trial with a larger, user-defined, water flow
> > > rate)...
> > > > > > > > > > >
> > > > > > > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>,
Richard
> > > > > Raustad
> > > > > > > > > > > <RRaustad@> wrote:
> > > > > > > > > > > >
> > > > > > > > > > > > I have not looked at your input file, can
you tell
> > > me
> > > > > if the
> > > > > > > > > water
> > > > > > > > > > > mass
> > > > > > > > > > > > flow rate through the fan coil is at a
maximum when
> > > the
> > > > > > > cooling
> > > > > > > > > set
> > > > > > > > > > > > point is not met?
> > > > > > > > > > > >
> > > > > > > > > > > > anarui.oliveira wrote:
> > > > > > > > > > > > >
> > > > > > > > > > > > > Please forgive me for insisting, but I DO
have
> > > some
> > > > > > > urgency on
> > > > > > > > > > > this
> > > > > > > > > > > > > one...
> > > > > > > > > > > > > Again, thanks for any help,
> > > > > > > > > > > > > Ana.
> > > > > > > > > > > > >
> > > > > > > > > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > > > > > > > > <mailto:EnergyPlus_Support%
> > > > > > > > > 40yahoogroups.com>, "anarui.oliveira"
> > > > > > > > > > > > > <anarui.oliveira@> wrote:
> > > > > > > > > > > > > >
> > > > > > > > > > > > > > Hi again.
> > > > > > > > > > > > > >
> > > > > > > > > > > > > > I'm uploading a new file
> > > (Zone36598_cFancoil_exp),
> > > > > > > hoping
> > > > > > > > > that
> > > > > > > > > > > > > someone
> > > > > > > > > > > > > > can help me figure out why the cooling
setpoints
> > > > > are not
> > > > > > > > > being
> > > > > > > > > > > > > achieved
> > > > > > > > > > > > > > for all times when the controls are
active
> > > (namely
> > > > > in
> > > > > > > Zone
> > > > > > > > > > > 36598).
> > > > > > > > > > > > > The
> > > > > > > > > > > > > > model consists of Fancoil units created
with
> > > Compact
> > > > > > > HVAC,
> > > > > > > > > and
> > > > > > > > > > > then
> > > > > > > > > > > > > > edited in the expanded file.
> > > > > > > > > > > > > > I tried several user-defined and sizing
> > > options, but
> > > > > > > > > couldn't
> > > > > > > > > > > solve
> > > > > > > > > > > > > the
> > > > > > > > > > > > > > temperature peaks above 25ºC.
> > > > > > > > > > > > > >
> > > > > > > > > > > > > > Thanks in advance,
> > > > > > > > > > > > > > Ana Rui.
> > > > > > > > > > > > > >
> > > > > > > > > > > > >
> > > > > > > > > > > > >
> > > > > > > > > > > >
> > > > > > > > > > > > --
> > > > > > > > > > > > Richard A. Raustad
> > > > > > > > > > > > Senior Research Engineer
> > > > > > > > > > > > Florida Solar Energy Center
> > > > > > > > > > > > University of Central Florida
> > > > > > > > > > > > 1679 Clearlake Road
> > > > > > > > > > > > Cocoa, FL 32922-5703
> > > > > > > > > > > > Phone: (321) 638-1454
> > > > > > > > > > > > Fax: (321) 638-1439 or 1010
> > > > > > > > > > > > Visit our web site at:
http://www.fsec.ucf.edu
> > <http://www.fsec.ucf.edu>
> > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>
> > > > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>>
> > > > > > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>
> > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>>>
> > > > > > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>
> > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>>
> > > > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>
> > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>>>>
> > > > > > > > > > > >
> > > > > > > > > > > > UCF - From Promise to Prominence:
Celebrating 40
> > > Years
> > > > > > > > > > > >
> > > > > > > > > > >
> > > > > > > > > > >
> > > > > > > > > >
> > > > > > > > > > --
> > > > > > > > > > Richard A. Raustad
> > > > > > > > > > Senior Research Engineer
> > > > > > > > > > Florida Solar Energy Center
> > > > > > > > > > University of Central Florida
> > > > > > > > > > 1679 Clearlake Road
> > > > > > > > > > Cocoa, FL 32922-5703
> > > > > > > > > > Phone: (321) 638-1454
> > > > > > > > > > Fax: (321) 638-1439 or 1010
> > > > > > > > > > Visit our web site at: http://www.fsec.ucf.edu
> > <http://www.fsec.ucf.edu>
> > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>
> > > > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>>
> > > > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>
> > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>>>
> > > > > > > > > >
> > > > > > > > > > UCF - From Promise to Prominence: Celebrating 40
Years
> > > > > > > > > >
> > > > > > > > >
> > > > > > > > >
> > > > > > > >
> > > > > > > > --
> > > > > > > > Richard A. Raustad
> > > > > > > > Senior Research Engineer
> > > > > > > > Florida Solar Energy Center
> > > > > > > > University of Central Florida
> > > > > > > > 1679 Clearlake Road
> > > > > > > > Cocoa, FL 32922-5703
> > > > > > > > Phone: (321) 638-1454
> > > > > > > > Fax: (321) 638-1439 or 1010
> > > > > > > > Visit our web site at: http://www.fsec.ucf.edu
> > <http://www.fsec.ucf.edu>
> > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>
> > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>>
> > > > > > > >
> > > > > > > > UCF - From Promise to Prominence: Celebrating 40
Years
> > > > > > > >
> > > > > > >
> > > > > > >
> > > > > >
> > > > > > --
> > > > > > Richard A. Raustad
> > > > > > Senior Research Engineer
> > > > > > Florida Solar Energy Center
> > > > > > University of Central Florida
> > > > > > 1679 Clearlake Road
> > > > > > Cocoa, FL 32922-5703
> > > > > > Phone: (321) 638-1454
> > > > > > Fax: (321) 638-1439 or 1010
> > > > > > Visit our web site at: http://www.fsec.ucf.edu
> > <http://www.fsec.ucf.edu>
> > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>
> > > > > >
> > > > > > UCF - From Promise to Prominence: Celebrating 40 Years
> > > > > >
> > > > >
> > > > > --- End forwarded message ---
> > > > >
> > > > >
> > > >
> > > > --
> > > > Richard A. Raustad
> > > > Senior Research Engineer
> > > > Florida Solar Energy Center
> > > > University of Central Florida
> > > > 1679 Clearlake Road
> > > > Cocoa, FL 32922-5703
> > > > Phone: (321) 638-1454
> > > > Fax: (321) 638-1439 or 1010
> > > > Visit our web site at: http://www.fsec.ucf.edu
> > <http://www.fsec.ucf.edu> <http://www.fsec.ucf.edu
> > <http://www.fsec.ucf.edu>>
> > > >
> > > > UCF - From Promise to Prominence: Celebrating 40 Years
> > > >
> > >
> > >
> >
> > --
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL 32922-5703
> > Phone: (321) 638-1454
> > Fax: (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu
<http://www.fsec.ucf.edu>
> >
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/