Marzia,

In the case of PurchAirTable it is most likely due to the
lack of any infiltration and to the solar gain through an unshaded
south facing window. The internal gains (people, lights, equip) are
in the normal range.

Fred Buhl

marziasedino wrote:
> Hi there,
>
> I am having some problems in using the "PurchasedAir" in one of my E+ 
> model, apparently I get unreasonable outputs. 
> I analysed one of the E+ simplest examples "PurchAirTable" and realized 
> it shows the same problem: if you run it and check the Mean Air 
> temperature of the zones you can see the values are too high (up to 30°
> C) considering the outdoor temperature during the winter season. As the 
> internal heat gains are reasonable and the weather file I used is the 
> Venice one (where the solar heat gains are not high enough to justify 
> such a trend) I wonder if I am forgetting to consider some other 
> variable or if there is a problem in the model itself….
> Could you please let me know what you think?
>
> Thanks
>
> Marzia
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
>  
> Yahoo! Groups Links
>
>
>
>   


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/