Re: [EnergyPlus_Support] UTSC air preheat for a Air to Water Heat Pump Simulation



The UTSC (SOLAR COLLECTOR:UNGLAZED TRANSPIRED) outlet node should be an outside 
air inlet for an AIR PRIMARY LOOP system.  If we had an Air-to-Water heat pump 
model, then you could connect it to that.  All we have are water-to-water and 
water-to-air heat pumps.  By water-to-air, we mean the zone supply air is on 
the "air" side of the heat pump, and the water side is the source/sink.

Mike


On 10 Feb 2008 at 23:32, bgavin99 wrote:

> What would be the best object to use to couple these two devices and 
> make the simulation happen?
> UTSC seem to need a zone for output but I wonder if a plenum is 
> possible.
> I may be pushing the design of Energy Plus unfortunately.
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/