[EnergyPlus_Support] Re: ASHRAE 90.1 Windows
Strictly considering the ASHRAE 90.1 Appendix G modeling requirements:
The "Baseline" models are required to use a lightweight wall
construction with actual overall "U" equal to the Table 5.5-5
requirement. The "proposed" wall construction must use the actual
mass and other construction details, including consideration of
bridging effects.
This is general info related to the ASHRAE standard; I haven't looked
at the example files yet....
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "brittm35" <michelle@...>
wrote:
>
> Does the advice to use the example file generator also apply to
> building composite walls/roofs for which we don't find examples in the
> CompositeWallConstruction.idf file? The documentation says to not
> edit the inner layer of the composite wall construction...I see how to
> build layered walls, but once framing comes into play that creates
> bridging effect, or is otherwise not a "layer" I'm not clear. Someone
> said if the goal is an R-13 (for example) just layer something that
> gives you an R-13, this doesn't sound right? Shouldn't I be building
> something that reflects different thermal properties of say an R-13
> concrete vs steel framed vs stick framed?
>
> Thank you, and I apologize if this is terribly basic, I did scour old
> posts and documentation.
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Griffith, Brent"
> <brent_griffith@> wrote:
> >
> > You can copy minimum-standard constructions out of example files
> > produced by the EnergyPlus Example File Generator.
> >
> >
> >
> > ________________________________
> >
> > From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> > [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of JV Dirkes II
> > Sent: Monday, February 11, 2008 4:38 PM
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> > Subject: [EnergyPlus_Support] ASHRAE 90.1 Windows
> >
> >
> >
> > Dear EPlus Support Team,
> >
> > I'm hoping that someone has compiled a set of glazing inputs which
> > match the "U" and "SHGC" values needed for the ASHRAE 90.1 "baseline"
> > models.. and are willing to share them. I'm working on a Climate Zone
> > 5 model and am trying to avoid the iterations in Window 5 in order to
> > get the proper properties. Thanks!
> >
> >
> >
> >
> >
> > [Non-text portions of this message have been removed]
> >
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/