[EnergyPlus_Support] Daylighting Detailed. Illumination Map: Grid Error?



Dear all, 

Why is it that the Y ref point = 12.25 when i set the max to 10.00? 
The two warnings in the .err file are as follows: 

Program Version,EnergyPlus 2.1.0.023, 14/02/2008 5:17 PM,IDD_Version 
2.1.0.023
   ** Warning ** World Coordinate System selected.  Any non-zero 
Building/Zone North Axes or non-zero Zone Origins are ignored.
   **   ~~~   ** These will be used in Daylighting:Detailed 
calculations but not in normal geometry inputs.
   ** Warning ** SetUpDaylightCoords: Reference Map point Y Value 
outside Zone Min/Max Y, Zone=LEVEL1
   **   ~~~   ** ...Y Reference Point= 12.25, Zone Minimum Y= 0.00, 
Zone Maximum Y= 10.00

The Y coordinates of the two reference points in the Daylighting 
Detail object are 3 and 6.

regards,
ooi 



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/