Currently, not all equipment types register plant flow requirements for
autosizing. Some of these have been fixed, but in general if the water flow
rate is not autosizeable (as it the case for COIL:WaterToAirHP:*) then the
plant loop probably does not see that flow rate when autosizing the loop flow.
Check the autosized plant loop flow rate in the eio output file to see if it
seems reasonable. I suspect you will need to use hard sizes for the plant loop
flow rates.
Mike
On 20 Feb 2008 at 14:20, bkdawe1979 wrote:
> Hi all
> I'm modelling a building with a WLHP system and having some trouble
> with the following warning, which is fairly typical for all zones.
> Basically, I'm not sure how the loop temperatures are reaching
> the levels indicated in the error report since I've set my schedules
> and plant sizing objects to an appropriate range for this type of
> system. Also, the cooling tower should be sized highed enough to handle
> the load. The error doesn't seem to be having a major impact on space
> temperature so I'm not even sure that it's a concern. Can anybody
> suggest how I can get rid of this error? Any help would be
> appreciated.
>
> Thanks
> Brad
>
>
> Warning ** WaterToAir Heat pump:cooling [HEAT PUMP COOLING MODE AHU226]
> shut off on high pressure > 4000000
> This error occurred 39201 times. Max=73.049928 SourceSideInletTemp[C]
> Min=62.835061 SourceSideInletTemp[C]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/