The building envlope load is not readily reportable with current output
options. In the Input Output Reference, search for the report variables and
find the definitions. Zone Window Heat Loss/Gain already include the
transmitted solar. And Zone Opaque Surface Inside Face Conduction is only
meaningful when summed over longer periods of time (at least a day, better a
week or month) because of thermal storage in the wall construction.
Mike
On 22 Feb 2008 at 3:35, olifpp wrote:
> hello:
> i have a question that " how to get the heating load and coolind
> load of the building envelop hourly?"
> i try to plus "Zone Opaque Surface Inside Face Conduction Loss"
> and "Zone Transmitted Solar" and "Zone Window Heat Loss", and i think
> the sum of the three is the building envelop load.
> and i also use the " purchased air" model to simulate the same
> building in which there is no people,lighting and equipment. i think
> the purchased air heating rate and the purchased air cooling rate is
> the building envelop load hourly.
>
> but the first result is not equal to the second, do i understand
> mistakenly? can you give me some help? thanks much!
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/