Re: [EnergyPlus_Support] regeneration coil
Did you "list" the HW coil type and name in the Outside Air System object?
You would also want the HW coil to turn on only when the desiccant
system is on. The only way I can think of is to manually create an
availability schedule for the HW coil based on the times when the
desiccant system operates.
davide.loba wrote:
>
> Hi all,
>
> I have a problem with a desiccant dehumidifier, placed in the outside
> air system. I need to simulate a hot water coil as regeneration air
> heater, instead of a gas coil. To do that, I left blank the fields
> about the regeneration air heater in DESICCANT DEHUMIDIFIER object, and
> I put a COIL:Water:SimpleHeating coil in the outside air system. To
> control it, I use a CONTROLLER:SIMPLE controller, with the air outlet
> node as control_node, and water inlet node as actuator_node. There is a
> SET POINT:MANAGER:SCHEDULED fixed setpoint temperature (70°C) on air
> outlet node.
> The simulation ends correctly, without any severe error, but the
> regeneration coil doesn't work: "total water heating coil rate" is
> always 0.
> Is it possibile to simulate this type of system?
>
> Thanks in advance for your help.
>
> Loba
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/